[EnergyPlus_Support] Re: Heating Coil and Cooling Coil are running simultaneously!?!?





If I were you, I would open the expanded idf (xxx.expidf) and check how this is expanding. I don't use templates, so I can't really help you further. If your thermostat setpoints are 20/22, then your coil outlet air setpoints should vary between 20+11=31 for heating and 22-11=11 for cooling. If the template expands in such a way that it uses setpointmanager:scheduled to assign fixed setpoints, then it is obvious that no matter the demand, the outlet of the coil will be a fixed temperature. This is not the best solution for an AHU with cooling - heating coils in series. The heating coil will almost always be reheating cooled air.

If this is a VAV with reheat at the terminals, then you could set the heating coil to bring the same temp as the cooling coil in the AHU. Beware that the reheaters at the terminals will always reheat, regardless whether the zone needs cooling or heating. It only reheats to a smaller temperature in the case of cooling...so for it to really cool, it needs to be schedules to be off during cooling times.

__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___