Re: [EnergyPlus_Support] C-Factor for Underground Walls and F-Factor for Slab-on-Ground Floors (ASHRAE 90.1, Title 24 etc)



Thank you very much, Jean. Very detailed and useful reply.
However, I still cannot come out of this maze, I need a straightforward confirmation to my statements below.
(A) In EnergyPlus, we can definitely use F-factor, C-factor objects and do not need to care about layered construction at all (E+ does, as you said: f-factor c-factor objects create layered constructions internally, which has also been confirmed by EneryPlus support staff).
(B) As an alternative way, we can also use layered constructions for F-factor (as an example) with the procedures as (1) read F-factor value from Tables 5.5-1 through 5.5-8 depending on climate zone and space conditioning category; (2) calculate equivalent U-factor based on the ground floor area and exposed perimeter; (3) create layered construction (normally a concrete plus an insulation) to meet U-factor calculated by step 2; (4) set outside boundary condition to ground (not FCfactorMethod then). For this setting, we just forget about F-factor (just used as an input to calculate U-factor), but use conventional U-factor instead.
Best regards,
Sean



__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31311/stime=1392724788>

<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJlcmYxZDhlBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5MjcyNDc4OA-->Visit Your Group
* <http://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJmN2Q0c2hnBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTI3MjQ3ODg-?o=6>New Members 9
<http://groups.yahoo.com/;_ylc=X3oDMTJkM2MzM2JtBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzkyNzI0Nzg4><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <http://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <http://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___