[EnergyPlus_Support] Re: Heating Coil and Cooling Coil are running simultaneously!?!?





Once expanded:

You have to use a "Cooling type Setpointmanager" with Min Temp=11 and Max Temp=99 (one of those: SetpointManager:SingleZone:Cooling, SetpointManager:MultiZone:Cooling:Average, SetpointManager:Warmest or SetpointManager:WarmestTemperatureFlow) in the "XXX_VAVSYS Supply Fan Outlet" node and a "Heating type Setpointmanager" with Min Temp=0 and MaxTemp=33 (SetpointManager:SingleZone:Heating, SetpointManager:MultiZone:Cooling:Heating) in the "XXX_VAVSYS Supply Path Inlet" node.

Then verify that you have two SetpointManager:MixedAir:

One for  the cooling water coil with:

Reference Setpoint Node Name: XXX_VAVSYS Supply Fan Outlet
Fan Inlet Node Name: XXX_VAVSYS Heating Coil Outlet
Faon Outlet Node Name: XXX_VAVSYS Supply Fan Outlet
Setpoint Node: XXX_VAVSYS Mixed Air Nodes

One for the heating water coil with:

Reference Setpoint Node Name: XXX_VAVSYS Supply Path Inlet
Fan Inlet Node Name: XXX_VAVSYS Heating Coil Outlet
Faon Outlet Node Name: XXX_VAVSYS Supply Fan Outlet
Setpoint Node: XXX_VAVSYS Heating Coil Outlet

Regards,


_______________________________

Germán Campos

Aurea Consulting  


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___