[EnergyPlus_Support] Re: COP of a chiller in operative conditions




Actually, Iâ??m pretty satisfied with the results that I get now (after I have changed the â??EIR function of PLRâ?? curve).

As EIRFT curve Iâ??m using the following one:



Curve:Biquadratic,

    Clivet EIRFT,            !- Name

    0.63035,                 !- Coefficient1 Constant

    -.01942,                 !- Coefficient2 x

    0.00024,                 !- Coefficient3 x**2

    0.00171,                 !- Coefficient4 y

    0.00034,                 !- Coefficient5 y**2

    0.00013,                 !- Coefficient6 x*y

    5.0,                     !- Minimum Value of x

    20,                      !- Maximum Value of x

    24.0,                    !- Minimum Value of y

    42;                      !- Maximum Value of y



Then the curve is constant when the outdoor temperature is lower than 24°C (Minimum Value of y), it isnâ??t always constant: <http://oi62.tinypic.com/308zjug.jpg>http://oi62.tinypic.com/308zjug.jpg

To calculate the parameters I interpolated some operating points that are in the datasheet of the heat pump.

Some graphs that I obtained from the output data:

COPc and outdoor air temperature: <http://oi60.tinypic.com/30rpmhe.jpg>http://oi60.tinypic.com/30rpmhe.jpg

COPc and chiller inlet temperature: <http://oi57.tinypic.com/w882zr.jpg>http://oi57.tinypic.com/w882zr.jpg

Trend of COPc and temperatures in 10 days: <http://oi60.tinypic.com/12549ja.jpg>http://oi60.tinypic.com/12549ja.jpg

Regards

__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31502/stime=1394623185>

<https://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJldmtoYm5xBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5NDYyMzE4NQ-->Visit Your Group
* <https://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJmcHVubTJpBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTQ2MjMxODU-?o=6>New Members 11
<https://groups.yahoo.com/;_ylc=X3oDMTJkY2N1dmg1BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzk0NjIzMTg1><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___