Dear all,
I have noticed that no matter what SHGC value I enter in idf file, I always get a different value in the output, for example: I put 0.36 in idf editor, and for one simulation case I get the output to show 0.355 instead, and for another case I get 0.362, even if these two cases have only some u-values different for some constructions!
I am preparing a report that studies the effect of envelope on external heat gains, and half the building envelope is glass, this small difference in SHGC is changing the savings by too much!
I have tried changing the time step from 2 to 6 to increase accuracy, but it is all in vain!
I also noticed that when I reduced USI-values for glass (from 1.61 to 1.4) and for walls (from 0.24 to 0.215) EnergyPlus changed my SHGC from 0.355 to 0.362 (non of them is what I entered 0.36) and the savings in heat gains are reduced from 8% to 3% when using lower U-Values!!!
Please help!
Hisham.

__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31434/stime=1394017693>

<https://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJlcDE5MzduBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5NDAxNzY5Mw-->Visit Your Group
* <https://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJmZjQ4am9pBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTQwMTc2OTM-?o=6>New Members 8
<https://groups.yahoo.com/;_ylc=X3oDMTJkbWV1ZmsxBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzk0MDE3Njkz><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___