You have it! The key with (B) and energyplus is to understand that as long as you correctly reverse engineer the physical construction, the physics take care of themselves and you (should) hit the correct rating as per the rating method.
2014-02-18 12:59 GMT+01:00 <<mailto:seanking.1970@xxxxxxxxxxx>seanking.1970@xxxxxxxxxxx>:
> Â
Thank you very much, Jean. Very detailed and useful reply.
> However, I still cannot come out of this maze, I need a straightforward confirmation to my statements below.
> (A) In EnergyPlus, we can definitely use F-factor, C-factor objects and do not need to care about layered construction at all (E+ does, as you said:Â f-factor c-factor objects create layered constructions internally, which has also been confirmed by EneryPlus support staff).
> (B) As an alternative way, we can also use layered constructions for F-factor (as an example) with the procedures as (1) read F-factor value from Tables 5.5-1 through 5.5-8 depending on climate zone and space conditioning category; (2) calculate equivalent U-factor based on the ground floor area and exposed perimeter; (3) create layered construction (normally a concrete plus an insulation) to meet U-factor calculated by step 2; (4) set outside boundary condition to ground (not FCfactorMethod then). For this setting, we just forget about F-factor (just used as an input to calculate U-factor), but use conventional U-factor instead.
> Best regards,
> Sean
>
>
__._,_.___
Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31312/stime=1392728272>
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJlaGdkcG5hBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5MjcyODI3Mg-->Visit Your Group
* <http://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJmNXBoN29mBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTI3MjgyNzI-?o=6>New Members 9
<http://groups.yahoo.com/;_ylc=X3oDMTJkcWttajU5BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzkyNzI4Mjcy><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <http://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <http://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___