|
Because it has an "in-built" controller, as you say, adding a setpointmanager or a controller for this object has no effect (incidently this is also true for unitary units). For reheat coils, it is important to know that they operating both when the zone needs cooling and when it needs heating. When the zone needs cooling, the supply air temp is equal to the zone heating setpoint. That way unpleasant supply temp is avoided whilst avoiding as much energy waste as possible. Unfortunately, unless you specify the coil availability otherwise. So if the coil is scheduled always on, this behaviour is seen the whole year long. Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity) i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |