Fred is right. On the supply side, think of tree branching...as soon as two branches come together again, that is not allowed. So multiple outlets from a zonesplitter (badly named supply duct splitter) can't thereafter feed into a common plenumn. A plenumn is also a splitter and can feed multiple zones. Two plenums can't feed the same zone. On the return side, it's the same but backwards like stream tributeries feeding into a river. Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity) i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.