[EnergyPlus_Support] Re: COP of a chiller in operative conditions
As EIR function of PLR now Iâ??m using the following one:
Curve:Quadratic,
ideal EIRFPLR, !- Name
0, !- Coefficient1 Constant
1, !- Coefficient2 x
0, !- Coefficient3 x**2
-100, !- Minimum Value of x
100, !- Maximum Value of x
, !- Minimum Curve Output
, !- Maximum Curve Output
Dimensionless, !- Input Unit Type for X
Dimensionless; !- Output Unit Type
As you see in the following picutre, now there is a good agreement between
COPreference / EIRFT
and
Chiller COP CHILLER [W/W]
Picture: <http://oi60.tinypic.com/2808v9v.jpg>http://oi60.tinypic.com/2808v9v.jpg
I read in the Input Output Reference that â??An ideal chiller with the same efficiency at all part-load ratioâ??s would use a performance curve that has a value of 0 when the part-load ratio equals 0â??.
__._,_.___
Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31487/stime=1394554649>
<https://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJlNWU4MGZvBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5NDU1NDY0OQ-->Visit Your Group
* <https://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJmM2dsanNzBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTQ1NTQ2NDk-?o=6>New Members 13
<https://groups.yahoo.com/;_ylc=X3oDMTJkYmZ2ZXQ5BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzk0NTU0NjQ5><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___