|
Simge, Looking at your plots, it seems that the eQUEST fan is simply larger by 40% or so. Are you letting the programs autosize the equipment, and did you use any sizing-factors or sizing-ratios in the runs? I would just take the larger capacity of the two runs, and use that for both runs, which should take care of the discrepancy. Other observations: 1. eQUEST CYCLE-ON-ANY seems to keep the fans on the entire hour, whereas EnergyPlus seems to cycling them on only when the HVAC is on. 2. You seem to have daylight savings in the eQUEST, but not in the EnergyPlus model. Joe Joe Huang White Box Technologies, Inc. 346 Rheem Blvd., Suite 108D Moraga CA 94556 yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx http://weather.whiteboxtechnologies.com for simulation-ready weather data (o) (925)388-0265 (c) (510)928-2683 "building energy simulations at your fingertips" On 2/13/2014 8:05 AM, Simge Andolsun wrote:
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |