If you want more accuracy, you will have to use the complex fenestration inputs. The e+ simple glazing method reverse engineers a best fit complex glazing from your simple inputs. IMO the accuracy of the glazing is good. A SHGC difference of 0.07 between two real glazing assemblies is very small. However, 7% difference on solar gains is large. If you can't use the complex method, you could consider changing the glazed area slightly. Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity) i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.