Re: [EnergyPlus_Support] EMS error ** Severe ** Invalid Output:Variable or Output:Meter Index Key Name





I tried, but I'm obtaining the same result.



On Wednesday, January 29, 2014 3:14 PM, Richard Raustad <RRaustad@xxxxxxxxxxxx> wrote:
 
Use a detailed reporting frequency when looking at actual output.

Output:Variable,
    *,                       !- Key Value
    schedule value,          !- Variable Name
    Detailed,                !- Reporting Frequency
    schedprova;              !- Schedule Name


On 1/29/2014 8:57 AM, Marco Aldegheri wrote:
Hello,
unfortunately I have another (probably) newbie doubt... I hope that it is one of the last... :)

I created a schedule to enable or disable  the opening program. The schedule I'm speaking about is called in the filei"schedprova".

I don't know why but, apparently it seems to be written in a correct form but, when I plot its value vs time, I see that his behaviour is not like the implemented one. I'm plotting it in timestep but i see it moving only between 0,5 and 1...  Maybe I committed a mistake somewhere or maybe there is something that I haven't understood yet!

Thanks, again
Marco



-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 50 Years




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___