Matthew, 1. A mon avis, (in my opinion) a fan wall has no inherent efficiency advantages beyond a potentially higher fan mechanical efficiency than your current fan. If you currently have a forward curved fan and will convert to an airfoil fan wall, there’s probably a significant boost for mechanical efficiency. My experience says that only rarely does a forward curved fan’s efficiency exceed about 50%. For that matter, BI and AF fans are often not too much better L. 2. I designed a dual fan / dual duct system long ago and am forgetting some of the details. Nonetheless, the main benefit was that you could use two independent air handlers (1 for hot air, 1 for cold air) and therefore have minimal mixing and maximum turndown for heating and cooling. I have not modeled such in E+, but there are several example files of dual duct systems. You may be able to adapt one for dual fan� James V Dirkes II, PE, BEMP, LEED AP From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of matthew.sverre.anderson@xxxxxxxxx Hey everybody, __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |