[EnergyPlus_Support] Re: Heating Coil and Cooling Coil are running simultaneously!?!?



Thank you very much. I will try this and provide feedback.

EnergyPlus_Support@xxxxxxxxxxxxxxx, Germán Campos <ecoeficiente@...> wrote:
>
> Once expanded:
> 
> You have to use a "Cooling type Setpointmanager" with Min Temp=11 and Max
> Temp=99 (one of those: SetpointManager:SingleZone:Cooling,
> SetpointManager:MultiZone:Cooling:Average, SetpointManager:Warmest or
> SetpointManager:WarmestTemperatureFlow) in the "XXX_VAVSYS Supply Fan
> Outlet" node and a "Heating type Setpointmanager" with Min Temp=0 and
> MaxTemp=33 (SetpointManager:SingleZone:Heating,
> SetpointManager:MultiZone:Cooling:Heating)
> in the "XXX_VAVSYS Supply Path Inlet" node.
> 
> Then verify that you have two SetpointManager:MixedAir:
> 
> One for  the cooling water coil with:
> 
> Reference Setpoint Node Name: XXX_VAVSYS Supply Fan Outlet
> Fan Inlet Node Name: XXX_VAVSYS Heating Coil Outlet
> Faon Outlet Node Name: XXX_VAVSYS Supply Fan Outlet
> Setpoint Node: XXX_VAVSYS Mixed Air Nodes
> 
> One for the heating water coil with:
> 
> Reference Setpoint Node Name: XXX_VAVSYS Supply Path Inlet
> Fan Inlet Node Name: XXX_VAVSYS Heating Coil Outlet
> Faon Outlet Node Name: XXX_VAVSYS Supply Fan Outlet
> Setpoint Node: XXX_VAVSYS Heating Coil Outlet
> 
> Regards,
> 
> 
> _______________________________
> 
> Germán Campos
> 
> *Aurea Consulting  *
> www.ecoeficiente.es
> www.designbuilder.es
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo Groups is subject to:
    http://info.yahoo.com/legal/us/yahoo/utos/terms/