[EnergyPlus_Support] The control problem
- To: "EnergyPlus_Support@xxxxxxxxxxxxxxx" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
- Subject: [EnergyPlus_Support] The control problem
- From: "Yan, Ying" <yiy11005@xxxxxxxxxxxxxx>
- Date: Wed, 18 Dec 2013 20:06:33 +0000
- Accept-language: en-US
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Wed, 18 Dec 2013 13:06:38 -0700
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1387397195; bh=etgpGYU3RLE9UIfML1o+LIBIDvlZnSXSpbUYylcQ2p0=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:To:Thread-Topic:Thread-Index:Message-ID:Accept-Language:Content-Language:X-MS-Has-Attach:X-MS-TNEF-Correlator:X-Originating-IP:X-eGroups-Msg-Info:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type; b=WsqG2tGyHaz7oXRdRP+3xGUYv2TkUwtk3OugitwE/wXWFi93SI/FA+e9RgK/uCaPPhIPg3ZWfbwV4Ljif5A1YRYv8mdvRFxchen9A8L19kQatDsYifj22vwcTIQMbg0UxxPvn+eLaWxpu6rspcp2TDs2Mq3tbzG2Y2vD0+jFAIo=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echoe; d=yahoogroups.com; b=AAtT00/776MuxUNvK/L3v0Z/w6sS63Qg/SLc8ZdYCNoXM3QRtfY4eodEZ2NsfTYUvlkMpPJp0FNdmugrxKT6wPuMSqDIgfqbiIjslwzQorsVl/DC8lBuSfgaG8YeZdHxcsvswyAYmploYB51B3PIS79ayU8V7QbJHudISSkPiiw=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Thread-index: Ac78LHs0q4ZC4X0NS/aTS05m70iX3Q==
- Thread-topic: The control problem
Dear all,
I encountered a strange thing. I used a boiler to provide the hot water to the heating coil in the winter to ensure that the output air temperature should be 14 C. The setpoint of the boiler is that the output water should be 80 C. However, when I do the simulation, I got an error report as:
-------------------------------------------------------------------------------------------------------------
** Severe ** FindRootSimpleController: Controller error for controller = "FAU_1FLOOR AHU HEATING COIL CONTROLLER"
** ~~~ ** Environment=ENNSMARTBUILDING, at Simulation time=12/15 00:00 - 00:30
** ~~~ ** Controller function is inconsistent with user specified controller action = Normal action
** ~~~ ** Actuator will be set to maximum action
** ~~~ ** Controller control type=Temperature
** ~~~ ** Controller temperature setpoint = 14.00 [C]
** ~~~ ** Controller sensed temperature = 13.38 [C]
** ~~~ ** Controller actuator mass flow rate set to 1.39 [kg/s]
** ~~~ ** Controller actuator temperature = 11.71 [C]
** ~~~ ** Note: Chilled water coils should be reverse action and the entering chilled
** ~~~ ** water temperature (controller actuator temperature) should be below the setpoint temperature
** ~~~ ** Note: Hot water coils should be normal action and the entering hot
** ~~~ ** water temperature (controller actuator temperature) should be above the setpoint temperature
-------------------------------------------------------------------------------------------------------------
You can see that the setpoint is 14 C, and the hot water temperature is just 11.71 C. Therefore, the air temperature cannot increase because the water temperature is lower than the air temperature. But it is strange because the water temperature should be 80 C since it comes from the boiler, rather than 11.71 C. I do not know why this thing happened. Can you give me some suggestions? Thank you.
----------------------------------------
Best Regards
Ying Yan
Graduate Student
Electrical & Computer Engineering
School of Engineering
University of Connecticut
__._,_.___
Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=30949/stime=1387397195>
Your email settings: Individual Email|Traditional
<http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmZjE0cGJoBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzODczOTcxOTU->Change settings via the Web (Yahoo! ID required)
Change settings via email: <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email Delivery: Digest>Switch delivery to Daily Digest | Switch to Fully Featured
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkdmVldnRoBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzg3Mzk3MTk1>Visit Your Group | <http://info.yahoo.com/legal/us/yahoo/utos/terms/> Yahoo! Groups Terms of Use | <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> Unsubscribe
__,_._,___