RE: [EnergyPlus_Support] eQUEST vs EnergyPlus: Fan Energy Consumption




Your data indicates that there are probably several discrepancies because the pattern varies.

·         Are you aware that E+ ?fan efficiency? is actually (fan mechanical efficiency x motor efficiency)? (I don?t know how eQuest calculates?)

·         Clearly the eQuest fan is running non-stop, while the E+ fan is not.  There?s a schedule affecting them which is different?

o   E+ will not cycle its fan during unoccupied periods unless you use a AvailabilityManager:NightCycle

o   E+ cycles at night with a specific delta T variation from setpoint and for a minimum time period. These are specified in the AvailabilityManager mentioned above.







James V Dirkes II, PE, BEMP, LEED AP
__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31287/stime=1392308388>

<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJlaWRqYzhqBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5MjMwODM4OA-->Visit Your Group
* <http://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJmcDF2aHB0BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTIzMDgzODg-?o=6>New Members 6
<http://groups.yahoo.com/;_ylc=X3oDMTJkNmhqMDM0BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzkyMzA4Mzg4><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <http://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <http://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___