[EnergyPlus_Support] COP of a chiller in operative conditions [1 Attachment]
- To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
- Subject: [EnergyPlus_Support] COP of a chiller in operative conditions [1 Attachment]
- From: <fpasserini.tn@xxxxxxxxx>
- Date: 11 Mar 2014 04:57:08 -0700
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Tue, 11 Mar 2014 05:57:21 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1394539038; bh=n7/1i3yJwUzPOfoNCbHPl2LuzoIPwVVXezyCXRPjv2M=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:X-Yahoo-Newman-Property:Reply-To:Content-Type; b=5SQ04u+VqvFTot1j+w8459JAJ0wqyIorHgYQso4TlqrZhefzuuJMFzW3p9ZpwmVGAz1IZaaoi9A49uKG7uWpceAs0VxRkaFdzsNlEvwd+CCASZoraVzkoSLSs0RMD1NsKOwe/SktlkQfOiZ8epOFWNOPIqiKFRiTTCXKeQaeBUc=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echoe; d=yahoogroups.com; b=DrhV8W/MI2T3abXoyA3WQJUSYSYRAkXGwatq1ebnlE4vP5KvEo/4wH11pXMYuyoJGe/9ekv0POCzHdB7Z9Ln6RyoUDxTqpMocGy7nDsZt+EM83n2rHPL9AmvtbdepRMkmwCEw7zWgI6OtCtbeX71pKu8Lb73+s39GkQ7Kbor/c0=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
Iâ??m using the object Chiller:Electric:EIR. If I understand correctly, the COP of a chiller in operative conditions is equal to
COP = COPreference / (EIRFT * EIRFPLR)
Isnâ??t it?
Chiller:Electric:EIR,
Chiller, !- Name
19700, !- Reference Capacity {W}
2.89, !- Reference COP {W/W}
18, !- Reference Leaving Chilled Water Temperature {C}
38, !- Reference Entering Condenser Fluid Temperature {C}
0.00092, !- Reference Chilled Water Flow Rate {m3/s}
autosize, !- Reference Condenser Fluid Flow Rate {m3/s}
Clivet CAPFT, !- Cooling Capacity Function of Temperature Curve Name
Clivet EIRFT, !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
const, !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
0.10, !- Minimum Part Load Ratio
1.00, !- Maximum Part Load Ratio
1.00, !- Optimum Part Load Ratio
0.20, !- Minimum Unloading Ratio
Chiller CHW Inlet Node, !- Chilled Water Inlet Node Name
Chiller CHW Outlet Node, !- Chilled Water Outlet Node Name
Chiller Outdoor Air Node,!- Condenser Inlet Node Name
, !- Condenser Outlet Node Name
AirCooled, !- Condenser Type
0.00, !- Condenser Fan Power Ratio {W/W}
1.00, !- Fraction of Compressor Electric Consumption Rejected by Condenser
2.00, !- Leaving Chilled Water Lower Temperature Limit {C}
LeavingSetpointModulated,!- Chiller Flow Mode
0.000000, !- Design Heat Recovery Water Flow Rate {m3/s}
, !- Heat Recovery Inlet Node Name
, !- Heat Recovery Outlet Node Name
1.00, !- Sizing Factor
0.00, !- Basin Heater Capacity {W/K}
2.00, !- Basin Heater Setpoint Temperature {C}
2; !- Basin Heater Operating Schedule Name
The EIRFPLR â??Constâ?? is constantly equal to 1:
Curve:Quadratic,
const, !- Name
1, !- Coefficient1 Constant
0, !- Coefficient2 x
0, !- Coefficient3 x**2
-100, !- Minimum Value of x
100, !- Maximum Value of x
, !- Minimum Curve Output
, !- Maximum Curve Output
Dimensionless, !- Input Unit Type for X
Dimensionless; !- Output Unit Type
If EIRFPLR = 1, then the COP of the chiller in operative conditions should be equal to
COP = COPreference / EIRFT
In the .xls file that I attach I have copied the values of â??Performance Curve Output Value CLIVET EIRFT []â?? and of â??Chiller COP CHILLER [W/W]â?? from the .eso file. Then I calculated the COPreference / EIRFT ratio. I would aspect that ratio is equal to the â??Chiller COP CHILLER [W/W]â??, but it is very different.
Best Regards
__._,_.___
<https://groups.yahoo.com/group/EnergyPlus_Support/attachments/folder/1513322207/item/list>View attachments on the web
Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31485/stime=1394539030>
<https://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJlaXAyZjJoBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5NDUzOTAzMA-->Visit Your Group
* <https://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJmaWNnMzc2BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTQ1MzkwMzA-?o=6>New Members 13
<https://groups.yahoo.com/;_ylc=X3oDMTJkZTA0OW42BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzk0NTM5MDMw><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___