[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] The control problem
Dear Ying Yan,
I suggest comparing your IDF with one of the example files that include a boiler and a heating coil to see how to enable the boiler.
Phil
On 12/18/2013 1:25 PM, Yan, Ying wrote:
> Dear Phil,
> More information. As you said, I tried to check whether the boiler is shutting down. But I found that the boiler has no schedule item that can be used to control it, and I did not use the EMS to shut down the boiler. I do not know why the mass flow rate of the boiler is so low.
>
> ----------------------------------------
Best Regards
> Ying Yan
> Graduate Student
Electrical & Computer Engineering
School of Engineering
University of Connecticut
From: <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>EnergyPlus_Support@xxxxxxxxxxxxxxx [<mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>EnergyPlus_Support@xxxxxxxxxxxxxxx] on behalf of Yan, Ying [<mailto:yiy11005@xxxxxxxxxxxxxx>yiy11005@xxxxxxxxxxxxxx]
> Sent: Wednesday, December 18, 2013 4:17 PM
> To: Philip Haves; <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: RE: [EnergyPlus_Support] The control problem
>
> Dear Phil,
> Thank you so much for your help. I checked the outlet node of the boiler, the information is like
> ------------------------------
BOILER OUTLET NODE:System Node Temperature [C](Hourly): 80 (correct)
BOILER OUTLET NODE:System Node Mass Flow Rate [kg/s](Hourly): 0.0010233 (seems the boiler is shutting down.)
------------------------------
> The information of the heating coil:
------------------------------
FAU_1FLOOR SUPPLY SIDE INLET:System Node Temperature [C](Hourly): 13.00310 (This should be 80. Maybe it is because the boiler shuts down.)
FAU_1FLOOR SUPPLY SIDE INLET:System Node Mass Flow Rate [kg/s](Hourly): 0.554955 (This is strange since the boiler provides the hot water to several heating coil. The mass flow rate of the boiler should be greater than the mass flow rate of the heating coil. However, the opposite is true.)
------------------------------
> Can you give me some suggestions about this phenomenon? Thank you very much.
> ----------------------------------------
Best Regards
> Ying Yan
> Graduate Student
Electrical & Computer Engineering
School of Engineering
University of Connecticut
From: Philip Haves [<mailto:phaves@xxxxxxx>phaves@xxxxxxx]
> Sent: Wednesday, December 18, 2013 3:35 PM
> To: <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>EnergyPlus_Support@xxxxxxxxxxxxxxx
> Cc: Yan, Ying
> Subject: Re: [EnergyPlus_Support] The control problem
>
> Dear Ying Yan,
>
> Check that you actually have water through the coil and through the boiler, using report variables for the actual flow. Then check that the boiler is enabled - it may be scheduled off.
>
> Hope this helps,
>
> Phil
>
> On 12/18/2013 12:06 PM, Yan, Ying wrote:
>> Dear all,
>> I encountered a strange thing. I used a boiler to provide the hot water to the heating coil in the winter to ensure that the output air temperature should be 14 C. The setpoint of the boiler is that the output water should be 80 C. However, when I do the simulation, I got an error report as:
>> -------------------------------------------------------------------------------------------------------------
** Severe ** FindRootSimpleController: Controller error for controller = "FAU_1FLOOR AHU HEATING COIL CONTROLLER"
** ~~~ ** Environment=ENNSMARTBUILDING, at Simulation time=12/15 00:00 - 00:30
** ~~~ ** Controller function is inconsistent with user specified controller action = Normal action
** ~~~ ** Actuator will be set to maximum action
** ~~~ ** Controller control type=Temperature
** ~~~ ** Controller temperature setpoint = 14.00 [C]
** ~~~ ** Controller sensed temperature = 13.38 [C]
** ~~~ ** Controller actuator mass flow rate set to 1.39 [kg/s]
** ~~~ ** Controller actuator temperature = 11.71 [C]
** ~~~ ** Note: Chilled water coils should be reverse action and the entering chilled
** ~~~ ** water temperature (controller actuator temperature) should be below the setpoint temperature
** ~~~ ** Note: Hot water coils should be normal action and the entering hot
** ~~~ ** water temperature (controller actuator temperature) should be above the setpoint temperature
-------------------------------------------------------------------------------------------------------------
You can see that the setpoint is 14 C, and the hot water temperature is just 11.71 C. Therefore, the air temperature cannot increase because the water temperature is lower than the air temperature. But it is strange because the water temperature should be 80 C since it comes from the boiler, rather than 11.71 C. I do not know why this thing happened. Can you give me some suggestions? Thank you.
>> ----------------------------------------
Best Regards
>> Ying Yan
>> Graduate Student
Electrical & Computer Engineering
School of Engineering
University of Connecticut
> --
Philip Haves
Leader, Simulation Research Group
Lawrence Berkeley National Laboratory
One Cyclotron Road, MS 90R3145
Berkeley, CA 94720-8134
(510) 486 6512 (office)
(510) 486 4089 (fax)
__._,_.___
Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=30953/stime=1387403398>
Your email settings: Individual Email|Traditional
<http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmMnVzZTBsBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzODc0MDMzOTg->Change settings via the Web (Yahoo! ID required)
Change settings via email: <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email Delivery: Digest>Switch delivery to Daily Digest | Switch to Fully Featured
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkbDRiOHI1BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzg3NDAzMzk4>Visit Your Group | <http://info.yahoo.com/legal/us/yahoo/utos/terms/> Yahoo! Groups Terms of Use | <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> Unsubscribe
__,_._,___