RE: [EnergyPlus_Support] Cubic Curve in variable speed pump





Dear Adrian,

Lacking actual data from the pump and VSD supplier, use the ASHRAE 90.1-recommended coefficients:

E+ Format

 

 

90.1 VSD

C1

0.203671

C2

-0.827077

C3

1.181191

C4

0.442055

 

 

James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of adrianchong85@xxxxxxxxx
Sent: Wednesday, January 08, 2014 2:46 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Cubic Curve in variable speed pump

 

 

Dear EnergyPlus Users,

 

I'm trying to model a variable speed pump in eplus and one of the inputs required are coefficients to the cubic curve 

FractionFullLoadPower =C1   +  C2PLR + C3PLR2 + C4PLR3 

 

where PLR = VolFlowRate / NomVolFlowRate 

 

My question is how do we go about obtaining these coefficients? Is it correct to assume a constant head (maybe assume nameplate head) and using nameplate Power and Flow Rate as nominal data, obtain FractionFullLoadPower and PLR by reading off the Pump's performance curves (at different points with the same head) and then use least squares regression to get the coefficients.

 



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___