My understanding is that meter:custom works only for variables in
Joules. I learned this the hard way a few versions of EPlus ago. I do
not think that has changed.
Ery
On Thu, 13 Mar 2014, m.aldegheri@xxxxxxxxx wrote:
> Dear forum,
>
> I'm using meter:custom to calculate the sum (timestep per timestep) of the ach infiltration of a model. This model has many zones and i would like to read whole data for them. I created variables and meters in this way:
>
> !- =========== ALL OBJECTS IN CLASS: OUTPUT:VARIABLE ===========
>
> Output:Variable,
> *, !- Key Value
> AFN Zone Infiltration Air Volume, !- Variable Name
> Hourly; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> AFN Zone Infiltration Air Volume, !- Variable Name
> Daily; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> AFN Zone Infiltration Air Volume, !- Variable Name
> Monthly; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> AFN Zone Infiltration Air Volume, !- Variable Name
> Annual; !- Reporting Frequency
>
>
> !- =========== ALL OBJECTS IN CLASS: OUTPUT:METER ===========
>
> Output:Meter,
> Volume infiltrazione totale, !- Name
> Hourly; !- Reporting Frequency
>
> Output:Meter,
> Volume infiltrazione totale, !- Name
> Daily; !- Reporting Frequency
>
> Output:Meter,
> Volume infiltrazione totale, !- Name
> Monthly; !- Reporting Frequency
>
> Output:Meter,
> Volume infiltrazione totale, !- Name
> Annual; !- Reporting Frequency
>
>
> !- =========== ALL OBJECTS IN CLASS: OUTPUT:METER:METERFILEONLY ===========
>
> Output:Meter:MeterFileOnly,
> Volume infiltrazione totale, !- Name
> Hourly; !- Reporting Frequency
>
> Output:Meter:MeterFileOnly,
> Volume infiltrazione totale, !- Name
> Monthly; !- Reporting Frequency
>
> Output:Meter:MeterFileOnly,
> Volume infiltrazione totale, !- Name
> Daily; !- Reporting Frequency
>
> Output:Meter:MeterFileOnly,
> Volume infiltrazione totale, !- Name
> Annual; !- Reporting Frequency
>
>
> !- =========== ALL OBJECTS IN CLASS: METER:CUSTOM ===========
>
> Meter:Custom,
> Volume infiltrazione totale, !- Name
> Generic, !- Fuel Type
> *, !- Key Name 1
> AFN Zone Infiltration Air Volume; !- Output Variable or Meter Name 1
>
>
>
>
>
> (In this model there are 2 zones, and it's an example)
> The output variable maybe are useless, but using the meters I can't see the data in the sql file. How can I see the data?
>
> Marco
>
> p.s:
> Also using the following text it doesn't work.
>
> Meter:Custom,
> Volume infiltrazione totale, !- Name
> Generic, !- Fuel Type
> Block1:Zone1, !- Key Name 1
> AFN Zone Infiltration Air Volume; !- Output Variable or Meter Name 1
> Block2:Zone1, !- Key Name 2
> AFN Zone Infiltration Air Volume; !- Output Variable or Meter Name 2
> !-Generator IDFEditor 1.44
> !-Option SortedOrder
>
> !-NOTE: All comments with '!-' are ignored by the IDFEditor and are generated automatically.
> !- Use '!' comments if they need to be retained when using the IDFEditor.
>
>
> !- =========== ALL OBJECTS IN CLASS: VERSION ===========
>
> ! File generated by DesignBuilder - 3.2.0.073 1/4/2014 - 5:38:22 AM
> ! Source file: C:\Documents and Settings\Marco\Local Settings\Temp\Untitled 1.dsb
> Version,
> 8.1; !- Version Identifier
>
>
> !- =========== ALL OBJECTS IN CLASS: SIMULATIONCONTROL ===========
>
> SimulationControl,
> Yes, !- Do Zone Sizing Calculation
> Yes, !- Do System Sizing Calculation
> No, !- Do Plant Sizing Calculation
> No, !- Run Simulation for Sizing Periods
> Yes; !- Run Simulation for Weather File Run Periods
>
>
> !- =========== ALL OBJECTS IN CLASS: BUILDING ===========
>
> Building,
> Building, !- Name
> 0, !- North Axis {deg}
> Suburbs, !- Terrain
> 0.04, !- Loads Convergence Tolerance Value
> 0.4, !- Temperature Convergence Tolerance Value {deltaC}
> FullExterior, !- Solar Distribution
> 25, !- Maximum Number of Warmup Days
> 6; !- Minimum Number of Warmup Days
>
>
> !- =========== ALL OBJECTS IN CLASS: SHADOWCALCULATION ===========
>
> ShadowCalculation,
> AverageOverDaysInFrequency, !- Calculation Method
> 20, !- Calculation Frequency
> 15000, !- Maximum Figures in Shadow Overlap Calculations
> SutherlandHodgman, !- Polygon Clipping Algorithm
> SimpleSkyDiffuseModeling;!- Sky Diffuse Modeling Algorithm
>
>
> !- =========== ALL OBJECTS IN CLASS: SURFACECONVECTIONALGORITHM:INSIDE ===========
>
> SurfaceConvectionAlgorithm:Inside,
> TARP; !- Algorithm
>
>
> !- =========== ALL OBJECTS IN CLASS: SURFACECONVECTIONALGORITHM:OUTSIDE ===========
>
> SurfaceConvectionAlgorithm:Outside,
> DOE-2; !- Algorithm
>
>
> !- =========== ALL OBJECTS IN CLASS: HEATBALANCEALGORITHM ===========
>
> HeatBalanceAlgorithm,
> ConductionTransferFunction, !- Algorithm
> 2000; !- Surface Temperature Upper Limit {C}
>
>
> !- =========== ALL OBJECTS IN CLASS: ZONECAPACITANCEMULTIPLIER:RESEARCHSPECIAL ===========
>
> ZoneCapacitanceMultiplier:ResearchSpecial,
> 1.0, !- Temperature Capacity Multiplier
> 1.0, !- Humidity Capacity Multiplier
> 1.0, !- Carbon Dioxide Capacity Multiplier
> 1.0; !- Generic Contaminant Capacity Multiplier
>
>
> !- =========== ALL OBJECTS IN CLASS: TIMESTEP ===========
>
> Timestep,
> 6; !- Number of Timesteps per Hour
>
>
> !- =========== ALL OBJECTS IN CLASS: CONVERGENCELIMITS ===========
>
> ConvergenceLimits,
> 1, !- Minimum System Timestep {minutes}
> 20; !- Maximum HVAC Iterations
>
>
> !- =========== ALL OBJECTS IN CLASS: PROGRAMCONTROL ===========
>
> ProgramControl,
> 1; !- Number of Threads Allowed
>
>
> !- =========== ALL OBJECTS IN CLASS: SITE:LOCATION ===========
>
> ! Hourly weather file: C:\Documents and Settings\All Users\Application Data\DesignBuilder\Weather Data\GBR_LONDON_GATWICK_IWEC.epw
> Site:Location,
> Untitled, !- Name
> 51.15, !- Latitude {deg}
> -0.18, !- Longitude {deg}
> 0, !- Time Zone {hr}
> 62; !- Elevation {m}
>
>
> !- =========== ALL OBJECTS IN CLASS: SIZINGPERIOD:DESIGNDAY ===========
>
> SizingPeriod:DesignDay,
> Summer Design Day in Untitled, !- Name
> 7, !- Month
> 15, !- Day of Month
> SummerDesignDay, !- Day Type
> 27, !- Maximum Dry-Bulb Temperature {C}
> 9.7, !- Daily Dry-Bulb Temperature Range {deltaC}
> , !- Dry-Bulb Temperature Range Modifier Type
> , !- Dry-Bulb Temperature Range Modifier Day Schedule Name
> WetBulb, !- Humidity Condition Type
> 18.6, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
> , !- Humidity Condition Day Schedule Name
> , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
> , !- Enthalpy at Maximum Dry-Bulb {J/kg}
> , !- Daily Wet-Bulb Temperature Range {deltaC}
> 100582.4, !- Barometric Pressure {Pa}
> 0, !- Wind Speed {m/s}
> 0, !- Wind Direction {deg}
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 1, !- Daylight Saving Time Indicator
> , !- Solar Model Indicator
> , !- Beam Solar Day Schedule Name
> , !- Diffuse Solar Day Schedule Name
> , !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
> , !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
> 0.98; !- Sky Clearness
>
> SizingPeriod:DesignDay,
> Winter Design Day in Untitled, !- Name
> 1, !- Month
> 15, !- Day of Month
> WinterDesignDay, !- Day Type
> -4.8, !- Maximum Dry-Bulb Temperature {C}
> 0, !- Daily Dry-Bulb Temperature Range {deltaC}
> , !- Dry-Bulb Temperature Range Modifier Type
> , !- Dry-Bulb Temperature Range Modifier Day Schedule Name
> WetBulb, !- Humidity Condition Type
> -4.8, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
> , !- Humidity Condition Day Schedule Name
> , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
> , !- Enthalpy at Maximum Dry-Bulb {J/kg}
> , !- Daily Wet-Bulb Temperature Range {deltaC}
> 100582.4, !- Barometric Pressure {Pa}
> 12.7, !- Wind Speed {m/s}
> 0, !- Wind Direction {deg}
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 0, !- Daylight Saving Time Indicator
> , !- Solar Model Indicator
> , !- Beam Solar Day Schedule Name
> , !- Diffuse Solar Day Schedule Name
> , !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
> , !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
> 0; !- Sky Clearness
>
>
> !- =========== ALL OBJECTS IN CLASS: RUNPERIOD ===========
>
> RunPeriod,
> Untitled, !- Name
> 1, !- Begin Month
> 1, !- Begin Day of Month
> 12, !- End Month
> 31, !- End Day of Month
> UseWeatherFile, !- Day of Week for Start Day
> No, !- Use Weather File Holidays and Special Days
> No, !- Use Weather File Daylight Saving Period
> Yes, !- Apply Weekend Holiday Rule
> Yes, !- Use Weather File Rain Indicators
> Yes, !- Use Weather File Snow Indicators
> 1; !- Number of Times Runperiod to be Repeated
>
>
> !- =========== ALL OBJECTS IN CLASS: RUNPERIODCONTROL:DAYLIGHTSAVINGTIME ===========
>
> RunPeriodControl:DaylightSavingTime,
> Last Sunday in March, !- Start Date
> Last Sunday in October; !- End Date
>
>
> !- =========== ALL OBJECTS IN CLASS: SITE:GROUNDTEMPERATURE:BUILDINGSURFACE ===========
>
> Site:GroundTemperature:BuildingSurface,
> 18, !- January Ground Temperature {C}
> 18, !- February Ground Temperature {C}
> 18, !- March Ground Temperature {C}
> 18, !- April Ground Temperature {C}
> 18, !- May Ground Temperature {C}
> 18, !- June Ground Temperature {C}
> 18, !- July Ground Temperature {C}
> 18, !- August Ground Temperature {C}
> 18, !- September Ground Temperature {C}
> 18, !- October Ground Temperature {C}
> 18, !- November Ground Temperature {C}
> 18; !- December Ground Temperature {C}
>
>
> !- =========== ALL OBJECTS IN CLASS: SITE:GROUNDTEMPERATURE:SHALLOW ===========
>
> Site:GroundTemperature:Shallow,
> 14, !- January Surface Ground Temperature {C}
> 14, !- February Surface Ground Temperature {C}
> 14, !- March Surface Ground Temperature {C}
> 14, !- April Surface Ground Temperature {C}
> 14, !- May Surface Ground Temperature {C}
> 14, !- June Surface Ground Temperature {C}
> 14, !- July Surface Ground Temperature {C}
> 14, !- August Surface Ground Temperature {C}
> 14, !- September Surface Ground Temperature {C}
> 14, !- October Surface Ground Temperature {C}
> 14, !- November Surface Ground Temperature {C}
> 14; !- December Surface Ground Temperature {C}
>
>
> !- =========== ALL OBJECTS IN CLASS: SITE:GROUNDTEMPERATURE:DEEP ===========
>
> Site:GroundTemperature:Deep,
> 14, !- January Deep Ground Temperature {C}
> 14, !- February Deep Ground Temperature {C}
> 14, !- March Deep Ground Temperature {C}
> 14, !- April Deep Ground Temperature {C}
> 14, !- May Deep Ground Temperature {C}
> 14, !- June Deep Ground Temperature {C}
> 14, !- July Deep Ground Temperature {C}
> 14, !- August Deep Ground Temperature {C}
> 14, !- September Deep Ground Temperature {C}
> 14, !- October Deep Ground Temperature {C}
> 14, !- November Deep Ground Temperature {C}
> 14; !- December Deep Ground Temperature {C}
>
>
> !- =========== ALL OBJECTS IN CLASS: SITE:GROUNDREFLECTANCE ===========
>
> Site:GroundReflectance,
> 0.2, !- January Ground Reflectance {dimensionless}
> 0.2, !- February Ground Reflectance {dimensionless}
> 0.2, !- March Ground Reflectance {dimensionless}
> 0.2, !- April Ground Reflectance {dimensionless}
> 0.2, !- May Ground Reflectance {dimensionless}
> 0.2, !- June Ground Reflectance {dimensionless}
> 0.2, !- July Ground Reflectance {dimensionless}
> 0.2, !- August Ground Reflectance {dimensionless}
> 0.2, !- September Ground Reflectance {dimensionless}
> 0.2, !- October Ground Reflectance {dimensionless}
> 0.2, !- November Ground Reflectance {dimensionless}
> 0.2; !- December Ground Reflectance {dimensionless}
>
>
> !- =========== ALL OBJECTS IN CLASS: SITE:GROUNDREFLECTANCE:SNOWMODIFIER ===========
>
> Site:GroundReflectance:SnowModifier,
> 1.0, !- Ground Reflected Solar Modifier
> 1.0; !- Daylighting Ground Reflected Solar Modifier
>
>
> !- =========== ALL OBJECTS IN CLASS: SCHEDULETYPELIMITS ===========
>
> ScheduleTypeLimits,
> Any Number; !- Name
>
> ScheduleTypeLimits,
> Fraction, !- Name
> 0.0, !- Lower Limit Value
> 1.0, !- Upper Limit Value
> CONTINUOUS; !- Numeric Type
>
> ScheduleTypeLimits,
> Temperature, !- Name
> -60, !- Lower Limit Value
> 200, !- Upper Limit Value
> CONTINUOUS; !- Numeric Type
>
> ScheduleTypeLimits,
> Control Type, !- Name
> 0, !- Lower Limit Value
> 4, !- Upper Limit Value
> DISCRETE; !- Numeric Type
>
> ScheduleTypeLimits,
> On/Off, !- Name
> 0, !- Lower Limit Value
> 1, !- Upper Limit Value
> DISCRETE; !- Numeric Type
>
>
> !- =========== ALL OBJECTS IN CLASS: SCHEDULE:DAY:HOURLY ===========
>
> ! off heating day
> Schedule:Day:Hourly,
> 0, !- Name
> Any Number, !- Schedule Type Limits Name
> 0, !- Hour 1
> 0, !- Hour 2
> 0, !- Hour 3
> 0, !- Hour 4
> 0, !- Hour 5
> 0, !- Hour 6
> 0, !- Hour 7
> 0, !- Hour 8
> 0, !- Hour 9
> 0, !- Hour 10
> 0, !- Hour 11
> 0, !- Hour 12
> 0, !- Hour 13
> 0, !- Hour 14
> 0, !- Hour 15
> 0, !- Hour 16
> 0, !- Hour 17
> 0, !- Hour 18
> 0, !- Hour 19
> 0, !- Hour 20
> 0, !- Hour 21
> 0, !- Hour 22
> 0, !- Hour 23
> 0; !- Hour 24
>
> ! off cooling day
> Schedule:Day:Hourly,
> 50, !- Name
> Any Number, !- Schedule Type Limits Name
> 50, !- Hour 1
> 50, !- Hour 2
> 50, !- Hour 3
> 50, !- Hour 4
> 50, !- Hour 5
> 50, !- Hour 6
> 50, !- Hour 7
> 50, !- Hour 8
> 50, !- Hour 9
> 50, !- Hour 10
> 50, !- Hour 11
> 50, !- Hour 12
> 50, !- Hour 13
> 50, !- Hour 14
> 50, !- Hour 15
> 50, !- Hour 16
> 50, !- Hour 17
> 50, !- Hour 18
> 50, !- Hour 19
> 50, !- Hour 20
> 50, !- Hour 21
> 50, !- Hour 22
> 50, !- Hour 23
> 50; !- Hour 24
>
> ! used in seasonal schedules
> Schedule:Day:Hourly,
> Off, !- Name
> Fraction, !- Schedule Type Limits Name
> 0, !- Hour 1
> 0, !- Hour 2
> 0, !- Hour 3
> 0, !- Hour 4
> 0, !- Hour 5
> 0, !- Hour 6
> 0, !- Hour 7
> 0, !- Hour 8
> 0, !- Hour 9
> 0, !- Hour 10
> 0, !- Hour 11
> 0, !- Hour 12
> 0, !- Hour 13
> 0, !- Hour 14
> 0, !- Hour 15
> 0, !- Hour 16
> 0, !- Hour 17
> 0, !- Hour 18
> 0, !- Hour 19
> 0, !- Hour 20
> 0, !- Hour 21
> 0, !- Hour 22
> 0, !- Hour 23
> 0; !- Hour 24
>
> ! -------------------- Control type schedules (for heating & cooling) ----------------------
> Schedule:Day:Hourly,
> Summer Control Type Day Sch, !- Name
> Control Type, !- Schedule Type Limits Name
> 4, !- Hour 1
> 4, !- Hour 2
> 4, !- Hour 3
> 4, !- Hour 4
> 4, !- Hour 5
> 4, !- Hour 6
> 4, !- Hour 7
> 4, !- Hour 8
> 4, !- Hour 9
> 4, !- Hour 10
> 4, !- Hour 11
> 4, !- Hour 12
> 4, !- Hour 13
> 4, !- Hour 14
> 4, !- Hour 15
> 4, !- Hour 16
> 4, !- Hour 17
> 4, !- Hour 18
> 4, !- Hour 19
> 4, !- Hour 20
> 4, !- Hour 21
> 4, !- Hour 22
> 4, !- Hour 23
> 4; !- Hour 24
>
> Schedule:Day:Hourly,
> Winter Control Type Day Sch, !- Name
> Control Type, !- Schedule Type Limits Name
> 4, !- Hour 1
> 4, !- Hour 2
> 4, !- Hour 3
> 4, !- Hour 4
> 4, !- Hour 5
> 4, !- Hour 6
> 4, !- Hour 7
> 4, !- Hour 8
> 4, !- Hour 9
> 4, !- Hour 10
> 4, !- Hour 11
> 4, !- Hour 12
> 4, !- Hour 13
> 4, !- Hour 14
> 4, !- Hour 15
> 4, !- Hour 16
> 4, !- Hour 17
> 4, !- Hour 18
> 4, !- Hour 19
> 4, !- Hour 20
> 4, !- Hour 21
> 4, !- Hour 22
> 4, !- Hour 23
> 4; !- Hour 24
>
> Schedule:Day:Hourly,
> Summer Control Type Day Sch - cool, !- Name
> Control Type, !- Schedule Type Limits Name
> 2, !- Hour 1
> 2, !- Hour 2
> 2, !- Hour 3
> 2, !- Hour 4
> 2, !- Hour 5
> 2, !- Hour 6
> 2, !- Hour 7
> 2, !- Hour 8
> 2, !- Hour 9
> 2, !- Hour 10
> 2, !- Hour 11
> 2, !- Hour 12
> 2, !- Hour 13
> 2, !- Hour 14
> 2, !- Hour 15
> 2, !- Hour 16
> 2, !- Hour 17
> 2, !- Hour 18
> 2, !- Hour 19
> 2, !- Hour 20
> 2, !- Hour 21
> 2, !- Hour 22
> 2, !- Hour 23
> 2; !- Hour 24
>
> Schedule:Day:Hourly,
> Winter Control Type Day Sch - heat, !- Name
> Control Type, !- Schedule Type Limits Name
> 1, !- Hour 1
> 1, !- Hour 2
> 1, !- Hour 3
> 1, !- Hour 4
> 1, !- Hour 5
> 1, !- Hour 6
> 1, !- Hour 7
> 1, !- Hour 8
> 1, !- Hour 9
> 1, !- Hour 10
> 1, !- Hour 11
> 1, !- Hour 12
> 1, !- Hour 13
> 1, !- Hour 14
> 1, !- Hour 15
> 1, !- Hour 16
> 1, !- Hour 17
> 1, !- Hour 18
> 1, !- Hour 19
> 1, !- Hour 20
> 1, !- Hour 21
> 1, !- Hour 22
> 1, !- Hour 23
> 1; !- Hour 24
>
>
> !- =========== ALL OBJECTS IN CLASS: SCHEDULE:WEEK:DAILY ===========
>
> Schedule:Week:Daily,
> Off, !- Name
> Off, !- Sunday Schedule:Day Name
> Off, !- Monday Schedule:Day Name
> Off, !- Tuesday Schedule:Day Name
> Off, !- Wednesday Schedule:Day Name
> Off, !- Thursday Schedule:Day Name
> Off, !- Friday Schedule:Day Name
> Off, !- Saturday Schedule:Day Name
> Off, !- Holiday Schedule:Day Name
> Off, !- SummerDesignDay Schedule:Day Name
> Off, !- WinterDesignDay Schedule:Day Name
> Off, !- CustomDay1 Schedule:Day Name
> Off; !- CustomDay2 Schedule:Day Name
>
> Schedule:Week:Daily,
> Summer Control Type Week Sch, !- Name
> Summer Control Type Day Sch, !- Sunday Schedule:Day Name
> Summer Control Type Day Sch, !- Monday Schedule:Day Name
> Summer Control Type Day Sch, !- Tuesday Schedule:Day Name
> Summer Control Type Day Sch, !- Wednesday Schedule:Day Name
> Summer Control Type Day Sch, !- Thursday Schedule:Day Name
> Summer Control Type Day Sch, !- Friday Schedule:Day Name
> Summer Control Type Day Sch, !- Saturday Schedule:Day Name
> Summer Control Type Day Sch, !- Holiday Schedule:Day Name
> Summer Control Type Day Sch, !- SummerDesignDay Schedule:Day Name
> Summer Control Type Day Sch, !- WinterDesignDay Schedule:Day Name
> Summer Control Type Day Sch, !- CustomDay1 Schedule:Day Name
> Summer Control Type Day Sch; !- CustomDay2 Schedule:Day Name
>
> Schedule:Week:Daily,
> Winter Control Type Week Sch, !- Name
> Winter Control Type Day Sch, !- Sunday Schedule:Day Name
> Winter Control Type Day Sch, !- Monday Schedule:Day Name
> Winter Control Type Day Sch, !- Tuesday Schedule:Day Name
> Winter Control Type Day Sch, !- Wednesday Schedule:Day Name
> Winter Control Type Day Sch, !- Thursday Schedule:Day Name
> Winter Control Type Day Sch, !- Friday Schedule:Day Name
> Winter Control Type Day Sch, !- Saturday Schedule:Day Name
> Winter Control Type Day Sch, !- Holiday Schedule:Day Name
> Winter Control Type Day Sch, !- SummerDesignDay Schedule:Day Name
> Winter Control Type Day Sch, !- WinterDesignDay Schedule:Day Name
> Winter Control Type Day Sch, !- CustomDay1 Schedule:Day Name
> Winter Control Type Day Sch; !- CustomDay2 Schedule:Day Name
>
> Schedule:Week:Daily,
> Summer Control Type Week Sch - cool, !- Name
> Summer Control Type Day Sch - cool, !- Sunday Schedule:Day Name
> Summer Control Type Day Sch - cool, !- Monday Schedule:Day Name
> Summer Control Type Day Sch - cool, !- Tuesday Schedule:Day Name
> Summer Control Type Day Sch - cool, !- Wednesday Schedule:Day Name
> Summer Control Type Day Sch - cool, !- Thursday Schedule:Day Name
> Summer Control Type Day Sch - cool, !- Friday Schedule:Day Name
> Summer Control Type Day Sch - cool, !- Saturday Schedule:Day Name
> Summer Control Type Day Sch - cool, !- Holiday Schedule:Day Name
> Summer Control Type Day Sch - cool, !- SummerDesignDay Schedule:Day Name
> Summer Control Type Day Sch - cool, !- WinterDesignDay Schedule:Day Name
> Summer Control Type Day Sch - cool, !- CustomDay1 Schedule:Day Name
> Summer Control Type Day Sch - cool; !- CustomDay2 Schedule:Day Name
>
> Schedule:Week:Daily,
> Winter Control Type Week Sch - heat, !- Name
> Winter Control Type Day Sch - heat, !- Sunday Schedule:Day Name
> Winter Control Type Day Sch - heat, !- Monday Schedule:Day Name
> Winter Control Type Day Sch - heat, !- Tuesday Schedule:Day Name
> Winter Control Type Day Sch - heat, !- Wednesday Schedule:Day Name
> Winter Control Type Day Sch - heat, !- Thursday Schedule:Day Name
> Winter Control Type Day Sch - heat, !- Friday Schedule:Day Name
> Winter Control Type Day Sch - heat, !- Saturday Schedule:Day Name
> Winter Control Type Day Sch - heat, !- Holiday Schedule:Day Name
> Winter Control Type Day Sch - heat, !- SummerDesignDay Schedule:Day Name
> Winter Control Type Day Sch - heat, !- WinterDesignDay Schedule:Day Name
> Winter Control Type Day Sch - heat, !- CustomDay1 Schedule:Day Name
> Winter Control Type Day Sch - heat; !- CustomDay2 Schedule:Day Name
>
>
> !- =========== ALL OBJECTS IN CLASS: SCHEDULE:YEAR ===========
>
> Schedule:Year,
> Zone Control Type Sched, !- Name
> Control Type, !- Schedule Type Limits Name
> Winter Control Type Week Sch, !- Schedule:Week Name 1
> 1, !- Start Month 1
> 1, !- Start Day 1
> 3, !- End Month 1
> 31, !- End Day 1
> Summer Control Type Week Sch, !- Schedule:Week Name 2
> 4, !- Start Month 2
> 1, !- Start Day 2
> 9, !- End Month 2
> 30, !- End Day 2
> Winter Control Type Week Sch, !- Schedule:Week Name 3
> 10, !- Start Month 3
> 1, !- Start Day 3
> 12, !- End Month 3
> 31; !- End Day 3
>
>
> !- =========== ALL OBJECTS IN CLASS: SCHEDULE:COMPACT ===========
>
> Schedule:Compact,
> On, !- Name
> Any Number, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, !- Field 3
> 1; !- Field 4
>
> Schedule:Compact,
> Off, !- Name
> Any Number, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, !- Field 3
> 0; !- Field 4
>
> Schedule:Compact,
> Work efficiency, !- Name
> Any Number, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, !- Field 3
> 0; !- Field 4
>
> Schedule:Compact,
> OpaqueShade, !- Name
> Any Number, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, !- Field 3
> 0; !- Field 4
>
> Schedule:Compact,
> Zone Comfort Control Type Sched, !- Name
> Control Type, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, !- Field 3
> 4; !- Field 4
>
> Schedule:Compact,
> Design Days Only, !- Name
> Any Number, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: SummerDesignDay WinterDesignDay, !- Field 2
> Until: 24:00, !- Field 3
> 1, !- Field 4
> For: AllOtherDays, !- Field 5
> Until: 24:00, !- Field 6
> 0; !- Field 7
>
> Schedule:Compact,
> AirVelocitySchedule, !- Name
> Any Number, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, !- Field 3
> .137; !- Field 4
>
> ! Schedule: Office_OpenOff_Occ
> Schedule:Compact,
> 2864, !- Name
> Fraction, !- Schedule Type Limits Name
> Through: 31 Dec, !- Field 1
> For: Weekdays SummerDesignDay, !- Field 2
> Until: 07:00, !- Field 3
> 0, !- Field 4
> Until: 08:00, !- Field 5
> 0.25, !- Field 6
> Until: 09:00, !- Field 7
> 0.5, !- Field 8
> Until: 12:00, !- Field 9
> 1, !- Field 10
> Until: 14:00, !- Field 11
> 0.75, !- Field 12
> Until: 17:00, !- Field 13
> 1, !- Field 14
> Until: 18:00, !- Field 15
> 0.5, !- Field 16
> Until: 19:00, !- Field 17
> 0.25, !- Field 18
> Until: 24:00, !- Field 19
> 0, !- Field 20
> For: Weekends, !- Field 21
> Until: 24:00, !- Field 22
> 0, !- Field 23
> For: Holidays, !- Field 24
> Until: 24:00, !- Field 25
> 0, !- Field 26
> For: WinterDesignDay AllOtherDays, !- Field 27
> Until: 24:00, !- Field 28
> 0; !- Field 29
>
> ! Schedule: Office_OpenOff_Equip
> Schedule:Compact,
> 2867, !- Name
> Fraction, !- Schedule Type Limits Name
> Through: 31 Dec, !- Field 1
> For: Weekdays SummerDesignDay, !- Field 2
> Until: 07:00, !- Field 3
> 0.05, !- Field 4
> Until: 20:00, !- Field 5
> 1, !- Field 6
> Until: 24:00, !- Field 7
> 0.05, !- Field 8
> For: Weekends, !- Field 9
> Until: 24:00, !- Field 10
> 0.05, !- Field 11
> For: Holidays, !- Field 12
> Until: 24:00, !- Field 13
> 0.05, !- Field 14
> For: WinterDesignDay AllOtherDays, !- Field 15
> Until: 24:00, !- Field 16
> 0; !- Field 17
>
> ! Schedule: Office_OpenOff_Light
> Schedule:Compact,
> 2868, !- Name
> Fraction, !- Schedule Type Limits Name
> Through: 31 Dec, !- Field 1
> For: Weekdays SummerDesignDay, !- Field 2
> Until: 07:00, !- Field 3
> 0, !- Field 4
> Until: 19:00, !- Field 5
> 1, !- Field 6
> Until: 24:00, !- Field 7
> 0, !- Field 8
> For: Weekends, !- Field 9
> Until: 24:00, !- Field 10
> 0, !- Field 11
> For: Holidays, !- Field 12
> Until: 24:00, !- Field 13
> 0, !- Field 14
> For: WinterDesignDay AllOtherDays, !- Field 15
> Until: 24:00, !- Field 16
> 0; !- Field 17
>
> Schedule:Compact,
> 20001, !- Name
> Any Number, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: Weekdays Weekends SummerDesignDays, !- Field 2
> Until: 24:00, !- Field 3
> 0, !- Field 4
> For: WinterDesignDays, !- Field 5
> Until: 24:00, !- Field 6
> 0, !- Field 7
> For: AllOtherDays, !- Field 8
> Until: 24:00, !- Field 9
> 0; !- Field 10
>
> Schedule:Compact,
> 20002, !- Name
> Any Number, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: Weekdays Weekends SummerDesignDays, !- Field 2
> Until: 24:00, !- Field 3
> 22, !- Field 4
> For: WinterDesignDays, !- Field 5
> Until: 24:00, !- Field 6
> 0, !- Field 7
> For: AllOtherDays, !- Field 8
> Until: 24:00, !- Field 9
> 22; !- Field 10
>
> Schedule:Compact,
> Activity Schedule 16, !- Name
> Any Number, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, !- Field 3
> 110.7; !- Field 4
>
> Schedule:Compact,
> Clothing Schedule 16, !- Name
> Any Number, !- Schedule Type Limits Name
> Through: 4/1, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, !- Field 3
> 1, !- Field 4
> Through: 9/30, !- Field 5
> For: AllDays, !- Field 6
> Until: 24:00, !- Field 7
> .5, !- Field 8
> Through: 12/31, !- Field 9
> For: AllDays, !- Field 10
> Until: 24:00, !- Field 11
> 1; !- Field 12
>
> Schedule:Compact,
> Activity Schedule 47, !- Name
> Any Number, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, !- Field 3
> 110.7; !- Field 4
>
> Schedule:Compact,
> Clothing Schedule 47, !- Name
> Any Number, !- Schedule Type Limits Name
> Through: 4/1, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, !- Field 3
> 1, !- Field 4
> Through: 9/30, !- Field 5
> For: AllDays, !- Field 6
> Until: 24:00, !- Field 7
> .5, !- Field 8
> Through: 12/31, !- Field 9
> For: AllDays, !- Field 10
> Until: 24:00, !- Field 11
> 1; !- Field 12
>
> Schedule:Compact,
> schedprova, !- Name
> Fraction, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 10:00, !- Field 3
> 0, !- Field 4
> Until: 12:00, !- Field 5
> 1, !- Field 6
> Until: 19:00, !- Field 7
> 0.5, !- Field 8
> Until: 22:00, !- Field 9
> 0, !- Field 10
> Until: 24:00, !- Field 11
> 1; !- Field 12
>
>
> !- =========== ALL OBJECTS IN CLASS: MATERIAL ===========
>
> ! Urea Formaldehyde Foam- thickness 0.1327
> Material,
> Urea Formaldehyde Foam_0.1327, !- Name
> Rough, !- Roughness
> 0.1327, !- Thickness {m}
> 0.04, !- Conductivity {W/m-K}
> 10, !- Density {kg/m3}
> 1400, !- Specific Heat {J/kg-K}
> 0.9, !- Thermal Absorptance
> 0.6, !- Solar Absorptance
> 0.6; !- Visible Absorptance
>
> ! Cast Concrete- thickness 0.1
> Material,
> Cast Concrete_0.1, !- Name
> Rough, !- Roughness
> 0.1, !- Thickness {m}
> 1.13, !- Conductivity {W/m-K}
> 2000, !- Density {kg/m3}
> 1000, !- Specific Heat {J/kg-K}
> 0.9, !- Thermal Absorptance
> 0.6, !- Solar Absorptance
> 0.6; !- Visible Absorptance
>
> ! Floor/Roof Screed- thickness 0.07
> Material,
> Floor/Roof Screed_0.07, !- Name
> Rough, !- Roughness
> 0.07, !- Thickness {m}
> 0.41, !- Conductivity {W/m-K}
> 1200, !- Density {kg/m3}
> 840, !- Specific Heat {J/kg-K}
> 0.9, !- Thermal Absorptance
> 0.73, !- Solar Absorptance
> 0.73; !- Visible Absorptance
>
> ! Timber Flooring- thickness 0.03
> Material,
> Timber Flooring_0.03, !- Name
> Rough, !- Roughness
> 0.03, !- Thickness {m}
> 0.14, !- Conductivity {W/m-K}
> 650, !- Density {kg/m3}
> 1200, !- Specific Heat {J/kg-K}
> 0.9, !- Thermal Absorptance
> 0.78, !- Solar Absorptance
> 0.78; !- Visible Absorptance
>
> ! Cast Concrete (Dense)- thickness 0.1
> Material,
> Cast Concrete (Dense)_0.1, !- Name
> Rough, !- Roughness
> 0.1, !- Thickness {m}
> 1.4, !- Conductivity {W/m-K}
> 2100, !- Density {kg/m3}
> 840, !- Specific Heat {J/kg-K}
> 0.9, !- Thermal Absorptance
> 0.6, !- Solar Absorptance
> 0.6; !- Visible Absorptance
>
> ! Brickwork, Outer Leaf- thickness 0.1
> Material,
> Brickwork Outer Leaf_0.1,!- Name
> Rough, !- Roughness
> 0.1, !- Thickness {m}
> 0.84, !- Conductivity {W/m-K}
> 1700, !- Density {kg/m3}
> 800, !- Specific Heat {J/kg-K}
> 0.9, !- Thermal Absorptance
> 0.7, !- Solar Absorptance
> 0.7; !- Visible Absorptance
>
> ! XPS Extruded Polystyrene - CO2 Blowing- thickness 0.0795
> Material,
> XPS Extruded Polystyrene - CO2 Blowing_0.0795, !- Name
> Rough, !- Roughness
> 0.0795, !- Thickness {m}
> 0.034, !- Conductivity {W/m-K}
> 35, !- Density {kg/m3}
> 1400, !- Specific Heat {J/kg-K}
> 0.9, !- Thermal Absorptance
> 0.6, !- Solar Absorptance
> 0.6; !- Visible Absorptance
>
> ! Concrete Block (Medium)- thickness 0.1
> Material,
> Concrete Block (Medium)_0.1, !- Name
> Rough, !- Roughness
> 0.1, !- Thickness {m}
> 0.51, !- Conductivity {W/m-K}
> 1400, !- Density {kg/m3}
> 1000, !- Specific Heat {J/kg-K}
> 0.9, !- Thermal Absorptance
> 0.6, !- Solar Absorptance
> 0.6; !- Visible Absorptance
>
> ! Gypsum Plastering- thickness 0.013
> Material,
> Gypsum Plastering_0.013, !- Name
> Rough, !- Roughness
> 0.013, !- Thickness {m}
> 0.4, !- Conductivity {W/m-K}
> 1000, !- Density {kg/m3}
> 1000, !- Specific Heat {J/kg-K}
> 0.9, !- Thermal Absorptance
> 0.5, !- Solar Absorptance
> 0.5; !- Visible Absorptance
>
> ! Asphalt- thickness 0.01
> Material,
> Asphalt_0.01, !- Name
> Rough, !- Roughness
> 0.01, !- Thickness {m}
> 0.7, !- Conductivity {W/m-K}
> 2100, !- Density {kg/m3}
> 1000, !- Specific Heat {J/kg-K}
> 0.9, !- Thermal Absorptance
> 0.85, !- Solar Absorptance
> 0.9; !- Visible Absorptance
>
> ! MW Glass Wool (rolls)- thickness 0.1445
> Material,
> MW Glass Wool (rolls)_0.1445, !- Name
> Rough, !- Roughness
> 0.1445, !- Thickness {m}
> 0.04, !- Conductivity {W/m-K}
> 12, !- Density {kg/m3}
> 840, !- Specific Heat {J/kg-K}
> 0.9, !- Thermal Absorptance
> 0.6, !- Solar Absorptance
> 0.6; !- Visible Absorptance
>
> ! Plasterboard- thickness 0.013
> Material,
> Plasterboard_0.013, !- Name
> Rough, !- Roughness
> 0.013, !- Thickness {m}
> 0.25, !- Conductivity {W/m-K}
> 2800, !- Density {kg/m3}
> 896, !- Specific Heat {J/kg-K}
> 0.9, !- Thermal Absorptance
> 0.5, !- Solar Absorptance
> 0.5; !- Visible Absorptance
>
>
> !- =========== ALL OBJECTS IN CLASS: MATERIAL:NOMASS ===========
>
> !Material:InfraredTransparent,
> !IRTMaterial; !- Name
> !Construction,
> !IRTSurface, !- Name
> !IRTMaterial; !- Outside Layer
> Material:NoMass,
> LinearBridgingLayer, !- Name
> Rough, !- Roughness
> 1, !- Thermal Resistance {m2-K/W}
> 0.0100000, !- Thermal Absorptance
> 0.0100000, !- Solar Absorptance
> 0.0100000; !- Visible Absorptance
>
> ! Special material to represent an R-value for the next construction
> Material:NoMass,
> 7_RVAL_3, !- Name
> Rough, !- Roughness
> 0.18, !- Thermal Resistance {m2-K/W}
> 0.9, !- Thermal Absorptance
> 0.7, !- Solar Absorptance
> 0.7; !- Visible Absorptance
>
> ! Special material to represent an R-value for the next construction
> Material:NoMass,
> 8_RVAL_2, !- Name
> Rough, !- Roughness
> 0.18, !- Thermal Resistance {m2-K/W}
> 0.9, !- Thermal Absorptance
> 0.7, !- Solar Absorptance
> 0.7; !- Visible Absorptance
>
> ! Special material to represent an R-value for the next construction
> Material:NoMass,
> 9_RVAL_1, !- Name
> Rough, !- Roughness
> 999, !- Thermal Resistance {m2-K/W}
> 0.9, !- Thermal Absorptance
> 0.7, !- Solar Absorptance
> 0.7; !- Visible Absorptance
>
> ! Special material to represent an R-value for the next construction
> Material:NoMass,
> 10_RVAL_1, !- Name
> Rough, !- Roughness
> 999, !- Thermal Resistance {m2-K/W}
> 0.9, !- Thermal Absorptance
> 0.7, !- Solar Absorptance
> 0.7; !- Visible Absorptance
>
>
> !- =========== ALL OBJECTS IN CLASS: MATERIAL:INFRAREDTRANSPARENT ===========
>
> Material:InfraredTransparent,
> IRTMaterial; !- Name
>
>
> !- =========== ALL OBJECTS IN CLASS: WINDOWMATERIAL:GLAZING ===========
>
> WindowMaterial:Glazing,
> 2, !- Name
> SpectralAverage, !- Optical Data Type
> , !- Window Glass Spectral Data Set Name
> 0.003, !- Thickness {m}
> 0.837, !- Solar Transmittance at Normal Incidence
> 0.075, !- Front Side Solar Reflectance at Normal Incidence
> 0.075, !- Back Side Solar Reflectance at Normal Incidence
> 0.898, !- Visible Transmittance at Normal Incidence
> 0.081, !- Front Side Visible Reflectance at Normal Incidence
> 0.081, !- Back Side Visible Reflectance at Normal Incidence
> 0.0, !- Infrared Transmittance at Normal Incidence
> 0.84, !- Front Side Infrared Hemispherical Emissivity
> 0.84, !- Back Side Infrared Hemispherical Emissivity
> 0.9, !- Conductivity {W/m-K}
> 1; !- Dirt Correction Factor for Solar and Visible Transmittance
>
> WindowMaterial:Glazing,
> 38, !- Name
> SpectralAverage, !- Optical Data Type
> , !- Window Glass Spectral Data Set Name
> 0.003, !- Thickness {m}
> 0.740, !- Solar Transmittance at Normal Incidence
> 0.090, !- Front Side Solar Reflectance at Normal Incidence
> 0.100, !- Back Side Solar Reflectance at Normal Incidence
> 0.820, !- Visible Transmittance at Normal Incidence
> 0.110, !- Front Side Visible Reflectance at Normal Incidence
> 0.120, !- Back Side Visible Reflectance at Normal Incidence
> 0.0, !- Infrared Transmittance at Normal Incidence
> 0.84, !- Front Side Infrared Hemispherical Emissivity
> 0.20, !- Back Side Infrared Hemispherical Emissivity
> 0.9, !- Conductivity {W/m-K}
> 1; !- Dirt Correction Factor for Solar and Visible Transmittance
>
>
> !- =========== ALL OBJECTS IN CLASS: WINDOWMATERIAL:GAS ===========
>
> WindowMaterial:Gas,
> 1002, !- Name
> Air, !- Gas Type
> 0.013; !- Thickness {m}
>
> WindowMaterial:Gas,
> Half thickness 1002, !- Name
> Air, !- Gas Type
> 0.0065; !- Thickness {m}
>
>
> !- =========== ALL OBJECTS IN CLASS: CONSTRUCTION ===========
>
> Construction,
> LinearBridgingConstruction, !- Name
> LinearBridgingLayer; !- Outside Layer
>
> Construction,
> IRTSurface, !- Name
> IRTMaterial; !- Outside Layer
>
> ! Project ground floor
> Construction,
> Project ground floor, !- Name
> Urea Formaldehyde Foam_0.1327, !- Outside Layer
> Cast Concrete_0.1, !- Layer 2
> Floor/Roof Screed_0.07, !- Layer 3
> Timber Flooring_0.03; !- Layer 4
>
> ! <Previous reversed>
> Construction,
> Project ground floor_Rev,!- Name
> Timber Flooring_0.03, !- Outside Layer
> Floor/Roof Screed_0.07, !- Layer 2
> Cast Concrete_0.1, !- Layer 3
> Urea Formaldehyde Foam_0.1327; !- Layer 4
>
> ! Project internal floor_Reversed
> Construction,
> Project internal floor_Reversed, !- Name
> Cast Concrete (Dense)_0.1; !- Outside Layer
>
> ! <Previous reversed>
> Construction,
> Project internal floor_Reversed_Rev, !- Name
> Cast Concrete (Dense)_0.1; !- Outside Layer
>
> ! Project wall
> Construction,
> Project wall, !- Name
> Brickwork Outer Leaf_0.1,!- Outside Layer
> XPS Extruded Polystyrene - CO2 Blowing_0.0795, !- Layer 2
> Concrete Block (Medium)_0.1, !- Layer 3
> Gypsum Plastering_0.013; !- Layer 4
>
> ! <Previous reversed>
> Construction,
> Project wall_Rev, !- Name
> Gypsum Plastering_0.013, !- Outside Layer
> Concrete Block (Medium)_0.1, !- Layer 2
> XPS Extruded Polystyrene - CO2 Blowing_0.0795, !- Layer 3
> Brickwork Outer Leaf_0.1;!- Layer 4
>
> ! Project flat roof
> Construction,
> Project flat roof, !- Name
> Asphalt_0.01, !- Outside Layer
> MW Glass Wool (rolls)_0.1445, !- Layer 2
> 7_RVAL_3, !- Layer 3
> Plasterboard_0.013; !- Layer 4
>
> ! <Previous reversed>
> Construction,
> Project flat roof_Rev, !- Name
> Plasterboard_0.013, !- Outside Layer
> 8_RVAL_2, !- Layer 2
> MW Glass Wool (rolls)_0.1445, !- Layer 3
> Asphalt_0.01; !- Layer 4
>
> ! Link body
> Construction,
> Link body, !- Name
> 9_RVAL_1; !- Outside Layer
>
> ! <Previous reversed>
> Construction,
> Link body_Rev, !- Name
> 10_RVAL_1; !- Outside Layer
>
> Construction,
> 1001, !- Name
> 38, !- Outside Layer
> 1002, !- Layer 2
> 2; !- Layer 3
>
>
> !- =========== ALL OBJECTS IN CLASS: GLOBALGEOMETRYRULES ===========
>
> GlobalGeometryRules,
> LowerLeftCorner, !- Starting Vertex Position
> CounterClockWise, !- Vertex Entry Direction
> Relative; !- Coordinate System
>
>
> !- =========== ALL OBJECTS IN CLASS: ZONE ===========
>
> ! Block 1 - Zone 1
> Zone,
> Block1:Zone1, !- Name
> 0, !- Direction of Relative North {deg}
> 0, !- X Origin {m}
> 0, !- Y Origin {m}
> 0, !- Z Origin {m}
> 1, !- Type
> 1, !- Multiplier
> , !- Ceiling Height {m}
> 93.2009, !- Volume {m3}
> 26.6288, !- Floor Area {m2}
> TARP; !- Zone Inside Convection Algorithm
>
> ! Block 2 - Zone 1
> Zone,
> Block2:Zone1, !- Name
> 0, !- Direction of Relative North {deg}
> 0, !- X Origin {m}
> 0, !- Y Origin {m}
> 0, !- Z Origin {m}
> 1, !- Type
> 1, !- Multiplier
> , !- Ceiling Height {m}
> 93.2009, !- Volume {m3}
> 26.6288, !- Floor Area {m2}
> TARP; !- Zone Inside Convection Algorithm
>
>
> !- =========== ALL OBJECTS IN CLASS: BUILDINGSURFACE:DETAILED ===========
>
> ! Block 1, Zone 1, Ground floor - 26.629 m2 (Ground), Surface Area: 26.629m2
> BuildingSurface:Detailed,
> Block1:Zone1_GroundFloor_0_0_0, !- Name
> Floor, !- Surface Type
> Project ground floor, !- Construction Name
> Block1:Zone1, !- Zone Name
> Ground, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 1, !- View Factor to Ground
> 4, !- Number of Vertices
> 4.2007186701, !- Vertex 1 X-coordinate {m}
> -2.1541501501, !- Vertex 1 Y-coordinate {m}
> 0, !- Vertex 1 Z-coordinate {m}
> -2.234534097, !- Vertex 2 X-coordinate {m}
> -2.1541501501, !- Vertex 2 Y-coordinate {m}
> 0, !- Vertex 2 Z-coordinate {m}
> -2.234534097, !- Vertex 3 X-coordinate {m}
> 1.983811669, !- Vertex 3 Y-coordinate {m}
> 0, !- Vertex 3 Z-coordinate {m}
> 4.2007186701, !- Vertex 4 X-coordinate {m}
> 1.983811669, !- Vertex 4 Y-coordinate {m}
> 0; !- Vertex 4 Z-coordinate {m}
>
> ! Block 1, Zone 1, Ceiling - 26.629 m2, Surface Area: 26.6288
> BuildingSurface:Detailed,
> Block1:Zone1_Ceiling_1_0_0, !- Name
> Ceiling, !- Surface Type
> Project internal floor_Reversed, !- Construction Name
> Block1:Zone1, !- Zone Name
> Surface, !- Outside Boundary Condition
> Block2:Zone1_Floor_0_0_10000, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0, !- View Factor to Ground
> 4, !- Number of Vertices
> -2.2345341, !- Vertex 1 X-coordinate {m}
> -2.15415015, !- Vertex 1 Y-coordinate {m}
> 3.5, !- Vertex 1 Z-coordinate {m}
> 4.20071867, !- Vertex 2 X-coordinate {m}
> -2.15415015, !- Vertex 2 Y-coordinate {m}
> 3.5, !- Vertex 2 Z-coordinate {m}
> 4.20071867, !- Vertex 3 X-coordinate {m}
> 1.98381167, !- Vertex 3 Y-coordinate {m}
> 3.5, !- Vertex 3 Z-coordinate {m}
> -2.2345341, !- Vertex 4 X-coordinate {m}
> 1.98381167, !- Vertex 4 Y-coordinate {m}
> 3.5; !- Vertex 4 Z-coordinate {m}
>
> ! Block 1, Zone 1, Ceiling - 26.629 m2, Surface Area: 26.6288 <Other side>
> BuildingSurface:Detailed,
> Block2:Zone1_Floor_0_0_10000, !- Name
> Floor, !- Surface Type
> Project internal floor_Reversed_Rev, !- Construction Name
> Block2:Zone1, !- Zone Name
> Surface, !- Outside Boundary Condition
> Block1:Zone1_Ceiling_1_0_0, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0, !- View Factor to Ground
> 4, !- Number of Vertices
> 4.20071867, !- Vertex 1 X-coordinate {m}
> -2.15415015, !- Vertex 1 Y-coordinate {m}
> 3.5, !- Vertex 1 Z-coordinate {m}
> -2.2345341, !- Vertex 2 X-coordinate {m}
> -2.15415015, !- Vertex 2 Y-coordinate {m}
> 3.5, !- Vertex 2 Z-coordinate {m}
> -2.2345341, !- Vertex 3 X-coordinate {m}
> 1.98381167, !- Vertex 3 Y-coordinate {m}
> 3.5, !- Vertex 3 Z-coordinate {m}
> 4.20071867, !- Vertex 4 X-coordinate {m}
> 1.98381167, !- Vertex 4 Y-coordinate {m}
> 3.5; !- Vertex 4 Z-coordinate {m}
>
> ! Block 1, Zone 1, Wall - 14.483 m2 - 90.0?, Surface Area: 14.483m2
> BuildingSurface:Detailed,
> Block1:Zone1_Wall_2_0_0, !- Name
> Wall, !- Surface Type
> Project wall, !- Construction Name
> Block1:Zone1, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> 0.5, !- View Factor to Ground
> 4, !- Number of Vertices
> 4.2007186701, !- Vertex 1 X-coordinate {m}
> -2.1541501501, !- Vertex 1 Y-coordinate {m}
> 0, !- Vertex 1 Z-coordinate {m}
> 4.2007186701, !- Vertex 2 X-coordinate {m}
> 1.983811669, !- Vertex 2 Y-coordinate {m}
> 0, !- Vertex 2 Z-coordinate {m}
> 4.2007186701, !- Vertex 3 X-coordinate {m}
> 1.983811669, !- Vertex 3 Y-coordinate {m}
> 3.5, !- Vertex 3 Z-coordinate {m}
> 4.2007186701, !- Vertex 4 X-coordinate {m}
> -2.1541501501, !- Vertex 4 Y-coordinate {m}
> 3.5; !- Vertex 4 Z-coordinate {m}
>
> ! Block 1, Zone 1, Wall - 22.523 m2 - 0.0?, Surface Area: 22.523m2
> BuildingSurface:Detailed,
> Block1:Zone1_Wall_3_0_0, !- Name
> Wall, !- Surface Type
> Project wall, !- Construction Name
> Block1:Zone1, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> 0.5, !- View Factor to Ground
> 4, !- Number of Vertices
> 4.2007186701, !- Vertex 1 X-coordinate {m}
> 1.983811669, !- Vertex 1 Y-coordinate {m}
> 0, !- Vertex 1 Z-coordinate {m}
> -2.234534097, !- Vertex 2 X-coordinate {m}
> 1.983811669, !- Vertex 2 Y-coordinate {m}
> 0, !- Vertex 2 Z-coordinate {m}
> -2.234534097, !- Vertex 3 X-coordinate {m}
> 1.983811669, !- Vertex 3 Y-coordinate {m}
> 3.5, !- Vertex 3 Z-coordinate {m}
> 4.2007186701, !- Vertex 4 X-coordinate {m}
> 1.983811669, !- Vertex 4 Y-coordinate {m}
> 3.5; !- Vertex 4 Z-coordinate {m}
>
> ! Block 1, Zone 1, Wall - 14.483 m2 - 270.0?, Surface Area: 14.483m2
> BuildingSurface:Detailed,
> Block1:Zone1_Wall_4_0_0, !- Name
> Wall, !- Surface Type
> Project wall, !- Construction Name
> Block1:Zone1, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> 0.5, !- View Factor to Ground
> 4, !- Number of Vertices
> -2.234534097, !- Vertex 1 X-coordinate {m}
> 1.983811669, !- Vertex 1 Y-coordinate {m}
> 0, !- Vertex 1 Z-coordinate {m}
> -2.234534097, !- Vertex 2 X-coordinate {m}
> -2.1541501501, !- Vertex 2 Y-coordinate {m}
> 0, !- Vertex 2 Z-coordinate {m}
> -2.234534097, !- Vertex 3 X-coordinate {m}
> -2.1541501501, !- Vertex 3 Y-coordinate {m}
> 3.5, !- Vertex 3 Z-coordinate {m}
> -2.234534097, !- Vertex 4 X-coordinate {m}
> 1.983811669, !- Vertex 4 Y-coordinate {m}
> 3.5; !- Vertex 4 Z-coordinate {m}
>
> ! Block 1, Zone 1, Wall - 22.523 m2 - 180.0?, Surface Area: 22.523m2
> BuildingSurface:Detailed,
> Block1:Zone1_Wall_5_0_0, !- Name
> Wall, !- Surface Type
> Project wall, !- Construction Name
> Block1:Zone1, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> 0.5, !- View Factor to Ground
> 4, !- Number of Vertices
> -2.234534097, !- Vertex 1 X-coordinate {m}
> -2.1541501501, !- Vertex 1 Y-coordinate {m}
> 0, !- Vertex 1 Z-coordinate {m}
> 4.2007186701, !- Vertex 2 X-coordinate {m}
> -2.1541501501, !- Vertex 2 Y-coordinate {m}
> 0, !- Vertex 2 Z-coordinate {m}
> 4.2007186701, !- Vertex 3 X-coordinate {m}
> -2.1541501501, !- Vertex 3 Y-coordinate {m}
> 3.5, !- Vertex 3 Z-coordinate {m}
> -2.234534097, !- Vertex 4 X-coordinate {m}
> -2.1541501501, !- Vertex 4 Y-coordinate {m}
> 3.5; !- Vertex 4 Z-coordinate {m}
>
> ! Block 2, Zone 1, Roof - 26.629 m2, Surface Area: 26.629m2
> BuildingSurface:Detailed,
> Block2:Zone1_Roof_1_0_0, !- Name
> Roof, !- Surface Type
> Project flat roof, !- Construction Name
> Block2:Zone1, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> 0, !- View Factor to Ground
> 4, !- Number of Vertices
> -2.234534097, !- Vertex 1 X-coordinate {m}
> -2.1541501501, !- Vertex 1 Y-coordinate {m}
> 7, !- Vertex 1 Z-coordinate {m}
> 4.2007186701, !- Vertex 2 X-coordinate {m}
> -2.1541501501, !- Vertex 2 Y-coordinate {m}
> 7, !- Vertex 2 Z-coordinate {m}
> 4.2007186701, !- Vertex 3 X-coordinate {m}
> 1.983811669, !- Vertex 3 Y-coordinate {m}
> 7, !- Vertex 3 Z-coordinate {m}
> -2.234534097, !- Vertex 4 X-coordinate {m}
> 1.983811669, !- Vertex 4 Y-coordinate {m}
> 7; !- Vertex 4 Z-coordinate {m}
>
> ! Block 2, Zone 1, Wall - 14.483 m2 - 90.0?, Surface Area: 14.483m2
> BuildingSurface:Detailed,
> Block2:Zone1_Wall_2_0_0, !- Name
> Wall, !- Surface Type
> Project wall, !- Construction Name
> Block2:Zone1, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> 0.5, !- View Factor to Ground
> 4, !- Number of Vertices
> 4.2007186701, !- Vertex 1 X-coordinate {m}
> -2.1541501501, !- Vertex 1 Y-coordinate {m}
> 3.5, !- Vertex 1 Z-coordinate {m}
> 4.2007186701, !- Vertex 2 X-coordinate {m}
> 1.983811669, !- Vertex 2 Y-coordinate {m}
> 3.5, !- Vertex 2 Z-coordinate {m}
> 4.2007186701, !- Vertex 3 X-coordinate {m}
> 1.983811669, !- Vertex 3 Y-coordinate {m}
> 7, !- Vertex 3 Z-coordinate {m}
> 4.2007186701, !- Vertex 4 X-coordinate {m}
> -2.1541501501, !- Vertex 4 Y-coordinate {m}
> 7; !- Vertex 4 Z-coordinate {m}
>
> ! Block 2, Zone 1, Wall - 22.523 m2 - 0.0?, Surface Area: 22.523m2
> BuildingSurface:Detailed,
> Block2:Zone1_Wall_3_0_0, !- Name
> Wall, !- Surface Type
> Project wall, !- Construction Name
> Block2:Zone1, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> 0.5, !- View Factor to Ground
> 4, !- Number of Vertices
> 4.2007186701, !- Vertex 1 X-coordinate {m}
> 1.983811669, !- Vertex 1 Y-coordinate {m}
> 3.5, !- Vertex 1 Z-coordinate {m}
> -2.234534097, !- Vertex 2 X-coordinate {m}
> 1.983811669, !- Vertex 2 Y-coordinate {m}
> 3.5, !- Vertex 2 Z-coordinate {m}
> -2.234534097, !- Vertex 3 X-coordinate {m}
> 1.983811669, !- Vertex 3 Y-coordinate {m}
> 7, !- Vertex 3 Z-coordinate {m}
> 4.2007186701, !- Vertex 4 X-coordinate {m}
> 1.983811669, !- Vertex 4 Y-coordinate {m}
> 7; !- Vertex 4 Z-coordinate {m}
>
> ! Block 2, Zone 1, Wall - 14.483 m2 - 270.0?, Surface Area: 14.483m2
> BuildingSurface:Detailed,
> Block2:Zone1_Wall_4_0_0, !- Name
> Wall, !- Surface Type
> Project wall, !- Construction Name
> Block2:Zone1, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> 0.5, !- View Factor to Ground
> 4, !- Number of Vertices
> -2.234534097, !- Vertex 1 X-coordinate {m}
> 1.983811669, !- Vertex 1 Y-coordinate {m}
> 3.5, !- Vertex 1 Z-coordinate {m}
> -2.234534097, !- Vertex 2 X-coordinate {m}
> -2.1541501501, !- Vertex 2 Y-coordinate {m}
> 3.5, !- Vertex 2 Z-coordinate {m}
> -2.234534097, !- Vertex 3 X-coordinate {m}
> -2.1541501501, !- Vertex 3 Y-coordinate {m}
> 7, !- Vertex 3 Z-coordinate {m}
> -2.234534097, !- Vertex 4 X-coordinate {m}
> 1.983811669, !- Vertex 4 Y-coordinate {m}
> 7; !- Vertex 4 Z-coordinate {m}
>
> ! Block 2, Zone 1, Wall - 22.523 m2 - 180.0?, Surface Area: 22.523m2
> BuildingSurface:Detailed,
> Block2:Zone1_Wall_5_0_0, !- Name
> Wall, !- Surface Type
> Project wall, !- Construction Name
> Block2:Zone1, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> 0.5, !- View Factor to Ground
> 4, !- Number of Vertices
> -2.234534097, !- Vertex 1 X-coordinate {m}
> -2.1541501501, !- Vertex 1 Y-coordinate {m}
> 3.5, !- Vertex 1 Z-coordinate {m}
> 4.2007186701, !- Vertex 2 X-coordinate {m}
> -2.1541501501, !- Vertex 2 Y-coordinate {m}
> 3.5, !- Vertex 2 Z-coordinate {m}
> 4.2007186701, !- Vertex 3 X-coordinate {m}
> -2.1541501501, !- Vertex 3 Y-coordinate {m}
> 7, !- Vertex 3 Z-coordinate {m}
> -2.234534097, !- Vertex 4 X-coordinate {m}
> -2.1541501501, !- Vertex 4 Y-coordinate {m}
> 7; !- Vertex 4 Z-coordinate {m}
>
> ! The following crack data is added for zone Block2:Zone1 to satisfy the AIRNET requirement for each AIRNET zone to have >= 2 flow connections
> ! This zone only has 1 unique air flow paths to different zones/outside defined in the DesignBuilder model
> ! dummy surface for crack
> BuildingSurface:Detailed,
> Extra Crack 1, !- Name
> Wall, !- Surface Type
> Link body, !- Construction Name
> Block2:Zone1, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0, !- View Factor to Ground
> 3, !- Number of Vertices
> 100001, !- Vertex 1 X-coordinate {m}
> 0, !- Vertex 1 Y-coordinate {m}
> 7, !- Vertex 1 Z-coordinate {m}
> 100002, !- Vertex 2 X-coordinate {m}
> 0, !- Vertex 2 Y-coordinate {m}
> 7, !- Vertex 2 Z-coordinate {m}
> 100002, !- Vertex 3 X-coordinate {m}
> 1, !- Vertex 3 Y-coordinate {m}
> 7; !- Vertex 3 Z-coordinate {m}
>
>
> !- =========== ALL OBJECTS IN CLASS: FENESTRATIONSURFACE:DETAILED ===========
>
> ! Window, 1.211m2
> FenestrationSurface:Detailed,
> Block1:Zone1_Wall_4_0_0_0_0_0_Win, !- Name
> Window, !- Surface Type
> 1001, !- Construction Name
> Block1:Zone1_Wall_4_0_0, !- Building Surface Name
> , !- Outside Boundary Condition Object
> 0.5, !- View Factor to Ground
> , !- Shading Control Name
> 1, !- Frame and Divider Name
> 1, !- Multiplier
> 4, !- Number of Vertices
> -2.234534097, !- Vertex 1 X-coordinate {m}
> 0.2537962986, !- Vertex 1 Y-coordinate {m}
> 1.149626874, !- Vertex 1 Z-coordinate {m}
> -2.234534097, !- Vertex 2 X-coordinate {m}
> -.7568854095, !- Vertex 2 Y-coordinate {m}
> 1.149626874, !- Vertex 2 Z-coordinate {m}
> -2.234534097, !- Vertex 3 X-coordinate {m}
> -.7568854095, !- Vertex 3 Y-coordinate {m}
> 2.3479171554, !- Vertex 3 Z-coordinate {m}
> -2.234534097, !- Vertex 4 X-coordinate {m}
> 0.2537962986, !- Vertex 4 Y-coordinate {m}
> 2.3479171554; !- Vertex 4 Z-coordinate {m}
>
> ! Window, 1.610m2
> FenestrationSurface:Detailed,
> Block2:Zone1_Wall_5_0_0_0_0_0_Win, !- Name
> Window, !- Surface Type
> 1001, !- Construction Name
> Block2:Zone1_Wall_5_0_0, !- Building Surface Name
> , !- Outside Boundary Condition Object
> 0.5, !- View Factor to Ground
> , !- Shading Control Name
> 1, !- Frame and Divider Name
> 1, !- Multiplier
> 4, !- Number of Vertices
> 0.6757518142, !- Vertex 1 X-coordinate {m}
> -2.1541501501, !- Vertex 1 Y-coordinate {m}
> 4.5953754514, !- Vertex 1 Z-coordinate {m}
> 1.8782401037, !- Vertex 2 X-coordinate {m}
> -2.1541501501, !- Vertex 2 Y-coordinate {m}
> 4.5953754514, !- Vertex 2 Z-coordinate {m}
> 1.8782401037, !- Vertex 3 X-coordinate {m}
> -2.1541501501, !- Vertex 3 Y-coordinate {m}
> 5.934287367, !- Vertex 3 Z-coordinate {m}
> 0.6757518142, !- Vertex 4 X-coordinate {m}
> -2.1541501501, !- Vertex 4 Y-coordinate {m}
> 5.934287367; !- Vertex 4 Z-coordinate {m}
>
>
> !- =========== ALL OBJECTS IN CLASS: WINDOWPROPERTY:FRAMEANDDIVIDER ===========
>
> WindowProperty:FrameAndDivider,
> 1, !- Name
> 0.040, !- Frame Width {m}
> 0.0, !- Frame Outside Projection {m}
> 0.0, !- Frame Inside Projection {m}
> 9.5, !- Frame Conductance {W/m2-K}
> 1.0, !- Ratio of Frame-Edge Glass Conductance to Center-Of-Glass Conductance
> 0.5, !- Frame Solar Absorptance
> 0.5, !- Frame Visible Absorptance
> 0.9, !- Frame Thermal Hemispherical Emissivity
> DividedLite, !- Divider Type
> 0.020, !- Divider Width {m}
> 1, !- Number of Horizontal Dividers
> 1, !- Number of Vertical Dividers
> 0.0, !- Divider Outside Projection {m}
> 0.0, !- Divider Inside Projection {m}
> 9.5, !- Divider Conductance {W/m2-K}
> 1.0, !- Ratio of Divider-Edge Glass Conductance to Center-Of-Glass Conductance
> 0.5, !- Divider Solar Absorptance
> 0.5, !- Divider Visible Absorptance
> 0.9, !- Divider Thermal Hemispherical Emissivity
> 0.5, !- Outside Reveal Solar Absorptance
> 0.0, !- Inside Sill Depth {m}
> 0.5, !- Inside Sill Solar Absorptance
> 0.0, !- Inside Reveal Depth {m}
> 0.5; !- Inside Reveal Solar Absorptance
>
>
> !- =========== ALL OBJECTS IN CLASS: PEOPLE ===========
>
> People,
> People Block1:Zone1, !- Name
> Block1:Zone1, !- Zone or ZoneList Name
> 2864, !- Number of People Schedule Name
> People, !- Number of People Calculation Method
> 6.7301631, !- Number of People
> , !- People per Zone Floor Area {person/m2}
> , !- Zone Floor Area per Person {m2/person}
> 0.3, !- Fraction Radiant
> AUTOCALCULATE, !- Sensible Heat Fraction
> Activity Schedule 16, !- Activity Level Schedule Name
> 0.0000000382, !- Carbon Dioxide Generation Rate {m3/s-W}
> Yes, !- Enable ASHRAE 55 Comfort Warnings
> ZoneAveraged, !- Mean Radiant Temperature Calculation Type
> , !- Surface Name/Angle Factor List Name
> Work efficiency, !- Work Efficiency Schedule Name
> ClothingInsulationSchedule, !- Clothing Insulation Calculation Method
> , !- Clothing Insulation Calculation Method Schedule Name
> Clothing Schedule 16, !- Clothing Insulation Schedule Name
> AirVelocitySchedule, !- Air Velocity Schedule Name
> AdaptiveCEN15251; !- Thermal Comfort Model 1 Type
>
>
> !- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:SIMULATIONCONTROL ===========
>
> AirflowNetwork:SimulationControl,
> VENT, !- Name
> MultizoneWithoutDistribution, !- AirflowNetwork Control
> Input, !- Wind Pressure Coefficient Type
> Cp Data, !- AirflowNetwork Wind Pressure Coefficient Array Name
> OpeningHeight, !- Height Selection for Local Wind Pressure Calculation
> LowRise, !- Building Type
> 1000, !- Maximum Number of Iterations {dimensionless}
> ZeroNodePressures, !- Initialization Type
> 0.0001, !- Relative Airflow Convergence Tolerance {dimensionless}
> 0.000001, !- Absolute Airflow Convergence Tolerance {kg/s}
> -0.5, !- Convergence Acceleration Limit {dimensionless}
> , !- Azimuth Angle of Long Axis of Building {deg}
> ; !- Ratio of Building Width Along Short Axis to Width Along Long Axis
>
>
> !- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:ZONE ===========
>
> AirflowNetwork:MultiZone:Zone,
> Block1:Zone1, !- Zone Name
> Temperature, !- Ventilation Control Mode
> 20002, !- Ventilation Control Zone Temperature Setpoint Schedule Name
> , !- Minimum Venting Open Factor {dimensionless}
> , !- Indoor and Outdoor Temperature Difference Lower Limit For Maximum Venting Open Factor {deltaC}
> , !- Indoor and Outdoor Temperature Difference Upper Limit for Minimun Venting Open Factor {deltaC}
> , !- Indoor and Outdoor Enthalpy Difference Lower Limit For Maximum Venting Open Factor {deltaJ/kg}
> , !- Indoor and Outdoor Enthalpy Difference Upper Limit for Minimun Venting Open Factor {deltaJ/kg}
> 20001; !- Venting Availability Schedule Name
>
> AirflowNetwork:MultiZone:Zone,
> Block2:Zone1, !- Zone Name
> Temperature, !- Ventilation Control Mode
> 20002, !- Ventilation Control Zone Temperature Setpoint Schedule Name
> , !- Minimum Venting Open Factor {dimensionless}
> , !- Indoor and Outdoor Temperature Difference Lower Limit For Maximum Venting Open Factor {deltaC}
> , !- Indoor and Outdoor Temperature Difference Upper Limit for Minimun Venting Open Factor {deltaC}
> , !- Indoor and Outdoor Enthalpy Difference Lower Limit For Maximum Venting Open Factor {deltaJ/kg}
> , !- Indoor and Outdoor Enthalpy Difference Upper Limit for Minimun Venting Open Factor {deltaJ/kg}
> 20001; !- Venting Availability Schedule Name
>
>
> !- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:SURFACE ===========
>
> AirflowNetwork:MultiZone:Surface,
> Block1:Zone1_Ceiling_1_0_0, !- Surface Name
> Block1:Zone1_Ceiling_1_0_0, !- Leakage Component Name
> , !- External Node Name
> 1; !- Window/Door Opening Factor, or Crack Factor {dimensionless}
>
> AirflowNetwork:MultiZone:Surface,
> Block1:Zone1_Wall_2_0_0, !- Surface Name
> Block1:Zone1_Wall_2_0_0, !- Leakage Component Name
> Block1:Zone1_Wall_2_0_0, !- External Node Name
> 1; !- Window/Door Opening Factor, or Crack Factor {dimensionless}
>
> AirflowNetwork:MultiZone:Surface,
> Block1:Zone1_Wall_3_0_0, !- Surface Name
> Block1:Zone1_Wall_3_0_0, !- Leakage Component Name
> Block1:Zone1_Wall_3_0_0, !- External Node Name
> 1; !- Window/Door Opening Factor, or Crack Factor {dimensionless}
>
> AirflowNetwork:MultiZone:Surface,
> Block1:Zone1_Wall_4_0_0, !- Surface Name
> Block1:Zone1_Wall_4_0_0, !- Leakage Component Name
> Block1:Zone1_Wall_4_0_0, !- External Node Name
> 1; !- Window/Door Opening Factor, or Crack Factor {dimensionless}
>
> AirflowNetwork:MultiZone:Surface,
> Block1:Zone1_Wall_4_0_0_0_0_0_Win, !- Surface Name
> Block1:Zone1_Wall_4_0_0_0_0_0_Win, !- Leakage Component Name
> Block1:Zone1_Wall_4_0_0_0_0_0_Win, !- External Node Name
> 1, !- Window/Door Opening Factor, or Crack Factor {dimensionless}
> Temperature, !- Ventilation Control Mode
> 20002, !- Ventilation Control Zone Temperature Setpoint Schedule Name
> , !- Minimum Venting Open Factor {dimensionless}
> , !- Indoor and Outdoor Temperature Difference Lower Limit For Maximum Venting Open Factor {deltaC}
> , !- Indoor and Outdoor Temperature Difference Upper Limit for Minimun Venting Open Factor {deltaC}
> , !- Indoor and Outdoor Enthalpy Difference Lower Limit For Maximum Venting Open Factor {deltaJ/kg}
> , !- Indoor and Outdoor Enthalpy Difference Upper Limit for Minimun Venting Open Factor {deltaJ/kg}
> 2864; !- Venting Availability Schedule Name
>
> AirflowNetwork:MultiZone:Surface,
> Block1:Zone1_Wall_5_0_0, !- Surface Name
> Block1:Zone1_Wall_5_0_0, !- Leakage Component Name
> Block1:Zone1_Wall_5_0_0, !- External Node Name
> 1; !- Window/Door Opening Factor, or Crack Factor {dimensionless}
>
> AirflowNetwork:MultiZone:Surface,
> Block2:Zone1_Wall_5_0_0_0_0_0_Win, !- Surface Name
> Block2:Zone1_Wall_5_0_0_0_0_0_Win, !- Leakage Component Name
> Block2:Zone1_Wall_5_0_0_0_0_0_Win, !- External Node Name
> 1, !- Window/Door Opening Factor, or Crack Factor {dimensionless}
> Temperature, !- Ventilation Control Mode
> 20002, !- Ventilation Control Zone Temperature Setpoint Schedule Name
> , !- Minimum Venting Open Factor {dimensionless}
> , !- Indoor and Outdoor Temperature Difference Lower Limit For Maximum Venting Open Factor {deltaC}
> , !- Indoor and Outdoor Temperature Difference Upper Limit for Minimun Venting Open Factor {deltaC}
> , !- Indoor and Outdoor Enthalpy Difference Lower Limit For Maximum Venting Open Factor {deltaJ/kg}
> , !- Indoor and Outdoor Enthalpy Difference Upper Limit for Minimun Venting Open Factor {deltaJ/kg}
> 2864; !- Venting Availability Schedule Name
>
> AirflowNetwork:MultiZone:Surface,
> Extra Crack 1, !- Surface Name
> Extra Crack 1, !- Leakage Component Name
> Extra Crack 1, !- External Node Name
> 1; !- Window/Door Opening Factor, or Crack Factor {dimensionless}
>
>
> !- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:REFERENCECRACKCONDITIONS ===========
>
> AirflowNetwork:MultiZone:ReferenceCrackConditions,
> Reference Crack Conditions, !- Name
> 20, !- Reference Temperature {C}
> 101320, !- Reference Barometric Pressure {Pa}
> 0.005; !- Reference Humidity Ratio {kgWater/kgDryAir}
>
>
> !- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:SURFACE:CRACK ===========
>
> AirflowNetwork:MultiZone:Surface:Crack,
> DefaultCrack, !- Name
> 0.00000000001, !- Air Mass Flow Coefficient at Reference Conditions {kg/s}
> 0.66, !- Air Mass Flow Exponent {dimensionless}
> Reference Crack Conditions; !- Reference Crack Conditions
>
> AirflowNetwork:MultiZone:Surface:Crack,
> Block1:Zone1_Ceiling_1_0_0, !- Name
> 0.0239659, !- Air Mass Flow Coefficient at Reference Conditions {kg/s}
> 0.7, !- Air Mass Flow Exponent {dimensionless}
> Reference Crack Conditions; !- Reference Crack Conditions
>
> AirflowNetwork:MultiZone:Surface:Crack,
> Block1:Zone1_Wall_2_0_0, !- Name
> 0.0014483, !- Air Mass Flow Coefficient at Reference Conditions {kg/s}
> 0.7, !- Air Mass Flow Exponent {dimensionless}
> Reference Crack Conditions; !- Reference Crack Conditions
>
> AirflowNetwork:MultiZone:Surface:Crack,
> Block1:Zone1_Wall_3_0_0, !- Name
> 0.0022523, !- Air Mass Flow Coefficient at Reference Conditions {kg/s}
> 0.7, !- Air Mass Flow Exponent {dimensionless}
> Reference Crack Conditions; !- Reference Crack Conditions
>
> AirflowNetwork:MultiZone:Surface:Crack,
> Block1:Zone1_Wall_4_0_0, !- Name
> 0.0013272, !- Air Mass Flow Coefficient at Reference Conditions {kg/s}
> 0.7, !- Air Mass Flow Exponent {dimensionless}
> Reference Crack Conditions; !- Reference Crack Conditions
>
> AirflowNetwork:MultiZone:Surface:Crack,
> Block1:Zone1_Wall_5_0_0, !- Name
> 0.0022523, !- Air Mass Flow Coefficient at Reference Conditions {kg/s}
> 0.7, !- Air Mass Flow Exponent {dimensionless}
> Reference Crack Conditions; !- Reference Crack Conditions
>
> AirflowNetwork:MultiZone:Surface:Crack,
> Extra Crack 1, !- Name
> 0.00000000001, !- Air Mass Flow Coefficient at Reference Conditions {kg/s}
> 0.5, !- Air Mass Flow Exponent {dimensionless}
> Reference Crack Conditions; !- Reference Crack Conditions
>
>
> !- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:COMPONENT:DETAILEDOPENING ===========
>
> AirflowNetwork:MultiZone:Component:DetailedOpening,
> Block1:Zone1_Wall_4_0_0_0_0_0_Win, !- Name
> 0.00014, !- Air Mass Flow Coefficient When Opening is Closed {kg/s-m}
> 0.65, !- Air Mass Flow Exponent When Opening is Closed {dimensionless}
> NonPivoted, !- Type of Rectanguler Large Vertical Opening (LVO)
> 0, !- Extra Crack Length or Height of Pivoting Axis {m}
> 2, !- Number of Sets of Opening Factor Data
> 0, !- Opening Factor 1 {dimensionless}
> 0.65, !- Discharge Coefficient for Opening Factor 1 {dimensionless}
> 0, !- Width Factor for Opening Factor 1 {dimensionless}
> 1, !- Height Factor for Opening Factor 1 {dimensionless}
> 0, !- Start Height Factor for Opening Factor 1 {dimensionless}
> 1, !- Opening Factor 2 {dimensionless}
> 0.65, !- Discharge Coefficient for Opening Factor 2 {dimensionless}
> 0.00000001, !- Width Factor for Opening Factor 2 {dimensionless}
> 1, !- Height Factor for Opening Factor 2 {dimensionless}
> 0, !- Start Height Factor for Opening Factor 2 {dimensionless}
> 0, !- Opening Factor 3 {dimensionless}
> 0, !- Discharge Coefficient for Opening Factor 3 {dimensionless}
> 0, !- Width Factor for Opening Factor 3 {dimensionless}
> 0, !- Height Factor for Opening Factor 3 {dimensionless}
> 0, !- Start Height Factor for Opening Factor 3 {dimensionless}
> 0, !- Opening Factor 4 {dimensionless}
> 0, !- Discharge Coefficient for Opening Factor 4 {dimensionless}
> 0, !- Width Factor for Opening Factor 4 {dimensionless}
> 0, !- Height Factor for Opening Factor 4 {dimensionless}
> 0; !- Start Height Factor for Opening Factor 4 {dimensionless}
>
> AirflowNetwork:MultiZone:Component:DetailedOpening,
> Block2:Zone1_Wall_5_0_0_0_0_0_Win, !- Name
> 0.00000001, !- Air Mass Flow Coefficient When Opening is Closed {kg/s-m}
> 0.5, !- Air Mass Flow Exponent When Opening is Closed {dimensionless}
> NonPivoted, !- Type of Rectanguler Large Vertical Opening (LVO)
> 0, !- Extra Crack Length or Height of Pivoting Axis {m}
> 2, !- Number of Sets of Opening Factor Data
> 0, !- Opening Factor 1 {dimensionless}
> 0.65, !- Discharge Coefficient for Opening Factor 1 {dimensionless}
> 0, !- Width Factor for Opening Factor 1 {dimensionless}
> 1, !- Height Factor for Opening Factor 1 {dimensionless}
> 0, !- Start Height Factor for Opening Factor 1 {dimensionless}
> 1, !- Opening Factor 2 {dimensionless}
> 0.65, !- Discharge Coefficient for Opening Factor 2 {dimensionless}
> 0.00000001, !- Width Factor for Opening Factor 2 {dimensionless}
> 1, !- Height Factor for Opening Factor 2 {dimensionless}
> 0, !- Start Height Factor for Opening Factor 2 {dimensionless}
> 0, !- Opening Factor 3 {dimensionless}
> 0, !- Discharge Coefficient for Opening Factor 3 {dimensionless}
> 0, !- Width Factor for Opening Factor 3 {dimensionless}
> 0, !- Height Factor for Opening Factor 3 {dimensionless}
> 0, !- Start Height Factor for Opening Factor 3 {dimensionless}
> 0, !- Opening Factor 4 {dimensionless}
> 0, !- Discharge Coefficient for Opening Factor 4 {dimensionless}
> 0, !- Width Factor for Opening Factor 4 {dimensionless}
> 0, !- Height Factor for Opening Factor 4 {dimensionless}
> 0; !- Start Height Factor for Opening Factor 4 {dimensionless}
>
>
> !- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:EXTERNALNODE ===========
>
> AirflowNetwork:MultiZone:ExternalNode,
> Block1:Zone1_Wall_2_0_0, !- Name
> 2.33, !- External Node Height {m}
> Block1:Zone1_Wall_2_0_0; !- Wind Pressure Coefficient Values Object Name
>
> AirflowNetwork:MultiZone:ExternalNode,
> Block1:Zone1_Wall_3_0_0, !- Name
> 2.33, !- External Node Height {m}
> Block1:Zone1_Wall_3_0_0; !- Wind Pressure Coefficient Values Object Name
>
> AirflowNetwork:MultiZone:ExternalNode,
> Block1:Zone1_Wall_4_0_0, !- Name
> 2.33, !- External Node Height {m}
> Block1:Zone1_Wall_4_0_0; !- Wind Pressure Coefficient Values Object Name
>
> AirflowNetwork:MultiZone:ExternalNode,
> Block1:Zone1_Wall_4_0_0_0_0_0_Win, !- Name
> 2.33, !- External Node Height {m}
> Block1:Zone1_Wall_4_0_0_0_0_0_Win; !- Wind Pressure Coefficient Values Object Name
>
> AirflowNetwork:MultiZone:ExternalNode,
> Block1:Zone1_Wall_5_0_0, !- Name
> 2.33, !- External Node Height {m}
> Block1:Zone1_Wall_5_0_0; !- Wind Pressure Coefficient Values Object Name
>
> AirflowNetwork:MultiZone:ExternalNode,
> Block2:Zone1_Wall_5_0_0_0_0_0_Win, !- Name
> 7.02, !- External Node Height {m}
> Block2:Zone1_Wall_5_0_0_0_0_0_Win; !- Wind Pressure Coefficient Values Object Name
>
> AirflowNetwork:MultiZone:ExternalNode,
> Extra Crack 1, !- Name
> 0, !- External Node Height {m}
> Extra Crack 1; !- Wind Pressure Coefficient Values Object Name
>
>
> !- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:WINDPRESSURECOEFFICIENTARRAY ===========
>
> AirflowNetwork:MultiZone:WindPressureCoefficientArray,
> Cp Data, !- Name
> 0, !- Wind Direction 1 {deg}
> 45, !- Wind Direction 2 {deg}
> 90, !- Wind Direction 3 {deg}
> 135, !- Wind Direction 4 {deg}
> 180, !- Wind Direction 5 {deg}
> 225, !- Wind Direction 6 {deg}
> 270, !- Wind Direction 7 {deg}
> 315; !- Wind Direction 8 {deg}
>
>
> !- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:WINDPRESSURECOEFFICIENTVALUES ===========
>
> AirflowNetwork:MultiZone:WindPressureCoefficientValues,
> Block1:Zone1_Wall_2_0_0, !- Name
> Cp Data, !- AirflowNetwork:MultiZone:WindPressureCoefficientArray Name
> -.3, !- Wind Pressure Coefficient Value 1 {dimensionless}
> 0.1, !- Wind Pressure Coefficient Value 2 {dimensionless}
> 0.4, !- Wind Pressure Coefficient Value 3 {dimensionless}
> 0.1, !- Wind Pressure Coefficient Value 4 {dimensionless}
> -.3, !- Wind Pressure Coefficient Value 5 {dimensionless}
> -.35, !- Wind Pressure Coefficient Value 6 {dimensionless}
> -.2, !- Wind Pressure Coefficient Value 7 {dimensionless}
> -.35; !- Wind Pressure Coefficient Value 8 {dimensionless}
>
> AirflowNetwork:MultiZone:WindPressureCoefficientValues,
> Block1:Zone1_Wall_3_0_0, !- Name
> Cp Data, !- AirflowNetwork:MultiZone:WindPressureCoefficientArray Name
> 0.4, !- Wind Pressure Coefficient Value 1 {dimensionless}
> 0.1, !- Wind Pressure Coefficient Value 2 {dimensionless}
> -.3, !- Wind Pressure Coefficient Value 3 {dimensionless}
> -.35, !- Wind Pressure Coefficient Value 4 {dimensionless}
> -.2, !- Wind Pressure Coefficient Value 5 {dimensionless}
> -.35, !- Wind Pressure Coefficient Value 6 {dimensionless}
> -.3, !- Wind Pressure Coefficient Value 7 {dimensionless}
> 0.1; !- Wind Pressure Coefficient Value 8 {dimensionless}
>
> AirflowNetwork:MultiZone:WindPressureCoefficientValues,
> Block1:Zone1_Wall_4_0_0, !- Name
> Cp Data, !- AirflowNetwork:MultiZone:WindPressureCoefficientArray Name
> -.3, !- Wind Pressure Coefficient Value 1 {dimensionless}
> -.35, !- Wind Pressure Coefficient Value 2 {dimensionless}
> -.2, !- Wind Pressure Coefficient Value 3 {dimensionless}
> -.35, !- Wind Pressure Coefficient Value 4 {dimensionless}
> -.3, !- Wind Pressure Coefficient Value 5 {dimensionless}
> 0.1, !- Wind Pressure Coefficient Value 6 {dimensionless}
> 0.4, !- Wind Pressure Coefficient Value 7 {dimensionless}
> 0.1; !- Wind Pressure Coefficient Value 8 {dimensionless}
>
> AirflowNetwork:MultiZone:WindPressureCoefficientValues,
> Block1:Zone1_Wall_4_0_0_0_0_0_Win, !- Name
> Cp Data, !- AirflowNetwork:MultiZone:WindPressureCoefficientArray Name
> -.3, !- Wind Pressure Coefficient Value 1 {dimensionless}
> -.35, !- Wind Pressure Coefficient Value 2 {dimensionless}
> -.2, !- Wind Pressure Coefficient Value 3 {dimensionless}
> -.35, !- Wind Pressure Coefficient Value 4 {dimensionless}
> -.3, !- Wind Pressure Coefficient Value 5 {dimensionless}
> 0.1, !- Wind Pressure Coefficient Value 6 {dimensionless}
> 0.4, !- Wind Pressure Coefficient Value 7 {dimensionless}
> 0.1; !- Wind Pressure Coefficient Value 8 {dimensionless}
>
> AirflowNetwork:MultiZone:WindPressureCoefficientValues,
> Block1:Zone1_Wall_5_0_0, !- Name
> Cp Data, !- AirflowNetwork:MultiZone:WindPressureCoefficientArray Name
> -.2, !- Wind Pressure Coefficient Value 1 {dimensionless}
> -.35, !- Wind Pressure Coefficient Value 2 {dimensionless}
> -.3, !- Wind Pressure Coefficient Value 3 {dimensionless}
> 0.1, !- Wind Pressure Coefficient Value 4 {dimensionless}
> 0.4, !- Wind Pressure Coefficient Value 5 {dimensionless}
> 0.1, !- Wind Pressure Coefficient Value 6 {dimensionless}
> -.3, !- Wind Pressure Coefficient Value 7 {dimensionless}
> -.35; !- Wind Pressure Coefficient Value 8 {dimensionless}
>
> AirflowNetwork:MultiZone:WindPressureCoefficientValues,
> Block2:Zone1_Wall_5_0_0_0_0_0_Win, !- Name
> Cp Data, !- AirflowNetwork:MultiZone:WindPressureCoefficientArray Name
> -.2, !- Wind Pressure Coefficient Value 1 {dimensionless}
> -.35, !- Wind Pressure Coefficient Value 2 {dimensionless}
> -.3, !- Wind Pressure Coefficient Value 3 {dimensionless}
> 0.1, !- Wind Pressure Coefficient Value 4 {dimensionless}
> 0.4, !- Wind Pressure Coefficient Value 5 {dimensionless}
> 0.1, !- Wind Pressure Coefficient Value 6 {dimensionless}
> -.3, !- Wind Pressure Coefficient Value 7 {dimensionless}
> -.35; !- Wind Pressure Coefficient Value 8 {dimensionless}
>
> AirflowNetwork:MultiZone:WindPressureCoefficientValues,
> Extra Crack 1, !- Name
> Cp Data, !- AirflowNetwork:MultiZone:WindPressureCoefficientArray Name
> 0, !- Wind Pressure Coefficient Value 1 {dimensionless}
> 0, !- Wind Pressure Coefficient Value 2 {dimensionless}
> 0, !- Wind Pressure Coefficient Value 3 {dimensionless}
> 0, !- Wind Pressure Coefficient Value 4 {dimensionless}
> 0, !- Wind Pressure Coefficient Value 5 {dimensionless}
> 0, !- Wind Pressure Coefficient Value 6 {dimensionless}
> 0, !- Wind Pressure Coefficient Value 7 {dimensionless}
> 0; !- Wind Pressure Coefficient Value 8 {dimensionless}
>
>
> !- =========== ALL OBJECTS IN CLASS: SIZING:PARAMETERS ===========
>
> Sizing:Parameters,
> 1.2, !- Heating Sizing Factor
> 1.2, !- Cooling Sizing Factor
> 2; !- Timesteps in Averaging Window
>
>
> !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:SENSOR ===========
>
> EnergyManagementSystem:Sensor,
> Zonetemp1, !- Name
> Block1:Zone1, !- Output:Variable or Output:Meter Index Key Name
> Zone mean air temperature; !- Output:Variable or Output:Meter Name
>
> EnergyManagementSystem:Sensor,
> Zonetemp2, !- Name
> Block2:Zone1, !- Output:Variable or Output:Meter Index Key Name
> Zone mean air temperature; !- Output:Variable or Output:Meter Name
>
> EnergyManagementSystem:Sensor,
> Top1, !- Name
> Block1:Zone1, !- Output:Variable or Output:Meter Index Key Name
> Zone Operative Temperature; !- Output:Variable or Output:Meter Name
>
> EnergyManagementSystem:Sensor,
> text, !- Name
> , !- Output:Variable or Output:Meter Index Key Name
> Site Outdoor Air Drybulb Temperature; !- Output:Variable or Output:Meter Name
>
> EnergyManagementSystem:Sensor,
> tempmedmob, !- Name
> People Block1:Zone1, !- Output:Variable or Output:Meter Index Key Name
> Zone Thermal Comfort CEN 15251 Adaptive Model Running Average Outdoor Air Temperature; !- Output:Variable or Output:Meter Name
>
> EnergyManagementSystem:Sensor,
> sched, !- Name
> schedprova, !- Output:Variable or Output:Meter Index Key Name
> schedule value; !- Output:Variable or Output:Meter Name
>
>
> !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:ACTUATOR ===========
>
> EnergyManagementSystem:Actuator,
> MyOpenFactor1, !- Name
> Block1:Zone1_Wall_4_0_0_0_0_0_Win, !- Actuated Component Unique Name
> Airflow network window/door opening, !- Actuated Component Type
> venting opening factor; !- Actuated Component Control Type
>
> EnergyManagementSystem:Actuator,
> MyOpenFactor2, !- Name
> Block2:Zone1_Wall_5_0_0_0_0_0_Win, !- Actuated Component Unique Name
> Airflow network window/door opening, !- Actuated Component Type
> venting opening factor; !- Actuated Component Control Type
>
>
> !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:PROGRAMCALLINGMANAGER ===========
>
> EnergyManagementSystem:ProgramCallingManager,
> Temp_controlled_open_factor, !- Name
> BeginTimestepBeforePredictor, !- EnergyPlus Model Calling Point
> Temp_Opening_Controller1,!- Program Name 1
> Temp_Opening_controller2;!- Program Name 2
>
> EnergyManagementSystem:ProgramCallingManager,
> Initialize Random Number Generator, !- Name
> BeginNewEnvironment, !- EnergyPlus Model Calling Point
> InitRandomSeed; !- Program Name 1
>
>
> !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:PROGRAM ===========
>
> EnergyManagementSystem:Program,
> InitRandomSeed, !- Name
> Set seed = ActualDateAndTime, !- Program Line 1
> Set dummy = @SeedRandom seed; !- Program Line 2
>
> EnergyManagementSystem:Program,
> Temp_Opening_controller2,!- Name
> if Zonetemp1>0, !- Program Line 1
> set myopenfactor2 =@RandomUniform 0 1, !- Program Line 2
> endif; !- A4
>
> EnergyManagementSystem:Program,
> Temp_Opening_controller1,!- Name
> if tempmedmob>10, !- Program Line 1
> set tcomf=0.33*tempmedmob+18.8, !- Program Line 2
> else, !- A4
> set tcomf=0.09*tempmedmob+22.6, !- A5
> endif, !- A6
> set a=tcomf+2, !- A7
> set b=tcomf-2, !- A8
> set testerna=text, !- A9
> set num=(2.71828^(0.171*top1+0.166*text-6.4)), !- A10
> set den=(num+1), !- A11
> set pw=(num/den), !- A12
> run finestra1; !- A13
>
>
> !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:SUBROUTINE ===========
>
> EnergyManagementSystem:Subroutine,
> finestra1, !- Name
> if (sched>0), !- Program Line 1
> set plim=@RandomUniform 0 1, !- Program Line 2
> if ((Zonetemp1>a) || (Zonetemp1<b)), !- A4
> if (pw>plim), !- A5
> set myopenfactor1=1, !- A6
> else, !- A7
> set myopenfactor1=0, !- A8
> endif, !- A9
> endif, !- A10
> else, !- A11
> set myopenfactor1=0, !- A12
> endif, !- A13
> return; !- A14
>
>
> !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:GLOBALVARIABLE ===========
>
> EnergyManagementSystem:GlobalVariable,
> testerna, !- Erl Variable 1 Name
> pw, !- Erl Variable 2 Name
> a, !- Erl Variable 3 Name
> b, !- A4
> tcomf, !- A5
> plim; !- A6
>
>
> !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:OUTPUTVARIABLE ===========
>
> EnergyManagementSystem:OutputVariable,
> temperatura esterna ems, !- Name
> testerna, !- EMS Variable Name
> Averaged, !- Type of Data in Variable
> ZoneTimestep; !- Update Frequency
>
> EnergyManagementSystem:OutputVariable,
> Probabilita finestra, !- Name
> pw, !- EMS Variable Name
> Averaged, !- Type of Data in Variable
> ZoneTimestep; !- Update Frequency
>
> EnergyManagementSystem:OutputVariable,
> Tcomf+2, !- Name
> a, !- EMS Variable Name
> Averaged, !- Type of Data in Variable
> ZoneTimestep; !- Update Frequency
>
> EnergyManagementSystem:OutputVariable,
> Tcomf-2, !- Name
> b, !- EMS Variable Name
> Averaged, !- Type of Data in Variable
> ZoneTimestep; !- Update Frequency
>
> EnergyManagementSystem:OutputVariable,
> P lim, !- Name
> plim, !- EMS Variable Name
> Averaged, !- Type of Data in Variable
> ZoneTimestep; !- Update Frequency
>
>
> !- =========== ALL OBJECTS IN CLASS: OUTPUT:VARIABLEDICTIONARY ===========
>
> Output:VariableDictionary,
> regular; !- Key Field
>
>
> !- =========== ALL OBJECTS IN CLASS: OUTPUT:SURFACES:LIST ===========
>
> Output:Surfaces:List,
> Details; !- Report Type
>
>
> !- =========== ALL OBJECTS IN CLASS: OUTPUT:SURFACES:DRAWING ===========
>
> Output:Surfaces:Drawing,
> DXF, !- Report Type
> Triangulate3DFace; !- Report Specifications 1
>
>
> !- =========== ALL OBJECTS IN CLASS: OUTPUT:CONSTRUCTIONS ===========
>
> Output:Constructions,
> Construction; !- Details Type 1
>
>
> !- =========== ALL OBJECTS IN CLASS: OUTPUT:ENERGYMANAGEMENTSYSTEM ===========
>
> Output:EnergyManagementSystem,
> Verbose, !- Actuator Availability Dictionary Reporting
> Verbose, !- Internal Variable Availability Dictionary Reporting
> Verbose; !- EMS Runtime Language Debug Output Level
>
>
> !- =========== ALL OBJECTS IN CLASS: OUTPUT:TABLE:SUMMARYREPORTS ===========
>
> Output:Table:SummaryReports,
> AnnualBuildingUtilityPerformanceSummary, !- Report 1 Name
> SensibleHeatGainSummary, !- Report 2 Name
> InputVerificationandResultsSummary, !- Report 3 Name
> ClimaticDataSummary, !- Report 4 Name
> EquipmentSummary, !- Report 5 Name
> EnvelopeSummary, !- Report 6 Name
> LightingSummary, !- Report 7 Name
> HVACSizingSummary, !- Report 8 Name
> SystemSummary, !- Report 9 Name
> ComponentSizingSummary, !- Report 10 Name
> OutdoorAirSummary, !- Report 11 Name
> ObjectCountSummary; !- Report 12 Name
>
>
> !- =========== ALL OBJECTS IN CLASS: OUTPUTCONTROL:TABLE:STYLE ===========
>
> OutputControl:Table:Style,
> CommaAndHTML, !- Column Separator
> JtoKWH; !- Unit Conversion
>
>
> !- =========== ALL OBJECTS IN CLASS: OUTPUTCONTROL:REPORTINGTOLERANCES ===========
>
> OutputControl:ReportingTolerances,
> 0.2, !- Tolerance for Time Heating Setpoint Not Met {deltaC}
> 0.2; !- Tolerance for Time Cooling Setpoint Not Met {deltaC}
>
>
> !- =========== ALL OBJECTS IN CLASS: OUTPUT:VARIABLE ===========
>
> Output:Variable,
> *, !- Key Value
> Temp Media Mobile esterna giornaliera, !- Variable Name
> Timestep; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> Site Outdoor Air Drybulb Temperature , !- Variable Name
> Daily; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> Site Outdoor Air Drybulb Temperature, !- Variable Name
> monthly; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> Site Outdoor Air Dewpoint Temperature, !- Variable Name
> monthly; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> Site Outdoor Air Barometric Pressure, !- Variable Name
> monthly; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> AFN Surface Venting Window or Door Opening Factor, !- Variable Name
> Detailed; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> Temp Media Mobile esterna giornaliera; !- Variable Name
>
> Output:Variable,
> *, !- Key Value
> Site Outdoor Air Drybulb Temperature; !- Variable Name
>
> Output:Variable,
> *, !- Key Value
> Zone Thermal Comfort CEN 15251 Adaptive Model Running Average Outdoor Air, !- Variable Name
> Timestep; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> Zone Operative Temperature, !- Variable Name
> Hourly; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> Zone Operative Temperature, !- Variable Name
> Daily; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> Zone Operative Temperature, !- Variable Name
> Monthly; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> Zone Thermal Comfort CEN 15251 Adaptive Model Running Average Outdoor Air Temperature, !- Variable Name
> Hourly; !- Reporting Frequency
>
> Output:Variable,
> , !- Key Value
> temperatura esterna ems, !- Variable Name
> Timestep; !- Reporting Frequency
>
> Output:Variable,
> , !- Key Value
> probabilita finestra, !- Variable Name
> Detailed; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> P lim, !- Variable Name
> Detailed; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> Tcomf+2, !- Variable Name
> Hourly; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> Tcomf-2, !- Variable Name
> Hourly; !- Reporting Frequency
>
> Output:Variable,
> schedprova, !- Key Value
> schedule value, !- Variable Name
> Detailed; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> People Total Heating Energy , !- Variable Name
> Monthly; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> Zone Mean Air Temperature ; !- Variable Name
>
> Output:Variable,
> *, !- Key Value
> AFN Zone Infiltration Air Volume, !- Variable Name
> Hourly; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> AFN Zone Infiltration Air Volume, !- Variable Name
> Daily; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> AFN Zone Infiltration Air Volume, !- Variable Name
> Monthly; !- Reporting Frequency
>
> Output:Variable,
> *, !- Key Value
> AFN Zone Infiltration Air Volume, !- Variable Name
> Annual; !- Reporting Frequency
>
>
> !- =========== ALL OBJECTS IN CLASS: OUTPUT:METER ===========
>
> Output:Meter,
> Volume infiltrazione totale, !- Name
> Hourly; !- Reporting Frequency
>
> Output:Meter,
> Volume infiltrazione totale, !- Name
> Daily; !- Reporting Frequency
>
> Output:Meter,
> Volume infiltrazione totale, !- Name
> Monthly; !- Reporting Frequency
>
> Output:Meter,
> Volume infiltrazione totale, !- Name
> Annual; !- Reporting Frequency
>
>
> !- =========== ALL OBJECTS IN CLASS: OUTPUT:METER:METERFILEONLY ===========
>
> Output:Meter:MeterFileOnly,
> Volume infiltrazione totale, !- Name
> Hourly; !- Reporting Frequency
>
> Output:Meter:MeterFileOnly,
> Volume infiltrazione totale, !- Name
> Monthly; !- Reporting Frequency
>
> Output:Meter:MeterFileOnly,
> Volume infiltrazione totale, !- Name
> Daily; !- Reporting Frequency
>
> Output:Meter:MeterFileOnly,
> Volume infiltrazione totale, !- Name
> Annual; !- Reporting Frequency
>
>
> !- =========== ALL OBJECTS IN CLASS: METER:CUSTOM ===========
>
> Meter:Custom,
> Volume infiltrazione totale, !- Name
> Generic, !- Fuel Type
> *, !- Key Name 1
> AFN Zone Infiltration Air Volume; !- Output Variable or Meter Name 1
>
>
> !- =========== ALL OBJECTS IN CLASS: OUTPUT:SQLITE ===========
>
> Output:SQLite,
> SimpleAndTabular; !- Option Type
>
>
> !- =========== ALL OBJECTS IN CLASS: OUTPUT:DIAGNOSTICS ===========
>
> Output:Diagnostics,
> DisplayAdvancedReportVariables; !- Key 1
>
--
Dr. Ery Djunaedy
Research Scientist - Building Simulation Specialist
Integrated Design Lab University of Idaho
306 S 6th ST, Boise, ID 83702
Phone: 208-429-0220
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo Groups is subject to:
https://info.yahoo.com/legal/us/yahoo/utos/terms/