Re: [EnergyPlus_Support] Reporting global data through custom meter and how to view them



Ery is, I believe, right. Your next step would have to be EMS. Checkout the manual...they do custom report variables.


2014-03-13 17:43 GMT+01:00 Ery Djunaedy <<mailto:ery.mailinglist@xxxxxxxxx>ery.mailinglist@xxxxxxxxx>:
>  
My understanding is that meter:custom works only for variables in
> Joules. I learned this the hard way a few versions of EPlus ago. I do
> not think that has changed.
> 
> Ery
> 
> On Thu, 13 Mar 2014, <mailto:m.aldegheri@xxxxxxxxx>m.aldegheri@xxxxxxxxx wrote:
> 
> > Dear forum,
> >
> > I'm using meter:custom to calculate the sum (timestep per timestep) of the ach infiltration of a model. This model has many zones and i would like to read whole data for them. I created variables and meters in this way:
> >
> > !- =========== ALL OBJECTS IN CLASS: OUTPUT:VARIABLE ===========
> >
> > Output:Variable,
> > *, !- Key Value
> > AFN Zone Infiltration Air Volume, !- Variable Name
> > Hourly; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > AFN Zone Infiltration Air Volume, !- Variable Name
> > Daily; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > AFN Zone Infiltration Air Volume, !- Variable Name
> > Monthly; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > AFN Zone Infiltration Air Volume, !- Variable Name
> > Annual; !- Reporting Frequency
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: OUTPUT:METER ===========
> >
> > Output:Meter,
> > Volume infiltrazione totale, !- Name
> > Hourly; !- Reporting Frequency
> >
> > Output:Meter,
> > Volume infiltrazione totale, !- Name
> > Daily; !- Reporting Frequency
> >
> > Output:Meter,
> > Volume infiltrazione totale, !- Name
> > Monthly; !- Reporting Frequency
> >
> > Output:Meter,
> > Volume infiltrazione totale, !- Name
> > Annual; !- Reporting Frequency
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: OUTPUT:METER:METERFILEONLY ===========
> >
> > Output:Meter:MeterFileOnly,
> > Volume infiltrazione totale, !- Name
> > Hourly; !- Reporting Frequency
> >
> > Output:Meter:MeterFileOnly,
> > Volume infiltrazione totale, !- Name
> > Monthly; !- Reporting Frequency
> >
> > Output:Meter:MeterFileOnly,
> > Volume infiltrazione totale, !- Name
> > Daily; !- Reporting Frequency
> >
> > Output:Meter:MeterFileOnly,
> > Volume infiltrazione totale, !- Name
> > Annual; !- Reporting Frequency
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: METER:CUSTOM ===========
> >
> > Meter:Custom,
> > Volume infiltrazione totale, !- Name
> > Generic, !- Fuel Type
> > *, !- Key Name 1
> > AFN Zone Infiltration Air Volume; !- Output Variable or Meter Name 1
> >
> >
> >
> >
> >
> > (In this model there are 2 zones, and it's an example)
> > The output variable maybe are useless, but using the meters I can't see the data in the sql file. How can I see the data?
> >
> > Marco
> >
> > p.s:
> > Also using the following text it doesn't work.
> >
> > Meter:Custom,
> > Volume infiltrazione totale, !- Name
> > Generic, !- Fuel Type
> > Block1:Zone1, !- Key Name 1
> > AFN Zone Infiltration Air Volume; !- Output Variable or Meter Name 1
> > Block2:Zone1, !- Key Name 2
> > AFN Zone Infiltration Air Volume; !- Output Variable or Meter Name 2
> 
> > !-Generator IDFEditor 1.44
> > !-Option SortedOrder
> >
> > !-NOTE: All comments with '!-' are ignored by the IDFEditor and are generated automatically.
> > !- Use '!' comments if they need to be retained when using the IDFEditor.
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: VERSION ===========
> >
> > ! File generated by DesignBuilder - 3.2.0.073 1/4/2014 - 5:38:22 AM
> > ! Source file: C:\Documents and Settings\Marco\Local Settings\Temp\Untitled 1.dsb
> > Version,
> > 8.1; !- Version Identifier
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: SIMULATIONCONTROL ===========
> >
> > SimulationControl,
> > Yes, !- Do Zone Sizing Calculation
> > Yes, !- Do System Sizing Calculation
> > No, !- Do Plant Sizing Calculation
> > No, !- Run Simulation for Sizing Periods
> > Yes; !- Run Simulation for Weather File Run Periods
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: BUILDING ===========
> >
> > Building,
> > Building, !- Name
> > 0, !- North Axis {deg}
> > Suburbs, !- Terrain
> > 0.04, !- Loads Convergence Tolerance Value
> > 0.4, !- Temperature Convergence Tolerance Value {deltaC}
> > FullExterior, !- Solar Distribution
> > 25, !- Maximum Number of Warmup Days
> > 6; !- Minimum Number of Warmup Days
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: SHADOWCALCULATION ===========
> >
> > ShadowCalculation,
> > AverageOverDaysInFrequency, !- Calculation Method
> > 20, !- Calculation Frequency
> > 15000, !- Maximum Figures in Shadow Overlap Calculations
> > SutherlandHodgman, !- Polygon Clipping Algorithm
> > SimpleSkyDiffuseModeling;!- Sky Diffuse Modeling Algorithm
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: SURFACECONVECTIONALGORITHM:INSIDE ===========
> >
> > SurfaceConvectionAlgorithm:Inside,
> > TARP; !- Algorithm
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: SURFACECONVECTIONALGORITHM:OUTSIDE ===========
> >
> > SurfaceConvectionAlgorithm:Outside,
> > DOE-2; !- Algorithm
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: HEATBALANCEALGORITHM ===========
> >
> > HeatBalanceAlgorithm,
> > ConductionTransferFunction, !- Algorithm
> > 2000; !- Surface Temperature Upper Limit {C}
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: ZONECAPACITANCEMULTIPLIER:RESEARCHSPECIAL ===========
> >
> > ZoneCapacitanceMultiplier:ResearchSpecial,
> > 1.0, !- Temperature Capacity Multiplier
> > 1.0, !- Humidity Capacity Multiplier
> > 1.0, !- Carbon Dioxide Capacity Multiplier
> > 1.0; !- Generic Contaminant Capacity Multiplier
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: TIMESTEP ===========
> >
> > Timestep,
> > 6; !- Number of Timesteps per Hour
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: CONVERGENCELIMITS ===========
> >
> > ConvergenceLimits,
> > 1, !- Minimum System Timestep {minutes}
> > 20; !- Maximum HVAC Iterations
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: PROGRAMCONTROL ===========
> >
> > ProgramControl,
> > 1; !- Number of Threads Allowed
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: SITE:LOCATION ===========
> >
> > ! Hourly weather file: C:\Documents and Settings\All Users\Application Data\DesignBuilder\Weather Data\GBR_LONDON_GATWICK_IWEC.epw
> > Site:Location,
> > Untitled, !- Name
> > 51.15, !- Latitude {deg}
> > -0.18, !- Longitude {deg}
> > 0, !- Time Zone {hr}
> > 62; !- Elevation {m}
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: SIZINGPERIOD:DESIGNDAY ===========
> >
> > SizingPeriod:DesignDay,
> > Summer Design Day in Untitled, !- Name
> > 7, !- Month
> > 15, !- Day of Month
> > SummerDesignDay, !- Day Type
> > 27, !- Maximum Dry-Bulb Temperature {C}
> > 9.7, !- Daily Dry-Bulb Temperature Range {deltaC}
> > , !- Dry-Bulb Temperature Range Modifier Type
> > , !- Dry-Bulb Temperature Range Modifier Day Schedule Name
> > WetBulb, !- Humidity Condition Type
> > 18.6, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
> > , !- Humidity Condition Day Schedule Name
> > , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
> > , !- Enthalpy at Maximum Dry-Bulb {J/kg}
> > , !- Daily Wet-Bulb Temperature Range {deltaC}
> > 100582.4, !- Barometric Pressure {Pa}
> > 0, !- Wind Speed {m/s}
> > 0, !- Wind Direction {deg}
> > 0, !- Rain Indicator
> > 0, !- Snow Indicator
> > 1, !- Daylight Saving Time Indicator
> > , !- Solar Model Indicator
> > , !- Beam Solar Day Schedule Name
> > , !- Diffuse Solar Day Schedule Name
> > , !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
> > , !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
> > 0.98; !- Sky Clearness
> >
> > SizingPeriod:DesignDay,
> > Winter Design Day in Untitled, !- Name
> > 1, !- Month
> > 15, !- Day of Month
> > WinterDesignDay, !- Day Type
> > -4.8, !- Maximum Dry-Bulb Temperature {C}
> > 0, !- Daily Dry-Bulb Temperature Range {deltaC}
> > , !- Dry-Bulb Temperature Range Modifier Type
> > , !- Dry-Bulb Temperature Range Modifier Day Schedule Name
> > WetBulb, !- Humidity Condition Type
> > -4.8, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
> > , !- Humidity Condition Day Schedule Name
> > , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
> > , !- Enthalpy at Maximum Dry-Bulb {J/kg}
> > , !- Daily Wet-Bulb Temperature Range {deltaC}
> > 100582.4, !- Barometric Pressure {Pa}
> > 12.7, !- Wind Speed {m/s}
> > 0, !- Wind Direction {deg}
> > 0, !- Rain Indicator
> > 0, !- Snow Indicator
> > 0, !- Daylight Saving Time Indicator
> > , !- Solar Model Indicator
> > , !- Beam Solar Day Schedule Name
> > , !- Diffuse Solar Day Schedule Name
> > , !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
> > , !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
> > 0; !- Sky Clearness
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: RUNPERIOD ===========
> >
> > RunPeriod,
> > Untitled, !- Name
> > 1, !- Begin Month
> > 1, !- Begin Day of Month
> > 12, !- End Month
> > 31, !- End Day of Month
> > UseWeatherFile, !- Day of Week for Start Day
> > No, !- Use Weather File Holidays and Special Days
> > No, !- Use Weather File Daylight Saving Period
> > Yes, !- Apply Weekend Holiday Rule
> > Yes, !- Use Weather File Rain Indicators
> > Yes, !- Use Weather File Snow Indicators
> > 1; !- Number of Times Runperiod to be Repeated
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: RUNPERIODCONTROL:DAYLIGHTSAVINGTIME ===========
> >
> > RunPeriodControl:DaylightSavingTime,
> > Last Sunday in March, !- Start Date
> > Last Sunday in October; !- End Date
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: SITE:GROUNDTEMPERATURE:BUILDINGSURFACE ===========
> >
> > Site:GroundTemperature:BuildingSurface,
> > 18, !- January Ground Temperature {C}
> > 18, !- February Ground Temperature {C}
> > 18, !- March Ground Temperature {C}
> > 18, !- April Ground Temperature {C}
> > 18, !- May Ground Temperature {C}
> > 18, !- June Ground Temperature {C}
> > 18, !- July Ground Temperature {C}
> > 18, !- August Ground Temperature {C}
> > 18, !- September Ground Temperature {C}
> > 18, !- October Ground Temperature {C}
> > 18, !- November Ground Temperature {C}
> > 18; !- December Ground Temperature {C}
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: SITE:GROUNDTEMPERATURE:SHALLOW ===========
> >
> > Site:GroundTemperature:Shallow,
> > 14, !- January Surface Ground Temperature {C}
> > 14, !- February Surface Ground Temperature {C}
> > 14, !- March Surface Ground Temperature {C}
> > 14, !- April Surface Ground Temperature {C}
> > 14, !- May Surface Ground Temperature {C}
> > 14, !- June Surface Ground Temperature {C}
> > 14, !- July Surface Ground Temperature {C}
> > 14, !- August Surface Ground Temperature {C}
> > 14, !- September Surface Ground Temperature {C}
> > 14, !- October Surface Ground Temperature {C}
> > 14, !- November Surface Ground Temperature {C}
> > 14; !- December Surface Ground Temperature {C}
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: SITE:GROUNDTEMPERATURE:DEEP ===========
> >
> > Site:GroundTemperature:Deep,
> > 14, !- January Deep Ground Temperature {C}
> > 14, !- February Deep Ground Temperature {C}
> > 14, !- March Deep Ground Temperature {C}
> > 14, !- April Deep Ground Temperature {C}
> > 14, !- May Deep Ground Temperature {C}
> > 14, !- June Deep Ground Temperature {C}
> > 14, !- July Deep Ground Temperature {C}
> > 14, !- August Deep Ground Temperature {C}
> > 14, !- September Deep Ground Temperature {C}
> > 14, !- October Deep Ground Temperature {C}
> > 14, !- November Deep Ground Temperature {C}
> > 14; !- December Deep Ground Temperature {C}
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: SITE:GROUNDREFLECTANCE ===========
> >
> > Site:GroundReflectance,
> > 0.2, !- January Ground Reflectance {dimensionless}
> > 0.2, !- February Ground Reflectance {dimensionless}
> > 0.2, !- March Ground Reflectance {dimensionless}
> > 0.2, !- April Ground Reflectance {dimensionless}
> > 0.2, !- May Ground Reflectance {dimensionless}
> > 0.2, !- June Ground Reflectance {dimensionless}
> > 0.2, !- July Ground Reflectance {dimensionless}
> > 0.2, !- August Ground Reflectance {dimensionless}
> > 0.2, !- September Ground Reflectance {dimensionless}
> > 0.2, !- October Ground Reflectance {dimensionless}
> > 0.2, !- November Ground Reflectance {dimensionless}
> > 0.2; !- December Ground Reflectance {dimensionless}
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: SITE:GROUNDREFLECTANCE:SNOWMODIFIER ===========
> >
> > Site:GroundReflectance:SnowModifier,
> > 1.0, !- Ground Reflected Solar Modifier
> > 1.0; !- Daylighting Ground Reflected Solar Modifier
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: SCHEDULETYPELIMITS ===========
> >
> > ScheduleTypeLimits,
> > Any Number; !- Name
> >
> > ScheduleTypeLimits,
> > Fraction, !- Name
> > 0.0, !- Lower Limit Value
> > 1.0, !- Upper Limit Value
> > CONTINUOUS; !- Numeric Type
> >
> > ScheduleTypeLimits,
> > Temperature, !- Name
> > -60, !- Lower Limit Value
> > 200, !- Upper Limit Value
> > CONTINUOUS; !- Numeric Type
> >
> > ScheduleTypeLimits,
> > Control Type, !- Name
> > 0, !- Lower Limit Value
> > 4, !- Upper Limit Value
> > DISCRETE; !- Numeric Type
> >
> > ScheduleTypeLimits,
> > On/Off, !- Name
> > 0, !- Lower Limit Value
> > 1, !- Upper Limit Value
> > DISCRETE; !- Numeric Type
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: SCHEDULE:DAY:HOURLY ===========
> >
> > ! off heating day
> > Schedule:Day:Hourly,
> > 0, !- Name
> > Any Number, !- Schedule Type Limits Name
> > 0, !- Hour 1
> > 0, !- Hour 2
> > 0, !- Hour 3
> > 0, !- Hour 4
> > 0, !- Hour 5
> > 0, !- Hour 6
> > 0, !- Hour 7
> > 0, !- Hour 8
> > 0, !- Hour 9
> > 0, !- Hour 10
> > 0, !- Hour 11
> > 0, !- Hour 12
> > 0, !- Hour 13
> > 0, !- Hour 14
> > 0, !- Hour 15
> > 0, !- Hour 16
> > 0, !- Hour 17
> > 0, !- Hour 18
> > 0, !- Hour 19
> > 0, !- Hour 20
> > 0, !- Hour 21
> > 0, !- Hour 22
> > 0, !- Hour 23
> > 0; !- Hour 24
> >
> > ! off cooling day
> > Schedule:Day:Hourly,
> > 50, !- Name
> > Any Number, !- Schedule Type Limits Name
> > 50, !- Hour 1
> > 50, !- Hour 2
> > 50, !- Hour 3
> > 50, !- Hour 4
> > 50, !- Hour 5
> > 50, !- Hour 6
> > 50, !- Hour 7
> > 50, !- Hour 8
> > 50, !- Hour 9
> > 50, !- Hour 10
> > 50, !- Hour 11
> > 50, !- Hour 12
> > 50, !- Hour 13
> > 50, !- Hour 14
> > 50, !- Hour 15
> > 50, !- Hour 16
> > 50, !- Hour 17
> > 50, !- Hour 18
> > 50, !- Hour 19
> > 50, !- Hour 20
> > 50, !- Hour 21
> > 50, !- Hour 22
> > 50, !- Hour 23
> > 50; !- Hour 24
> >
> > ! used in seasonal schedules
> > Schedule:Day:Hourly,
> > Off, !- Name
> > Fraction, !- Schedule Type Limits Name
> > 0, !- Hour 1
> > 0, !- Hour 2
> > 0, !- Hour 3
> > 0, !- Hour 4
> > 0, !- Hour 5
> > 0, !- Hour 6
> > 0, !- Hour 7
> > 0, !- Hour 8
> > 0, !- Hour 9
> > 0, !- Hour 10
> > 0, !- Hour 11
> > 0, !- Hour 12
> > 0, !- Hour 13
> > 0, !- Hour 14
> > 0, !- Hour 15
> > 0, !- Hour 16
> > 0, !- Hour 17
> > 0, !- Hour 18
> > 0, !- Hour 19
> > 0, !- Hour 20
> > 0, !- Hour 21
> > 0, !- Hour 22
> > 0, !- Hour 23
> > 0; !- Hour 24
> >
> > ! -------------------- Control type schedules (for heating & cooling) ----------------------
> > Schedule:Day:Hourly,
> > Summer Control Type Day Sch, !- Name
> > Control Type, !- Schedule Type Limits Name
> > 4, !- Hour 1
> > 4, !- Hour 2
> > 4, !- Hour 3
> > 4, !- Hour 4
> > 4, !- Hour 5
> > 4, !- Hour 6
> > 4, !- Hour 7
> > 4, !- Hour 8
> > 4, !- Hour 9
> > 4, !- Hour 10
> > 4, !- Hour 11
> > 4, !- Hour 12
> > 4, !- Hour 13
> > 4, !- Hour 14
> > 4, !- Hour 15
> > 4, !- Hour 16
> > 4, !- Hour 17
> > 4, !- Hour 18
> > 4, !- Hour 19
> > 4, !- Hour 20
> > 4, !- Hour 21
> > 4, !- Hour 22
> > 4, !- Hour 23
> > 4; !- Hour 24
> >
> > Schedule:Day:Hourly,
> > Winter Control Type Day Sch, !- Name
> > Control Type, !- Schedule Type Limits Name
> > 4, !- Hour 1
> > 4, !- Hour 2
> > 4, !- Hour 3
> > 4, !- Hour 4
> > 4, !- Hour 5
> > 4, !- Hour 6
> > 4, !- Hour 7
> > 4, !- Hour 8
> > 4, !- Hour 9
> > 4, !- Hour 10
> > 4, !- Hour 11
> > 4, !- Hour 12
> > 4, !- Hour 13
> > 4, !- Hour 14
> > 4, !- Hour 15
> > 4, !- Hour 16
> > 4, !- Hour 17
> > 4, !- Hour 18
> > 4, !- Hour 19
> > 4, !- Hour 20
> > 4, !- Hour 21
> > 4, !- Hour 22
> > 4, !- Hour 23
> > 4; !- Hour 24
> >
> > Schedule:Day:Hourly,
> > Summer Control Type Day Sch - cool, !- Name
> > Control Type, !- Schedule Type Limits Name
> > 2, !- Hour 1
> > 2, !- Hour 2
> > 2, !- Hour 3
> > 2, !- Hour 4
> > 2, !- Hour 5
> > 2, !- Hour 6
> > 2, !- Hour 7
> > 2, !- Hour 8
> > 2, !- Hour 9
> > 2, !- Hour 10
> > 2, !- Hour 11
> > 2, !- Hour 12
> > 2, !- Hour 13
> > 2, !- Hour 14
> > 2, !- Hour 15
> > 2, !- Hour 16
> > 2, !- Hour 17
> > 2, !- Hour 18
> > 2, !- Hour 19
> > 2, !- Hour 20
> > 2, !- Hour 21
> > 2, !- Hour 22
> > 2, !- Hour 23
> > 2; !- Hour 24
> >
> > Schedule:Day:Hourly,
> > Winter Control Type Day Sch - heat, !- Name
> > Control Type, !- Schedule Type Limits Name
> > 1, !- Hour 1
> > 1, !- Hour 2
> > 1, !- Hour 3
> > 1, !- Hour 4
> > 1, !- Hour 5
> > 1, !- Hour 6
> > 1, !- Hour 7
> > 1, !- Hour 8
> > 1, !- Hour 9
> > 1, !- Hour 10
> > 1, !- Hour 11
> > 1, !- Hour 12
> > 1, !- Hour 13
> > 1, !- Hour 14
> > 1, !- Hour 15
> > 1, !- Hour 16
> > 1, !- Hour 17
> > 1, !- Hour 18
> > 1, !- Hour 19
> > 1, !- Hour 20
> > 1, !- Hour 21
> > 1, !- Hour 22
> > 1, !- Hour 23
> > 1; !- Hour 24
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: SCHEDULE:WEEK:DAILY ===========
> >
> > Schedule:Week:Daily,
> > Off, !- Name
> > Off, !- Sunday Schedule:Day Name
> > Off, !- Monday Schedule:Day Name
> > Off, !- Tuesday Schedule:Day Name
> > Off, !- Wednesday Schedule:Day Name
> > Off, !- Thursday Schedule:Day Name
> > Off, !- Friday Schedule:Day Name
> > Off, !- Saturday Schedule:Day Name
> > Off, !- Holiday Schedule:Day Name
> > Off, !- SummerDesignDay Schedule:Day Name
> > Off, !- WinterDesignDay Schedule:Day Name
> > Off, !- CustomDay1 Schedule:Day Name
> > Off; !- CustomDay2 Schedule:Day Name
> >
> > Schedule:Week:Daily,
> > Summer Control Type Week Sch, !- Name
> > Summer Control Type Day Sch, !- Sunday Schedule:Day Name
> > Summer Control Type Day Sch, !- Monday Schedule:Day Name
> > Summer Control Type Day Sch, !- Tuesday Schedule:Day Name
> > Summer Control Type Day Sch, !- Wednesday Schedule:Day Name
> > Summer Control Type Day Sch, !- Thursday Schedule:Day Name
> > Summer Control Type Day Sch, !- Friday Schedule:Day Name
> > Summer Control Type Day Sch, !- Saturday Schedule:Day Name
> > Summer Control Type Day Sch, !- Holiday Schedule:Day Name
> > Summer Control Type Day Sch, !- SummerDesignDay Schedule:Day Name
> > Summer Control Type Day Sch, !- WinterDesignDay Schedule:Day Name
> > Summer Control Type Day Sch, !- CustomDay1 Schedule:Day Name
> > Summer Control Type Day Sch; !- CustomDay2 Schedule:Day Name
> >
> > Schedule:Week:Daily,
> > Winter Control Type Week Sch, !- Name
> > Winter Control Type Day Sch, !- Sunday Schedule:Day Name
> > Winter Control Type Day Sch, !- Monday Schedule:Day Name
> > Winter Control Type Day Sch, !- Tuesday Schedule:Day Name
> > Winter Control Type Day Sch, !- Wednesday Schedule:Day Name
> > Winter Control Type Day Sch, !- Thursday Schedule:Day Name
> > Winter Control Type Day Sch, !- Friday Schedule:Day Name
> > Winter Control Type Day Sch, !- Saturday Schedule:Day Name
> > Winter Control Type Day Sch, !- Holiday Schedule:Day Name
> > Winter Control Type Day Sch, !- SummerDesignDay Schedule:Day Name
> > Winter Control Type Day Sch, !- WinterDesignDay Schedule:Day Name
> > Winter Control Type Day Sch, !- CustomDay1 Schedule:Day Name
> > Winter Control Type Day Sch; !- CustomDay2 Schedule:Day Name
> >
> > Schedule:Week:Daily,
> > Summer Control Type Week Sch - cool, !- Name
> > Summer Control Type Day Sch - cool, !- Sunday Schedule:Day Name
> > Summer Control Type Day Sch - cool, !- Monday Schedule:Day Name
> > Summer Control Type Day Sch - cool, !- Tuesday Schedule:Day Name
> > Summer Control Type Day Sch - cool, !- Wednesday Schedule:Day Name
> > Summer Control Type Day Sch - cool, !- Thursday Schedule:Day Name
> > Summer Control Type Day Sch - cool, !- Friday Schedule:Day Name
> > Summer Control Type Day Sch - cool, !- Saturday Schedule:Day Name
> > Summer Control Type Day Sch - cool, !- Holiday Schedule:Day Name
> > Summer Control Type Day Sch - cool, !- SummerDesignDay Schedule:Day Name
> > Summer Control Type Day Sch - cool, !- WinterDesignDay Schedule:Day Name
> > Summer Control Type Day Sch - cool, !- CustomDay1 Schedule:Day Name
> > Summer Control Type Day Sch - cool; !- CustomDay2 Schedule:Day Name
> >
> > Schedule:Week:Daily,
> > Winter Control Type Week Sch - heat, !- Name
> > Winter Control Type Day Sch - heat, !- Sunday Schedule:Day Name
> > Winter Control Type Day Sch - heat, !- Monday Schedule:Day Name
> > Winter Control Type Day Sch - heat, !- Tuesday Schedule:Day Name
> > Winter Control Type Day Sch - heat, !- Wednesday Schedule:Day Name
> > Winter Control Type Day Sch - heat, !- Thursday Schedule:Day Name
> > Winter Control Type Day Sch - heat, !- Friday Schedule:Day Name
> > Winter Control Type Day Sch - heat, !- Saturday Schedule:Day Name
> > Winter Control Type Day Sch - heat, !- Holiday Schedule:Day Name
> > Winter Control Type Day Sch - heat, !- SummerDesignDay Schedule:Day Name
> > Winter Control Type Day Sch - heat, !- WinterDesignDay Schedule:Day Name
> > Winter Control Type Day Sch - heat, !- CustomDay1 Schedule:Day Name
> > Winter Control Type Day Sch - heat; !- CustomDay2 Schedule:Day Name
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: SCHEDULE:YEAR ===========
> >
> > Schedule:Year,
> > Zone Control Type Sched, !- Name
> > Control Type, !- Schedule Type Limits Name
> > Winter Control Type Week Sch, !- Schedule:Week Name 1
> > 1, !- Start Month 1
> > 1, !- Start Day 1
> > 3, !- End Month 1
> > 31, !- End Day 1
> > Summer Control Type Week Sch, !- Schedule:Week Name 2
> > 4, !- Start Month 2
> > 1, !- Start Day 2
> > 9, !- End Month 2
> > 30, !- End Day 2
> > Winter Control Type Week Sch, !- Schedule:Week Name 3
> > 10, !- Start Month 3
> > 1, !- Start Day 3
> > 12, !- End Month 3
> > 31; !- End Day 3
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: SCHEDULE:COMPACT ===========
> >
> > Schedule:Compact,
> > On, !- Name
> > Any Number, !- Schedule Type Limits Name
> > Through: 12/31, !- Field 1
> > For: AllDays, !- Field 2
> > Until: 24:00, !- Field 3
> > 1; !- Field 4
> >
> > Schedule:Compact,
> > Off, !- Name
> > Any Number, !- Schedule Type Limits Name
> > Through: 12/31, !- Field 1
> > For: AllDays, !- Field 2
> > Until: 24:00, !- Field 3
> > 0; !- Field 4
> >
> > Schedule:Compact,
> > Work efficiency, !- Name
> > Any Number, !- Schedule Type Limits Name
> > Through: 12/31, !- Field 1
> > For: AllDays, !- Field 2
> > Until: 24:00, !- Field 3
> > 0; !- Field 4
> >
> > Schedule:Compact,
> > OpaqueShade, !- Name
> > Any Number, !- Schedule Type Limits Name
> > Through: 12/31, !- Field 1
> > For: AllDays, !- Field 2
> > Until: 24:00, !- Field 3
> > 0; !- Field 4
> >
> > Schedule:Compact,
> > Zone Comfort Control Type Sched, !- Name
> > Control Type, !- Schedule Type Limits Name
> > Through: 12/31, !- Field 1
> > For: AllDays, !- Field 2
> > Until: 24:00, !- Field 3
> > 4; !- Field 4
> >
> > Schedule:Compact,
> > Design Days Only, !- Name
> > Any Number, !- Schedule Type Limits Name
> > Through: 12/31, !- Field 1
> > For: SummerDesignDay WinterDesignDay, !- Field 2
> > Until: 24:00, !- Field 3
> > 1, !- Field 4
> > For: AllOtherDays, !- Field 5
> > Until: 24:00, !- Field 6
> > 0; !- Field 7
> >
> > Schedule:Compact,
> > AirVelocitySchedule, !- Name
> > Any Number, !- Schedule Type Limits Name
> > Through: 12/31, !- Field 1
> > For: AllDays, !- Field 2
> > Until: 24:00, !- Field 3
> > .137; !- Field 4
> >
> > ! Schedule: Office_OpenOff_Occ
> > Schedule:Compact,
> > 2864, !- Name
> > Fraction, !- Schedule Type Limits Name
> > Through: 31 Dec, !- Field 1
> > For: Weekdays SummerDesignDay, !- Field 2
> > Until: 07:00, !- Field 3
> > 0, !- Field 4
> > Until: 08:00, !- Field 5
> > 0.25, !- Field 6
> > Until: 09:00, !- Field 7
> > 0.5, !- Field 8
> > Until: 12:00, !- Field 9
> > 1, !- Field 10
> > Until: 14:00, !- Field 11
> > 0.75, !- Field 12
> > Until: 17:00, !- Field 13
> > 1, !- Field 14
> > Until: 18:00, !- Field 15
> > 0.5, !- Field 16
> > Until: 19:00, !- Field 17
> > 0.25, !- Field 18
> > Until: 24:00, !- Field 19
> > 0, !- Field 20
> > For: Weekends, !- Field 21
> > Until: 24:00, !- Field 22
> > 0, !- Field 23
> > For: Holidays, !- Field 24
> > Until: 24:00, !- Field 25
> > 0, !- Field 26
> > For: WinterDesignDay AllOtherDays, !- Field 27
> > Until: 24:00, !- Field 28
> > 0; !- Field 29
> >
> > ! Schedule: Office_OpenOff_Equip
> > Schedule:Compact,
> > 2867, !- Name
> > Fraction, !- Schedule Type Limits Name
> > Through: 31 Dec, !- Field 1
> > For: Weekdays SummerDesignDay, !- Field 2
> > Until: 07:00, !- Field 3
> > 0.05, !- Field 4
> > Until: 20:00, !- Field 5
> > 1, !- Field 6
> > Until: 24:00, !- Field 7
> > 0.05, !- Field 8
> > For: Weekends, !- Field 9
> > Until: 24:00, !- Field 10
> > 0.05, !- Field 11
> > For: Holidays, !- Field 12
> > Until: 24:00, !- Field 13
> > 0.05, !- Field 14
> > For: WinterDesignDay AllOtherDays, !- Field 15
> > Until: 24:00, !- Field 16
> > 0; !- Field 17
> >
> > ! Schedule: Office_OpenOff_Light
> > Schedule:Compact,
> > 2868, !- Name
> > Fraction, !- Schedule Type Limits Name
> > Through: 31 Dec, !- Field 1
> > For: Weekdays SummerDesignDay, !- Field 2
> > Until: 07:00, !- Field 3
> > 0, !- Field 4
> > Until: 19:00, !- Field 5
> > 1, !- Field 6
> > Until: 24:00, !- Field 7
> > 0, !- Field 8
> > For: Weekends, !- Field 9
> > Until: 24:00, !- Field 10
> > 0, !- Field 11
> > For: Holidays, !- Field 12
> > Until: 24:00, !- Field 13
> > 0, !- Field 14
> > For: WinterDesignDay AllOtherDays, !- Field 15
> > Until: 24:00, !- Field 16
> > 0; !- Field 17
> >
> > Schedule:Compact,
> > 20001, !- Name
> > Any Number, !- Schedule Type Limits Name
> > Through: 12/31, !- Field 1
> > For: Weekdays Weekends SummerDesignDays, !- Field 2
> > Until: 24:00, !- Field 3
> > 0, !- Field 4
> > For: WinterDesignDays, !- Field 5
> > Until: 24:00, !- Field 6
> > 0, !- Field 7
> > For: AllOtherDays, !- Field 8
> > Until: 24:00, !- Field 9
> > 0; !- Field 10
> >
> > Schedule:Compact,
> > 20002, !- Name
> > Any Number, !- Schedule Type Limits Name
> > Through: 12/31, !- Field 1
> > For: Weekdays Weekends SummerDesignDays, !- Field 2
> > Until: 24:00, !- Field 3
> > 22, !- Field 4
> > For: WinterDesignDays, !- Field 5
> > Until: 24:00, !- Field 6
> > 0, !- Field 7
> > For: AllOtherDays, !- Field 8
> > Until: 24:00, !- Field 9
> > 22; !- Field 10
> >
> > Schedule:Compact,
> > Activity Schedule 16, !- Name
> > Any Number, !- Schedule Type Limits Name
> > Through: 12/31, !- Field 1
> > For: AllDays, !- Field 2
> > Until: 24:00, !- Field 3
> > 110.7; !- Field 4
> >
> > Schedule:Compact,
> > Clothing Schedule 16, !- Name
> > Any Number, !- Schedule Type Limits Name
> > Through: 4/1, !- Field 1
> > For: AllDays, !- Field 2
> > Until: 24:00, !- Field 3
> > 1, !- Field 4
> > Through: 9/30, !- Field 5
> > For: AllDays, !- Field 6
> > Until: 24:00, !- Field 7
> > .5, !- Field 8
> > Through: 12/31, !- Field 9
> > For: AllDays, !- Field 10
> > Until: 24:00, !- Field 11
> > 1; !- Field 12
> >
> > Schedule:Compact,
> > Activity Schedule 47, !- Name
> > Any Number, !- Schedule Type Limits Name
> > Through: 12/31, !- Field 1
> > For: AllDays, !- Field 2
> > Until: 24:00, !- Field 3
> > 110.7; !- Field 4
> >
> > Schedule:Compact,
> > Clothing Schedule 47, !- Name
> > Any Number, !- Schedule Type Limits Name
> > Through: 4/1, !- Field 1
> > For: AllDays, !- Field 2
> > Until: 24:00, !- Field 3
> > 1, !- Field 4
> > Through: 9/30, !- Field 5
> > For: AllDays, !- Field 6
> > Until: 24:00, !- Field 7
> > .5, !- Field 8
> > Through: 12/31, !- Field 9
> > For: AllDays, !- Field 10
> > Until: 24:00, !- Field 11
> > 1; !- Field 12
> >
> > Schedule:Compact,
> > schedprova, !- Name
> > Fraction, !- Schedule Type Limits Name
> > Through: 12/31, !- Field 1
> > For: AllDays, !- Field 2
> > Until: 10:00, !- Field 3
> > 0, !- Field 4
> > Until: 12:00, !- Field 5
> > 1, !- Field 6
> > Until: 19:00, !- Field 7
> > 0.5, !- Field 8
> > Until: 22:00, !- Field 9
> > 0, !- Field 10
> > Until: 24:00, !- Field 11
> > 1; !- Field 12
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: MATERIAL ===========
> >
> > ! Urea Formaldehyde Foam- thickness 0.1327
> > Material,
> > Urea Formaldehyde Foam_0.1327, !- Name
> > Rough, !- Roughness
> > 0.1327, !- Thickness {m}
> > 0.04, !- Conductivity {W/m-K}
> > 10, !- Density {kg/m3}
> > 1400, !- Specific Heat {J/kg-K}
> > 0.9, !- Thermal Absorptance
> > 0.6, !- Solar Absorptance
> > 0.6; !- Visible Absorptance
> >
> > ! Cast Concrete- thickness 0.1
> > Material,
> > Cast Concrete_0.1, !- Name
> > Rough, !- Roughness
> > 0.1, !- Thickness {m}
> > 1.13, !- Conductivity {W/m-K}
> > 2000, !- Density {kg/m3}
> > 1000, !- Specific Heat {J/kg-K}
> > 0.9, !- Thermal Absorptance
> > 0.6, !- Solar Absorptance
> > 0.6; !- Visible Absorptance
> >
> > ! Floor/Roof Screed- thickness 0.07
> > Material,
> > Floor/Roof Screed_0.07, !- Name
> > Rough, !- Roughness
> > 0.07, !- Thickness {m}
> > 0.41, !- Conductivity {W/m-K}
> > 1200, !- Density {kg/m3}
> > 840, !- Specific Heat {J/kg-K}
> > 0.9, !- Thermal Absorptance
> > 0.73, !- Solar Absorptance
> > 0.73; !- Visible Absorptance
> >
> > ! Timber Flooring- thickness 0.03
> > Material,
> > Timber Flooring_0.03, !- Name
> > Rough, !- Roughness
> > 0.03, !- Thickness {m}
> > 0.14, !- Conductivity {W/m-K}
> > 650, !- Density {kg/m3}
> > 1200, !- Specific Heat {J/kg-K}
> > 0.9, !- Thermal Absorptance
> > 0.78, !- Solar Absorptance
> > 0.78; !- Visible Absorptance
> >
> > ! Cast Concrete (Dense)- thickness 0.1
> > Material,
> > Cast Concrete (Dense)_0.1, !- Name
> > Rough, !- Roughness
> > 0.1, !- Thickness {m}
> > 1.4, !- Conductivity {W/m-K}
> > 2100, !- Density {kg/m3}
> > 840, !- Specific Heat {J/kg-K}
> > 0.9, !- Thermal Absorptance
> > 0.6, !- Solar Absorptance
> > 0.6; !- Visible Absorptance
> >
> > ! Brickwork, Outer Leaf- thickness 0.1
> > Material,
> > Brickwork Outer Leaf_0.1,!- Name
> > Rough, !- Roughness
> > 0.1, !- Thickness {m}
> > 0.84, !- Conductivity {W/m-K}
> > 1700, !- Density {kg/m3}
> > 800, !- Specific Heat {J/kg-K}
> > 0.9, !- Thermal Absorptance
> > 0.7, !- Solar Absorptance
> > 0.7; !- Visible Absorptance
> >
> > ! XPS Extruded Polystyrene - CO2 Blowing- thickness 0.0795
> > Material,
> > XPS Extruded Polystyrene - CO2 Blowing_0.0795, !- Name
> > Rough, !- Roughness
> > 0.0795, !- Thickness {m}
> > 0.034, !- Conductivity {W/m-K}
> > 35, !- Density {kg/m3}
> > 1400, !- Specific Heat {J/kg-K}
> > 0.9, !- Thermal Absorptance
> > 0.6, !- Solar Absorptance
> > 0.6; !- Visible Absorptance
> >
> > ! Concrete Block (Medium)- thickness 0.1
> > Material,
> > Concrete Block (Medium)_0.1, !- Name
> > Rough, !- Roughness
> > 0.1, !- Thickness {m}
> > 0.51, !- Conductivity {W/m-K}
> > 1400, !- Density {kg/m3}
> > 1000, !- Specific Heat {J/kg-K}
> > 0.9, !- Thermal Absorptance
> > 0.6, !- Solar Absorptance
> > 0.6; !- Visible Absorptance
> >
> > ! Gypsum Plastering- thickness 0.013
> > Material,
> > Gypsum Plastering_0.013, !- Name
> > Rough, !- Roughness
> > 0.013, !- Thickness {m}
> > 0.4, !- Conductivity {W/m-K}
> > 1000, !- Density {kg/m3}
> > 1000, !- Specific Heat {J/kg-K}
> > 0.9, !- Thermal Absorptance
> > 0.5, !- Solar Absorptance
> > 0.5; !- Visible Absorptance
> >
> > ! Asphalt- thickness 0.01
> > Material,
> > Asphalt_0.01, !- Name
> > Rough, !- Roughness
> > 0.01, !- Thickness {m}
> > 0.7, !- Conductivity {W/m-K}
> > 2100, !- Density {kg/m3}
> > 1000, !- Specific Heat {J/kg-K}
> > 0.9, !- Thermal Absorptance
> > 0.85, !- Solar Absorptance
> > 0.9; !- Visible Absorptance
> >
> > ! MW Glass Wool (rolls)- thickness 0.1445
> > Material,
> > MW Glass Wool (rolls)_0.1445, !- Name
> > Rough, !- Roughness
> > 0.1445, !- Thickness {m}
> > 0.04, !- Conductivity {W/m-K}
> > 12, !- Density {kg/m3}
> > 840, !- Specific Heat {J/kg-K}
> > 0.9, !- Thermal Absorptance
> > 0.6, !- Solar Absorptance
> > 0.6; !- Visible Absorptance
> >
> > ! Plasterboard- thickness 0.013
> > Material,
> > Plasterboard_0.013, !- Name
> > Rough, !- Roughness
> > 0.013, !- Thickness {m}
> > 0.25, !- Conductivity {W/m-K}
> > 2800, !- Density {kg/m3}
> > 896, !- Specific Heat {J/kg-K}
> > 0.9, !- Thermal Absorptance
> > 0.5, !- Solar Absorptance
> > 0.5; !- Visible Absorptance
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: MATERIAL:NOMASS ===========
> >
> > !Material:InfraredTransparent,
> > !IRTMaterial; !- Name
> > !Construction,
> > !IRTSurface, !- Name
> > !IRTMaterial; !- Outside Layer
> > Material:NoMass,
> > LinearBridgingLayer, !- Name
> > Rough, !- Roughness
> > 1, !- Thermal Resistance {m2-K/W}
> > 0.0100000, !- Thermal Absorptance
> > 0.0100000, !- Solar Absorptance
> > 0.0100000; !- Visible Absorptance
> >
> > ! Special material to represent an R-value for the next construction
> > Material:NoMass,
> > 7_RVAL_3, !- Name
> > Rough, !- Roughness
> > 0.18, !- Thermal Resistance {m2-K/W}
> > 0.9, !- Thermal Absorptance
> > 0.7, !- Solar Absorptance
> > 0.7; !- Visible Absorptance
> >
> > ! Special material to represent an R-value for the next construction
> > Material:NoMass,
> > 8_RVAL_2, !- Name
> > Rough, !- Roughness
> > 0.18, !- Thermal Resistance {m2-K/W}
> > 0.9, !- Thermal Absorptance
> > 0.7, !- Solar Absorptance
> > 0.7; !- Visible Absorptance
> >
> > ! Special material to represent an R-value for the next construction
> > Material:NoMass,
> > 9_RVAL_1, !- Name
> > Rough, !- Roughness
> > 999, !- Thermal Resistance {m2-K/W}
> > 0.9, !- Thermal Absorptance
> > 0.7, !- Solar Absorptance
> > 0.7; !- Visible Absorptance
> >
> > ! Special material to represent an R-value for the next construction
> > Material:NoMass,
> > 10_RVAL_1, !- Name
> > Rough, !- Roughness
> > 999, !- Thermal Resistance {m2-K/W}
> > 0.9, !- Thermal Absorptance
> > 0.7, !- Solar Absorptance
> > 0.7; !- Visible Absorptance
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: MATERIAL:INFRAREDTRANSPARENT ===========
> >
> > Material:InfraredTransparent,
> > IRTMaterial; !- Name
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: WINDOWMATERIAL:GLAZING ===========
> >
> > WindowMaterial:Glazing,
> > 2, !- Name
> > SpectralAverage, !- Optical Data Type
> > , !- Window Glass Spectral Data Set Name
> > 0.003, !- Thickness {m}
> > 0.837, !- Solar Transmittance at Normal Incidence
> > 0.075, !- Front Side Solar Reflectance at Normal Incidence
> > 0.075, !- Back Side Solar Reflectance at Normal Incidence
> > 0.898, !- Visible Transmittance at Normal Incidence
> > 0.081, !- Front Side Visible Reflectance at Normal Incidence
> > 0.081, !- Back Side Visible Reflectance at Normal Incidence
> > 0.0, !- Infrared Transmittance at Normal Incidence
> > 0.84, !- Front Side Infrared Hemispherical Emissivity
> > 0.84, !- Back Side Infrared Hemispherical Emissivity
> > 0.9, !- Conductivity {W/m-K}
> > 1; !- Dirt Correction Factor for Solar and Visible Transmittance
> >
> > WindowMaterial:Glazing,
> > 38, !- Name
> > SpectralAverage, !- Optical Data Type
> > , !- Window Glass Spectral Data Set Name
> > 0.003, !- Thickness {m}
> > 0.740, !- Solar Transmittance at Normal Incidence
> > 0.090, !- Front Side Solar Reflectance at Normal Incidence
> > 0.100, !- Back Side Solar Reflectance at Normal Incidence
> > 0.820, !- Visible Transmittance at Normal Incidence
> > 0.110, !- Front Side Visible Reflectance at Normal Incidence
> > 0.120, !- Back Side Visible Reflectance at Normal Incidence
> > 0.0, !- Infrared Transmittance at Normal Incidence
> > 0.84, !- Front Side Infrared Hemispherical Emissivity
> > 0.20, !- Back Side Infrared Hemispherical Emissivity
> > 0.9, !- Conductivity {W/m-K}
> > 1; !- Dirt Correction Factor for Solar and Visible Transmittance
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: WINDOWMATERIAL:GAS ===========
> >
> > WindowMaterial:Gas,
> > 1002, !- Name
> > Air, !- Gas Type
> > 0.013; !- Thickness {m}
> >
> > WindowMaterial:Gas,
> > Half thickness 1002, !- Name
> > Air, !- Gas Type
> > 0.0065; !- Thickness {m}
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: CONSTRUCTION ===========
> >
> > Construction,
> > LinearBridgingConstruction, !- Name
> > LinearBridgingLayer; !- Outside Layer
> >
> > Construction,
> > IRTSurface, !- Name
> > IRTMaterial; !- Outside Layer
> >
> > ! Project ground floor
> > Construction,
> > Project ground floor, !- Name
> > Urea Formaldehyde Foam_0.1327, !- Outside Layer
> > Cast Concrete_0.1, !- Layer 2
> > Floor/Roof Screed_0.07, !- Layer 3
> > Timber Flooring_0.03; !- Layer 4
> >
> > ! <Previous reversed>
> > Construction,
> > Project ground floor_Rev,!- Name
> > Timber Flooring_0.03, !- Outside Layer
> > Floor/Roof Screed_0.07, !- Layer 2
> > Cast Concrete_0.1, !- Layer 3
> > Urea Formaldehyde Foam_0.1327; !- Layer 4
> >
> > ! Project internal floor_Reversed
> > Construction,
> > Project internal floor_Reversed, !- Name
> > Cast Concrete (Dense)_0.1; !- Outside Layer
> >
> > ! <Previous reversed>
> > Construction,
> > Project internal floor_Reversed_Rev, !- Name
> > Cast Concrete (Dense)_0.1; !- Outside Layer
> >
> > ! Project wall
> > Construction,
> > Project wall, !- Name
> > Brickwork Outer Leaf_0.1,!- Outside Layer
> > XPS Extruded Polystyrene - CO2 Blowing_0.0795, !- Layer 2
> > Concrete Block (Medium)_0.1, !- Layer 3
> > Gypsum Plastering_0.013; !- Layer 4
> >
> > ! <Previous reversed>
> > Construction,
> > Project wall_Rev, !- Name
> > Gypsum Plastering_0.013, !- Outside Layer
> > Concrete Block (Medium)_0.1, !- Layer 2
> > XPS Extruded Polystyrene - CO2 Blowing_0.0795, !- Layer 3
> > Brickwork Outer Leaf_0.1;!- Layer 4
> >
> > ! Project flat roof
> > Construction,
> > Project flat roof, !- Name
> > Asphalt_0.01, !- Outside Layer
> > MW Glass Wool (rolls)_0.1445, !- Layer 2
> > 7_RVAL_3, !- Layer 3
> > Plasterboard_0.013; !- Layer 4
> >
> > ! <Previous reversed>
> > Construction,
> > Project flat roof_Rev, !- Name
> > Plasterboard_0.013, !- Outside Layer
> > 8_RVAL_2, !- Layer 2
> > MW Glass Wool (rolls)_0.1445, !- Layer 3
> > Asphalt_0.01; !- Layer 4
> >
> > ! Link body
> > Construction,
> > Link body, !- Name
> > 9_RVAL_1; !- Outside Layer
> >
> > ! <Previous reversed>
> > Construction,
> > Link body_Rev, !- Name
> > 10_RVAL_1; !- Outside Layer
> >
> > Construction,
> > 1001, !- Name
> > 38, !- Outside Layer
> > 1002, !- Layer 2
> > 2; !- Layer 3
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: GLOBALGEOMETRYRULES ===========
> >
> > GlobalGeometryRules,
> > LowerLeftCorner, !- Starting Vertex Position
> > CounterClockWise, !- Vertex Entry Direction
> > Relative; !- Coordinate System
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: ZONE ===========
> >
> > ! Block 1 - Zone 1
> > Zone,
> > Block1:Zone1, !- Name
> > 0, !- Direction of Relative North {deg}
> > 0, !- X Origin {m}
> > 0, !- Y Origin {m}
> > 0, !- Z Origin {m}
> > 1, !- Type
> > 1, !- Multiplier
> > , !- Ceiling Height {m}
> > 93.2009, !- Volume {m3}
> > 26.6288, !- Floor Area {m2}
> > TARP; !- Zone Inside Convection Algorithm
> >
> > ! Block 2 - Zone 1
> > Zone,
> > Block2:Zone1, !- Name
> > 0, !- Direction of Relative North {deg}
> > 0, !- X Origin {m}
> > 0, !- Y Origin {m}
> > 0, !- Z Origin {m}
> > 1, !- Type
> > 1, !- Multiplier
> > , !- Ceiling Height {m}
> > 93.2009, !- Volume {m3}
> > 26.6288, !- Floor Area {m2}
> > TARP; !- Zone Inside Convection Algorithm
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: BUILDINGSURFACE:DETAILED ===========
> >
> > ! Block 1, Zone 1, Ground floor - 26.629 m2 (Ground), Surface Area: 26.629m2
> > BuildingSurface:Detailed,
> > Block1:Zone1_GroundFloor_0_0_0, !- Name
> > Floor, !- Surface Type
> > Project ground floor, !- Construction Name
> > Block1:Zone1, !- Zone Name
> > Ground, !- Outside Boundary Condition
> > , !- Outside Boundary Condition Object
> > NoSun, !- Sun Exposure
> > NoWind, !- Wind Exposure
> > 1, !- View Factor to Ground
> > 4, !- Number of Vertices
> > 4.2007186701, !- Vertex 1 X-coordinate {m}
> > -2.1541501501, !- Vertex 1 Y-coordinate {m}
> > 0, !- Vertex 1 Z-coordinate {m}
> > -2.234534097, !- Vertex 2 X-coordinate {m}
> > -2.1541501501, !- Vertex 2 Y-coordinate {m}
> > 0, !- Vertex 2 Z-coordinate {m}
> > -2.234534097, !- Vertex 3 X-coordinate {m}
> > 1.983811669, !- Vertex 3 Y-coordinate {m}
> > 0, !- Vertex 3 Z-coordinate {m}
> > 4.2007186701, !- Vertex 4 X-coordinate {m}
> > 1.983811669, !- Vertex 4 Y-coordinate {m}
> > 0; !- Vertex 4 Z-coordinate {m}
> >
> > ! Block 1, Zone 1, Ceiling - 26.629 m2, Surface Area: 26.6288
> > BuildingSurface:Detailed,
> > Block1:Zone1_Ceiling_1_0_0, !- Name
> > Ceiling, !- Surface Type
> > Project internal floor_Reversed, !- Construction Name
> > Block1:Zone1, !- Zone Name
> > Surface, !- Outside Boundary Condition
> > Block2:Zone1_Floor_0_0_10000, !- Outside Boundary Condition Object
> > NoSun, !- Sun Exposure
> > NoWind, !- Wind Exposure
> > 0, !- View Factor to Ground
> > 4, !- Number of Vertices
> > -2.2345341, !- Vertex 1 X-coordinate {m}
> > -2.15415015, !- Vertex 1 Y-coordinate {m}
> > 3.5, !- Vertex 1 Z-coordinate {m}
> > 4.20071867, !- Vertex 2 X-coordinate {m}
> > -2.15415015, !- Vertex 2 Y-coordinate {m}
> > 3.5, !- Vertex 2 Z-coordinate {m}
> > 4.20071867, !- Vertex 3 X-coordinate {m}
> > 1.98381167, !- Vertex 3 Y-coordinate {m}
> > 3.5, !- Vertex 3 Z-coordinate {m}
> > -2.2345341, !- Vertex 4 X-coordinate {m}
> > 1.98381167, !- Vertex 4 Y-coordinate {m}
> > 3.5; !- Vertex 4 Z-coordinate {m}
> >
> > ! Block 1, Zone 1, Ceiling - 26.629 m2, Surface Area: 26.6288 <Other side>
> > BuildingSurface:Detailed,
> > Block2:Zone1_Floor_0_0_10000, !- Name
> > Floor, !- Surface Type
> > Project internal floor_Reversed_Rev, !- Construction Name
> > Block2:Zone1, !- Zone Name
> > Surface, !- Outside Boundary Condition
> > Block1:Zone1_Ceiling_1_0_0, !- Outside Boundary Condition Object
> > NoSun, !- Sun Exposure
> > NoWind, !- Wind Exposure
> > 0, !- View Factor to Ground
> > 4, !- Number of Vertices
> > 4.20071867, !- Vertex 1 X-coordinate {m}
> > -2.15415015, !- Vertex 1 Y-coordinate {m}
> > 3.5, !- Vertex 1 Z-coordinate {m}
> > -2.2345341, !- Vertex 2 X-coordinate {m}
> > -2.15415015, !- Vertex 2 Y-coordinate {m}
> > 3.5, !- Vertex 2 Z-coordinate {m}
> > -2.2345341, !- Vertex 3 X-coordinate {m}
> > 1.98381167, !- Vertex 3 Y-coordinate {m}
> > 3.5, !- Vertex 3 Z-coordinate {m}
> > 4.20071867, !- Vertex 4 X-coordinate {m}
> > 1.98381167, !- Vertex 4 Y-coordinate {m}
> > 3.5; !- Vertex 4 Z-coordinate {m}
> >
> > ! Block 1, Zone 1, Wall - 14.483 m2 - 90.0?, Surface Area: 14.483m2
> > BuildingSurface:Detailed,
> > Block1:Zone1_Wall_2_0_0, !- Name
> > Wall, !- Surface Type
> > Project wall, !- Construction Name
> > Block1:Zone1, !- Zone Name
> > Outdoors, !- Outside Boundary Condition
> > , !- Outside Boundary Condition Object
> > SunExposed, !- Sun Exposure
> > WindExposed, !- Wind Exposure
> > 0.5, !- View Factor to Ground
> > 4, !- Number of Vertices
> > 4.2007186701, !- Vertex 1 X-coordinate {m}
> > -2.1541501501, !- Vertex 1 Y-coordinate {m}
> > 0, !- Vertex 1 Z-coordinate {m}
> > 4.2007186701, !- Vertex 2 X-coordinate {m}
> > 1.983811669, !- Vertex 2 Y-coordinate {m}
> > 0, !- Vertex 2 Z-coordinate {m}
> > 4.2007186701, !- Vertex 3 X-coordinate {m}
> > 1.983811669, !- Vertex 3 Y-coordinate {m}
> > 3.5, !- Vertex 3 Z-coordinate {m}
> > 4.2007186701, !- Vertex 4 X-coordinate {m}
> > -2.1541501501, !- Vertex 4 Y-coordinate {m}
> > 3.5; !- Vertex 4 Z-coordinate {m}
> >
> > ! Block 1, Zone 1, Wall - 22.523 m2 - 0.0?, Surface Area: 22.523m2
> > BuildingSurface:Detailed,
> > Block1:Zone1_Wall_3_0_0, !- Name
> > Wall, !- Surface Type
> > Project wall, !- Construction Name
> > Block1:Zone1, !- Zone Name
> > Outdoors, !- Outside Boundary Condition
> > , !- Outside Boundary Condition Object
> > SunExposed, !- Sun Exposure
> > WindExposed, !- Wind Exposure
> > 0.5, !- View Factor to Ground
> > 4, !- Number of Vertices
> > 4.2007186701, !- Vertex 1 X-coordinate {m}
> > 1.983811669, !- Vertex 1 Y-coordinate {m}
> > 0, !- Vertex 1 Z-coordinate {m}
> > -2.234534097, !- Vertex 2 X-coordinate {m}
> > 1.983811669, !- Vertex 2 Y-coordinate {m}
> > 0, !- Vertex 2 Z-coordinate {m}
> > -2.234534097, !- Vertex 3 X-coordinate {m}
> > 1.983811669, !- Vertex 3 Y-coordinate {m}
> > 3.5, !- Vertex 3 Z-coordinate {m}
> > 4.2007186701, !- Vertex 4 X-coordinate {m}
> > 1.983811669, !- Vertex 4 Y-coordinate {m}
> > 3.5; !- Vertex 4 Z-coordinate {m}
> >
> > ! Block 1, Zone 1, Wall - 14.483 m2 - 270.0?, Surface Area: 14.483m2
> > BuildingSurface:Detailed,
> > Block1:Zone1_Wall_4_0_0, !- Name
> > Wall, !- Surface Type
> > Project wall, !- Construction Name
> > Block1:Zone1, !- Zone Name
> > Outdoors, !- Outside Boundary Condition
> > , !- Outside Boundary Condition Object
> > SunExposed, !- Sun Exposure
> > WindExposed, !- Wind Exposure
> > 0.5, !- View Factor to Ground
> > 4, !- Number of Vertices
> > -2.234534097, !- Vertex 1 X-coordinate {m}
> > 1.983811669, !- Vertex 1 Y-coordinate {m}
> > 0, !- Vertex 1 Z-coordinate {m}
> > -2.234534097, !- Vertex 2 X-coordinate {m}
> > -2.1541501501, !- Vertex 2 Y-coordinate {m}
> > 0, !- Vertex 2 Z-coordinate {m}
> > -2.234534097, !- Vertex 3 X-coordinate {m}
> > -2.1541501501, !- Vertex 3 Y-coordinate {m}
> > 3.5, !- Vertex 3 Z-coordinate {m}
> > -2.234534097, !- Vertex 4 X-coordinate {m}
> > 1.983811669, !- Vertex 4 Y-coordinate {m}
> > 3.5; !- Vertex 4 Z-coordinate {m}
> >
> > ! Block 1, Zone 1, Wall - 22.523 m2 - 180.0?, Surface Area: 22.523m2
> > BuildingSurface:Detailed,
> > Block1:Zone1_Wall_5_0_0, !- Name
> > Wall, !- Surface Type
> > Project wall, !- Construction Name
> > Block1:Zone1, !- Zone Name
> > Outdoors, !- Outside Boundary Condition
> > , !- Outside Boundary Condition Object
> > SunExposed, !- Sun Exposure
> > WindExposed, !- Wind Exposure
> > 0.5, !- View Factor to Ground
> > 4, !- Number of Vertices
> > -2.234534097, !- Vertex 1 X-coordinate {m}
> > -2.1541501501, !- Vertex 1 Y-coordinate {m}
> > 0, !- Vertex 1 Z-coordinate {m}
> > 4.2007186701, !- Vertex 2 X-coordinate {m}
> > -2.1541501501, !- Vertex 2 Y-coordinate {m}
> > 0, !- Vertex 2 Z-coordinate {m}
> > 4.2007186701, !- Vertex 3 X-coordinate {m}
> > -2.1541501501, !- Vertex 3 Y-coordinate {m}
> > 3.5, !- Vertex 3 Z-coordinate {m}
> > -2.234534097, !- Vertex 4 X-coordinate {m}
> > -2.1541501501, !- Vertex 4 Y-coordinate {m}
> > 3.5; !- Vertex 4 Z-coordinate {m}
> >
> > ! Block 2, Zone 1, Roof - 26.629 m2, Surface Area: 26.629m2
> > BuildingSurface:Detailed,
> > Block2:Zone1_Roof_1_0_0, !- Name
> > Roof, !- Surface Type
> > Project flat roof, !- Construction Name
> > Block2:Zone1, !- Zone Name
> > Outdoors, !- Outside Boundary Condition
> > , !- Outside Boundary Condition Object
> > SunExposed, !- Sun Exposure
> > WindExposed, !- Wind Exposure
> > 0, !- View Factor to Ground
> > 4, !- Number of Vertices
> > -2.234534097, !- Vertex 1 X-coordinate {m}
> > -2.1541501501, !- Vertex 1 Y-coordinate {m}
> > 7, !- Vertex 1 Z-coordinate {m}
> > 4.2007186701, !- Vertex 2 X-coordinate {m}
> > -2.1541501501, !- Vertex 2 Y-coordinate {m}
> > 7, !- Vertex 2 Z-coordinate {m}
> > 4.2007186701, !- Vertex 3 X-coordinate {m}
> > 1.983811669, !- Vertex 3 Y-coordinate {m}
> > 7, !- Vertex 3 Z-coordinate {m}
> > -2.234534097, !- Vertex 4 X-coordinate {m}
> > 1.983811669, !- Vertex 4 Y-coordinate {m}
> > 7; !- Vertex 4 Z-coordinate {m}
> >
> > ! Block 2, Zone 1, Wall - 14.483 m2 - 90.0?, Surface Area: 14.483m2
> > BuildingSurface:Detailed,
> > Block2:Zone1_Wall_2_0_0, !- Name
> > Wall, !- Surface Type
> > Project wall, !- Construction Name
> > Block2:Zone1, !- Zone Name
> > Outdoors, !- Outside Boundary Condition
> > , !- Outside Boundary Condition Object
> > SunExposed, !- Sun Exposure
> > WindExposed, !- Wind Exposure
> > 0.5, !- View Factor to Ground
> > 4, !- Number of Vertices
> > 4.2007186701, !- Vertex 1 X-coordinate {m}
> > -2.1541501501, !- Vertex 1 Y-coordinate {m}
> > 3.5, !- Vertex 1 Z-coordinate {m}
> > 4.2007186701, !- Vertex 2 X-coordinate {m}
> > 1.983811669, !- Vertex 2 Y-coordinate {m}
> > 3.5, !- Vertex 2 Z-coordinate {m}
> > 4.2007186701, !- Vertex 3 X-coordinate {m}
> > 1.983811669, !- Vertex 3 Y-coordinate {m}
> > 7, !- Vertex 3 Z-coordinate {m}
> > 4.2007186701, !- Vertex 4 X-coordinate {m}
> > -2.1541501501, !- Vertex 4 Y-coordinate {m}
> > 7; !- Vertex 4 Z-coordinate {m}
> >
> > ! Block 2, Zone 1, Wall - 22.523 m2 - 0.0?, Surface Area: 22.523m2
> > BuildingSurface:Detailed,
> > Block2:Zone1_Wall_3_0_0, !- Name
> > Wall, !- Surface Type
> > Project wall, !- Construction Name
> > Block2:Zone1, !- Zone Name
> > Outdoors, !- Outside Boundary Condition
> > , !- Outside Boundary Condition Object
> > SunExposed, !- Sun Exposure
> > WindExposed, !- Wind Exposure
> > 0.5, !- View Factor to Ground
> > 4, !- Number of Vertices
> > 4.2007186701, !- Vertex 1 X-coordinate {m}
> > 1.983811669, !- Vertex 1 Y-coordinate {m}
> > 3.5, !- Vertex 1 Z-coordinate {m}
> > -2.234534097, !- Vertex 2 X-coordinate {m}
> > 1.983811669, !- Vertex 2 Y-coordinate {m}
> > 3.5, !- Vertex 2 Z-coordinate {m}
> > -2.234534097, !- Vertex 3 X-coordinate {m}
> > 1.983811669, !- Vertex 3 Y-coordinate {m}
> > 7, !- Vertex 3 Z-coordinate {m}
> > 4.2007186701, !- Vertex 4 X-coordinate {m}
> > 1.983811669, !- Vertex 4 Y-coordinate {m}
> > 7; !- Vertex 4 Z-coordinate {m}
> >
> > ! Block 2, Zone 1, Wall - 14.483 m2 - 270.0?, Surface Area: 14.483m2
> > BuildingSurface:Detailed,
> > Block2:Zone1_Wall_4_0_0, !- Name
> > Wall, !- Surface Type
> > Project wall, !- Construction Name
> > Block2:Zone1, !- Zone Name
> > Outdoors, !- Outside Boundary Condition
> > , !- Outside Boundary Condition Object
> > SunExposed, !- Sun Exposure
> > WindExposed, !- Wind Exposure
> > 0.5, !- View Factor to Ground
> > 4, !- Number of Vertices
> > -2.234534097, !- Vertex 1 X-coordinate {m}
> > 1.983811669, !- Vertex 1 Y-coordinate {m}
> > 3.5, !- Vertex 1 Z-coordinate {m}
> > -2.234534097, !- Vertex 2 X-coordinate {m}
> > -2.1541501501, !- Vertex 2 Y-coordinate {m}
> > 3.5, !- Vertex 2 Z-coordinate {m}
> > -2.234534097, !- Vertex 3 X-coordinate {m}
> > -2.1541501501, !- Vertex 3 Y-coordinate {m}
> > 7, !- Vertex 3 Z-coordinate {m}
> > -2.234534097, !- Vertex 4 X-coordinate {m}
> > 1.983811669, !- Vertex 4 Y-coordinate {m}
> > 7; !- Vertex 4 Z-coordinate {m}
> >
> > ! Block 2, Zone 1, Wall - 22.523 m2 - 180.0?, Surface Area: 22.523m2
> > BuildingSurface:Detailed,
> > Block2:Zone1_Wall_5_0_0, !- Name
> > Wall, !- Surface Type
> > Project wall, !- Construction Name
> > Block2:Zone1, !- Zone Name
> > Outdoors, !- Outside Boundary Condition
> > , !- Outside Boundary Condition Object
> > SunExposed, !- Sun Exposure
> > WindExposed, !- Wind Exposure
> > 0.5, !- View Factor to Ground
> > 4, !- Number of Vertices
> > -2.234534097, !- Vertex 1 X-coordinate {m}
> > -2.1541501501, !- Vertex 1 Y-coordinate {m}
> > 3.5, !- Vertex 1 Z-coordinate {m}
> > 4.2007186701, !- Vertex 2 X-coordinate {m}
> > -2.1541501501, !- Vertex 2 Y-coordinate {m}
> > 3.5, !- Vertex 2 Z-coordinate {m}
> > 4.2007186701, !- Vertex 3 X-coordinate {m}
> > -2.1541501501, !- Vertex 3 Y-coordinate {m}
> > 7, !- Vertex 3 Z-coordinate {m}
> > -2.234534097, !- Vertex 4 X-coordinate {m}
> > -2.1541501501, !- Vertex 4 Y-coordinate {m}
> > 7; !- Vertex 4 Z-coordinate {m}
> >
> > ! The following crack data is added for zone Block2:Zone1 to satisfy the AIRNET requirement for each AIRNET zone to have >= 2 flow connections
> > ! This zone only has 1 unique air flow paths to different zones/outside defined in the DesignBuilder model
> > ! dummy surface for crack
> > BuildingSurface:Detailed,
> > Extra Crack 1, !- Name
> > Wall, !- Surface Type
> > Link body, !- Construction Name
> > Block2:Zone1, !- Zone Name
> > Outdoors, !- Outside Boundary Condition
> > , !- Outside Boundary Condition Object
> > NoSun, !- Sun Exposure
> > NoWind, !- Wind Exposure
> > 0, !- View Factor to Ground
> > 3, !- Number of Vertices
> > 100001, !- Vertex 1 X-coordinate {m}
> > 0, !- Vertex 1 Y-coordinate {m}
> > 7, !- Vertex 1 Z-coordinate {m}
> > 100002, !- Vertex 2 X-coordinate {m}
> > 0, !- Vertex 2 Y-coordinate {m}
> > 7, !- Vertex 2 Z-coordinate {m}
> > 100002, !- Vertex 3 X-coordinate {m}
> > 1, !- Vertex 3 Y-coordinate {m}
> > 7; !- Vertex 3 Z-coordinate {m}
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: FENESTRATIONSURFACE:DETAILED ===========
> >
> > ! Window, 1.211m2
> > FenestrationSurface:Detailed,
> > Block1:Zone1_Wall_4_0_0_0_0_0_Win, !- Name
> > Window, !- Surface Type
> > 1001, !- Construction Name
> > Block1:Zone1_Wall_4_0_0, !- Building Surface Name
> > , !- Outside Boundary Condition Object
> > 0.5, !- View Factor to Ground
> > , !- Shading Control Name
> > 1, !- Frame and Divider Name
> > 1, !- Multiplier
> > 4, !- Number of Vertices
> > -2.234534097, !- Vertex 1 X-coordinate {m}
> > 0.<tel:2537962986>2537962986, !- Vertex 1 Y-coordinate {m}
> > 1.149626874, !- Vertex 1 Z-coordinate {m}
> > -2.234534097, !- Vertex 2 X-coordinate {m}
> > -.7568854095, !- Vertex 2 Y-coordinate {m}
> > 1.149626874, !- Vertex 2 Z-coordinate {m}
> > -2.234534097, !- Vertex 3 X-coordinate {m}
> > -.7568854095, !- Vertex 3 Y-coordinate {m}
> > 2.<tel:3479171554>3479171554, !- Vertex 3 Z-coordinate {m}
> > -2.234534097, !- Vertex 4 X-coordinate {m}
> > 0.<tel:2537962986>2537962986, !- Vertex 4 Y-coordinate {m}
> > 2.<tel:3479171554>3479171554; !- Vertex 4 Z-coordinate {m}
> >
> > ! Window, 1.610m2
> > FenestrationSurface:Detailed,
> > Block2:Zone1_Wall_5_0_0_0_0_0_Win, !- Name
> > Window, !- Surface Type
> > 1001, !- Construction Name
> > Block2:Zone1_Wall_5_0_0, !- Building Surface Name
> > , !- Outside Boundary Condition Object
> > 0.5, !- View Factor to Ground
> > , !- Shading Control Name
> > 1, !- Frame and Divider Name
> > 1, !- Multiplier
> > 4, !- Number of Vertices
> > 0.6757518142, !- Vertex 1 X-coordinate {m}
> > -2.1541501501, !- Vertex 1 Y-coordinate {m}
> > 4.5953754514, !- Vertex 1 Z-coordinate {m}
> > <tel:1.8782401037>1.8782401037, !- Vertex 2 X-coordinate {m}
> > -2.1541501501, !- Vertex 2 Y-coordinate {m}
> > 4.5953754514, !- Vertex 2 Z-coordinate {m}
> > <tel:1.8782401037>1.8782401037, !- Vertex 3 X-coordinate {m}
> > -2.1541501501, !- Vertex 3 Y-coordinate {m}
> > 5.934287367, !- Vertex 3 Z-coordinate {m}
> > 0.6757518142, !- Vertex 4 X-coordinate {m}
> > -2.1541501501, !- Vertex 4 Y-coordinate {m}
> > 5.934287367; !- Vertex 4 Z-coordinate {m}
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: WINDOWPROPERTY:FRAMEANDDIVIDER ===========
> >
> > WindowProperty:FrameAndDivider,
> > 1, !- Name
> > 0.040, !- Frame Width {m}
> > 0.0, !- Frame Outside Projection {m}
> > 0.0, !- Frame Inside Projection {m}
> > 9.5, !- Frame Conductance {W/m2-K}
> > 1.0, !- Ratio of Frame-Edge Glass Conductance to Center-Of-Glass Conductance
> > 0.5, !- Frame Solar Absorptance
> > 0.5, !- Frame Visible Absorptance
> > 0.9, !- Frame Thermal Hemispherical Emissivity
> > DividedLite, !- Divider Type
> > 0.020, !- Divider Width {m}
> > 1, !- Number of Horizontal Dividers
> > 1, !- Number of Vertical Dividers
> > 0.0, !- Divider Outside Projection {m}
> > 0.0, !- Divider Inside Projection {m}
> > 9.5, !- Divider Conductance {W/m2-K}
> > 1.0, !- Ratio of Divider-Edge Glass Conductance to Center-Of-Glass Conductance
> > 0.5, !- Divider Solar Absorptance
> > 0.5, !- Divider Visible Absorptance
> > 0.9, !- Divider Thermal Hemispherical Emissivity
> > 0.5, !- Outside Reveal Solar Absorptance
> > 0.0, !- Inside Sill Depth {m}
> > 0.5, !- Inside Sill Solar Absorptance
> > 0.0, !- Inside Reveal Depth {m}
> > 0.5; !- Inside Reveal Solar Absorptance
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: PEOPLE ===========
> >
> > People,
> > People Block1:Zone1, !- Name
> > Block1:Zone1, !- Zone or ZoneList Name
> > 2864, !- Number of People Schedule Name
> > People, !- Number of People Calculation Method
> > 6.7301631, !- Number of People
> > , !- People per Zone Floor Area {person/m2}
> > , !- Zone Floor Area per Person {m2/person}
> > 0.3, !- Fraction Radiant
> > AUTOCALCULATE, !- Sensible Heat Fraction
> > Activity Schedule 16, !- Activity Level Schedule Name
> > 0.0000000382, !- Carbon Dioxide Generation Rate {m3/s-W}
> > Yes, !- Enable ASHRAE 55 Comfort Warnings
> > ZoneAveraged, !- Mean Radiant Temperature Calculation Type
> > , !- Surface Name/Angle Factor List Name
> > Work efficiency, !- Work Efficiency Schedule Name
> > ClothingInsulationSchedule, !- Clothing Insulation Calculation Method
> > , !- Clothing Insulation Calculation Method Schedule Name
> > Clothing Schedule 16, !- Clothing Insulation Schedule Name
> > AirVelocitySchedule, !- Air Velocity Schedule Name
> > AdaptiveCEN15251; !- Thermal Comfort Model 1 Type
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:SIMULATIONCONTROL ===========
> >
> > AirflowNetwork:SimulationControl,
> > VENT, !- Name
> > MultizoneWithoutDistribution, !- AirflowNetwork Control
> > Input, !- Wind Pressure Coefficient Type
> > Cp Data, !- AirflowNetwork Wind Pressure Coefficient Array Name
> > OpeningHeight, !- Height Selection for Local Wind Pressure Calculation
> > LowRise, !- Building Type
> > 1000, !- Maximum Number of Iterations {dimensionless}
> > ZeroNodePressures, !- Initialization Type
> > 0.0001, !- Relative Airflow Convergence Tolerance {dimensionless}
> > 0.000001, !- Absolute Airflow Convergence Tolerance {kg/s}
> > -0.5, !- Convergence Acceleration Limit {dimensionless}
> > , !- Azimuth Angle of Long Axis of Building {deg}
> > ; !- Ratio of Building Width Along Short Axis to Width Along Long Axis
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:ZONE ===========
> >
> > AirflowNetwork:MultiZone:Zone,
> > Block1:Zone1, !- Zone Name
> > Temperature, !- Ventilation Control Mode
> > 20002, !- Ventilation Control Zone Temperature Setpoint Schedule Name
> > , !- Minimum Venting Open Factor {dimensionless}
> > , !- Indoor and Outdoor Temperature Difference Lower Limit For Maximum Venting Open Factor {deltaC}
> > , !- Indoor and Outdoor Temperature Difference Upper Limit for Minimun Venting Open Factor {deltaC}
> > , !- Indoor and Outdoor Enthalpy Difference Lower Limit For Maximum Venting Open Factor {deltaJ/kg}
> > , !- Indoor and Outdoor Enthalpy Difference Upper Limit for Minimun Venting Open Factor {deltaJ/kg}
> > 20001; !- Venting Availability Schedule Name
> >
> > AirflowNetwork:MultiZone:Zone,
> > Block2:Zone1, !- Zone Name
> > Temperature, !- Ventilation Control Mode
> > 20002, !- Ventilation Control Zone Temperature Setpoint Schedule Name
> > , !- Minimum Venting Open Factor {dimensionless}
> > , !- Indoor and Outdoor Temperature Difference Lower Limit For Maximum Venting Open Factor {deltaC}
> > , !- Indoor and Outdoor Temperature Difference Upper Limit for Minimun Venting Open Factor {deltaC}
> > , !- Indoor and Outdoor Enthalpy Difference Lower Limit For Maximum Venting Open Factor {deltaJ/kg}
> > , !- Indoor and Outdoor Enthalpy Difference Upper Limit for Minimun Venting Open Factor {deltaJ/kg}
> > 20001; !- Venting Availability Schedule Name
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:SURFACE ===========
> >
> > AirflowNetwork:MultiZone:Surface,
> > Block1:Zone1_Ceiling_1_0_0, !- Surface Name
> > Block1:Zone1_Ceiling_1_0_0, !- Leakage Component Name
> > , !- External Node Name
> > 1; !- Window/Door Opening Factor, or Crack Factor {dimensionless}
> >
> > AirflowNetwork:MultiZone:Surface,
> > Block1:Zone1_Wall_2_0_0, !- Surface Name
> > Block1:Zone1_Wall_2_0_0, !- Leakage Component Name
> > Block1:Zone1_Wall_2_0_0, !- External Node Name
> > 1; !- Window/Door Opening Factor, or Crack Factor {dimensionless}
> >
> > AirflowNetwork:MultiZone:Surface,
> > Block1:Zone1_Wall_3_0_0, !- Surface Name
> > Block1:Zone1_Wall_3_0_0, !- Leakage Component Name
> > Block1:Zone1_Wall_3_0_0, !- External Node Name
> > 1; !- Window/Door Opening Factor, or Crack Factor {dimensionless}
> >
> > AirflowNetwork:MultiZone:Surface,
> > Block1:Zone1_Wall_4_0_0, !- Surface Name
> > Block1:Zone1_Wall_4_0_0, !- Leakage Component Name
> > Block1:Zone1_Wall_4_0_0, !- External Node Name
> > 1; !- Window/Door Opening Factor, or Crack Factor {dimensionless}
> >
> > AirflowNetwork:MultiZone:Surface,
> > Block1:Zone1_Wall_4_0_0_0_0_0_Win, !- Surface Name
> > Block1:Zone1_Wall_4_0_0_0_0_0_Win, !- Leakage Component Name
> > Block1:Zone1_Wall_4_0_0_0_0_0_Win, !- External Node Name
> > 1, !- Window/Door Opening Factor, or Crack Factor {dimensionless}
> > Temperature, !- Ventilation Control Mode
> > 20002, !- Ventilation Control Zone Temperature Setpoint Schedule Name
> > , !- Minimum Venting Open Factor {dimensionless}
> > , !- Indoor and Outdoor Temperature Difference Lower Limit For Maximum Venting Open Factor {deltaC}
> > , !- Indoor and Outdoor Temperature Difference Upper Limit for Minimun Venting Open Factor {deltaC}
> > , !- Indoor and Outdoor Enthalpy Difference Lower Limit For Maximum Venting Open Factor {deltaJ/kg}
> > , !- Indoor and Outdoor Enthalpy Difference Upper Limit for Minimun Venting Open Factor {deltaJ/kg}
> > 2864; !- Venting Availability Schedule Name
> >
> > AirflowNetwork:MultiZone:Surface,
> > Block1:Zone1_Wall_5_0_0, !- Surface Name
> > Block1:Zone1_Wall_5_0_0, !- Leakage Component Name
> > Block1:Zone1_Wall_5_0_0, !- External Node Name
> > 1; !- Window/Door Opening Factor, or Crack Factor {dimensionless}
> >
> > AirflowNetwork:MultiZone:Surface,
> > Block2:Zone1_Wall_5_0_0_0_0_0_Win, !- Surface Name
> > Block2:Zone1_Wall_5_0_0_0_0_0_Win, !- Leakage Component Name
> > Block2:Zone1_Wall_5_0_0_0_0_0_Win, !- External Node Name
> > 1, !- Window/Door Opening Factor, or Crack Factor {dimensionless}
> > Temperature, !- Ventilation Control Mode
> > 20002, !- Ventilation Control Zone Temperature Setpoint Schedule Name
> > , !- Minimum Venting Open Factor {dimensionless}
> > , !- Indoor and Outdoor Temperature Difference Lower Limit For Maximum Venting Open Factor {deltaC}
> > , !- Indoor and Outdoor Temperature Difference Upper Limit for Minimun Venting Open Factor {deltaC}
> > , !- Indoor and Outdoor Enthalpy Difference Lower Limit For Maximum Venting Open Factor {deltaJ/kg}
> > , !- Indoor and Outdoor Enthalpy Difference Upper Limit for Minimun Venting Open Factor {deltaJ/kg}
> > 2864; !- Venting Availability Schedule Name
> >
> > AirflowNetwork:MultiZone:Surface,
> > Extra Crack 1, !- Surface Name
> > Extra Crack 1, !- Leakage Component Name
> > Extra Crack 1, !- External Node Name
> > 1; !- Window/Door Opening Factor, or Crack Factor {dimensionless}
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:REFERENCECRACKCONDITIONS ===========
> >
> > AirflowNetwork:MultiZone:ReferenceCrackConditions,
> > Reference Crack Conditions, !- Name
> > 20, !- Reference Temperature {C}
> > 101320, !- Reference Barometric Pressure {Pa}
> > 0.005; !- Reference Humidity Ratio {kgWater/kgDryAir}
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:SURFACE:CRACK ===========
> >
> > AirflowNetwork:MultiZone:Surface:Crack,
> > DefaultCrack, !- Name
> > 0.00000000001, !- Air Mass Flow Coefficient at Reference Conditions {kg/s}
> > 0.66, !- Air Mass Flow Exponent {dimensionless}
> > Reference Crack Conditions; !- Reference Crack Conditions
> >
> > AirflowNetwork:MultiZone:Surface:Crack,
> > Block1:Zone1_Ceiling_1_0_0, !- Name
> > 0.0239659, !- Air Mass Flow Coefficient at Reference Conditions {kg/s}
> > 0.7, !- Air Mass Flow Exponent {dimensionless}
> > Reference Crack Conditions; !- Reference Crack Conditions
> >
> > AirflowNetwork:MultiZone:Surface:Crack,
> > Block1:Zone1_Wall_2_0_0, !- Name
> > 0.0014483, !- Air Mass Flow Coefficient at Reference Conditions {kg/s}
> > 0.7, !- Air Mass Flow Exponent {dimensionless}
> > Reference Crack Conditions; !- Reference Crack Conditions
> >
> > AirflowNetwork:MultiZone:Surface:Crack,
> > Block1:Zone1_Wall_3_0_0, !- Name
> > 0.0022523, !- Air Mass Flow Coefficient at Reference Conditions {kg/s}
> > 0.7, !- Air Mass Flow Exponent {dimensionless}
> > Reference Crack Conditions; !- Reference Crack Conditions
> >
> > AirflowNetwork:MultiZone:Surface:Crack,
> > Block1:Zone1_Wall_4_0_0, !- Name
> > 0.0013272, !- Air Mass Flow Coefficient at Reference Conditions {kg/s}
> > 0.7, !- Air Mass Flow Exponent {dimensionless}
> > Reference Crack Conditions; !- Reference Crack Conditions
> >
> > AirflowNetwork:MultiZone:Surface:Crack,
> > Block1:Zone1_Wall_5_0_0, !- Name
> > 0.0022523, !- Air Mass Flow Coefficient at Reference Conditions {kg/s}
> > 0.7, !- Air Mass Flow Exponent {dimensionless}
> > Reference Crack Conditions; !- Reference Crack Conditions
> >
> > AirflowNetwork:MultiZone:Surface:Crack,
> > Extra Crack 1, !- Name
> > 0.00000000001, !- Air Mass Flow Coefficient at Reference Conditions {kg/s}
> > 0.5, !- Air Mass Flow Exponent {dimensionless}
> > Reference Crack Conditions; !- Reference Crack Conditions
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:COMPONENT:DETAILEDOPENING ===========
> >
> > AirflowNetwork:MultiZone:Component:DetailedOpening,
> > Block1:Zone1_Wall_4_0_0_0_0_0_Win, !- Name
> > 0.00014, !- Air Mass Flow Coefficient When Opening is Closed {kg/s-m}
> > 0.65, !- Air Mass Flow Exponent When Opening is Closed {dimensionless}
> > NonPivoted, !- Type of Rectanguler Large Vertical Opening (LVO)
> > 0, !- Extra Crack Length or Height of Pivoting Axis {m}
> > 2, !- Number of Sets of Opening Factor Data
> > 0, !- Opening Factor 1 {dimensionless}
> > 0.65, !- Discharge Coefficient for Opening Factor 1 {dimensionless}
> > 0, !- Width Factor for Opening Factor 1 {dimensionless}
> > 1, !- Height Factor for Opening Factor 1 {dimensionless}
> > 0, !- Start Height Factor for Opening Factor 1 {dimensionless}
> > 1, !- Opening Factor 2 {dimensionless}
> > 0.65, !- Discharge Coefficient for Opening Factor 2 {dimensionless}
> > 0.00000001, !- Width Factor for Opening Factor 2 {dimensionless}
> > 1, !- Height Factor for Opening Factor 2 {dimensionless}
> > 0, !- Start Height Factor for Opening Factor 2 {dimensionless}
> > 0, !- Opening Factor 3 {dimensionless}
> > 0, !- Discharge Coefficient for Opening Factor 3 {dimensionless}
> > 0, !- Width Factor for Opening Factor 3 {dimensionless}
> > 0, !- Height Factor for Opening Factor 3 {dimensionless}
> > 0, !- Start Height Factor for Opening Factor 3 {dimensionless}
> > 0, !- Opening Factor 4 {dimensionless}
> > 0, !- Discharge Coefficient for Opening Factor 4 {dimensionless}
> > 0, !- Width Factor for Opening Factor 4 {dimensionless}
> > 0, !- Height Factor for Opening Factor 4 {dimensionless}
> > 0; !- Start Height Factor for Opening Factor 4 {dimensionless}
> >
> > AirflowNetwork:MultiZone:Component:DetailedOpening,
> > Block2:Zone1_Wall_5_0_0_0_0_0_Win, !- Name
> > 0.00000001, !- Air Mass Flow Coefficient When Opening is Closed {kg/s-m}
> > 0.5, !- Air Mass Flow Exponent When Opening is Closed {dimensionless}
> > NonPivoted, !- Type of Rectanguler Large Vertical Opening (LVO)
> > 0, !- Extra Crack Length or Height of Pivoting Axis {m}
> > 2, !- Number of Sets of Opening Factor Data
> > 0, !- Opening Factor 1 {dimensionless}
> > 0.65, !- Discharge Coefficient for Opening Factor 1 {dimensionless}
> > 0, !- Width Factor for Opening Factor 1 {dimensionless}
> > 1, !- Height Factor for Opening Factor 1 {dimensionless}
> > 0, !- Start Height Factor for Opening Factor 1 {dimensionless}
> > 1, !- Opening Factor 2 {dimensionless}
> > 0.65, !- Discharge Coefficient for Opening Factor 2 {dimensionless}
> > 0.00000001, !- Width Factor for Opening Factor 2 {dimensionless}
> > 1, !- Height Factor for Opening Factor 2 {dimensionless}
> > 0, !- Start Height Factor for Opening Factor 2 {dimensionless}
> > 0, !- Opening Factor 3 {dimensionless}
> > 0, !- Discharge Coefficient for Opening Factor 3 {dimensionless}
> > 0, !- Width Factor for Opening Factor 3 {dimensionless}
> > 0, !- Height Factor for Opening Factor 3 {dimensionless}
> > 0, !- Start Height Factor for Opening Factor 3 {dimensionless}
> > 0, !- Opening Factor 4 {dimensionless}
> > 0, !- Discharge Coefficient for Opening Factor 4 {dimensionless}
> > 0, !- Width Factor for Opening Factor 4 {dimensionless}
> > 0, !- Height Factor for Opening Factor 4 {dimensionless}
> > 0; !- Start Height Factor for Opening Factor 4 {dimensionless}
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:EXTERNALNODE ===========
> >
> > AirflowNetwork:MultiZone:ExternalNode,
> > Block1:Zone1_Wall_2_0_0, !- Name
> > 2.33, !- External Node Height {m}
> > Block1:Zone1_Wall_2_0_0; !- Wind Pressure Coefficient Values Object Name
> >
> > AirflowNetwork:MultiZone:ExternalNode,
> > Block1:Zone1_Wall_3_0_0, !- Name
> > 2.33, !- External Node Height {m}
> > Block1:Zone1_Wall_3_0_0; !- Wind Pressure Coefficient Values Object Name
> >
> > AirflowNetwork:MultiZone:ExternalNode,
> > Block1:Zone1_Wall_4_0_0, !- Name
> > 2.33, !- External Node Height {m}
> > Block1:Zone1_Wall_4_0_0; !- Wind Pressure Coefficient Values Object Name
> >
> > AirflowNetwork:MultiZone:ExternalNode,
> > Block1:Zone1_Wall_4_0_0_0_0_0_Win, !- Name
> > 2.33, !- External Node Height {m}
> > Block1:Zone1_Wall_4_0_0_0_0_0_Win; !- Wind Pressure Coefficient Values Object Name
> >
> > AirflowNetwork:MultiZone:ExternalNode,
> > Block1:Zone1_Wall_5_0_0, !- Name
> > 2.33, !- External Node Height {m}
> > Block1:Zone1_Wall_5_0_0; !- Wind Pressure Coefficient Values Object Name
> >
> > AirflowNetwork:MultiZone:ExternalNode,
> > Block2:Zone1_Wall_5_0_0_0_0_0_Win, !- Name
> > 7.02, !- External Node Height {m}
> > Block2:Zone1_Wall_5_0_0_0_0_0_Win; !- Wind Pressure Coefficient Values Object Name
> >
> > AirflowNetwork:MultiZone:ExternalNode,
> > Extra Crack 1, !- Name
> > 0, !- External Node Height {m}
> > Extra Crack 1; !- Wind Pressure Coefficient Values Object Name
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:WINDPRESSURECOEFFICIENTARRAY ===========
> >
> > AirflowNetwork:MultiZone:WindPressureCoefficientArray,
> > Cp Data, !- Name
> > 0, !- Wind Direction 1 {deg}
> > 45, !- Wind Direction 2 {deg}
> > 90, !- Wind Direction 3 {deg}
> > 135, !- Wind Direction 4 {deg}
> > 180, !- Wind Direction 5 {deg}
> > 225, !- Wind Direction 6 {deg}
> > 270, !- Wind Direction 7 {deg}
> > 315; !- Wind Direction 8 {deg}
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:WINDPRESSURECOEFFICIENTVALUES ===========
> >
> > AirflowNetwork:MultiZone:WindPressureCoefficientValues,
> > Block1:Zone1_Wall_2_0_0, !- Name
> > Cp Data, !- AirflowNetwork:MultiZone:WindPressureCoefficientArray Name
> > -.3, !- Wind Pressure Coefficient Value 1 {dimensionless}
> > 0.1, !- Wind Pressure Coefficient Value 2 {dimensionless}
> > 0.4, !- Wind Pressure Coefficient Value 3 {dimensionless}
> > 0.1, !- Wind Pressure Coefficient Value 4 {dimensionless}
> > -.3, !- Wind Pressure Coefficient Value 5 {dimensionless}
> > -.35, !- Wind Pressure Coefficient Value 6 {dimensionless}
> > -.2, !- Wind Pressure Coefficient Value 7 {dimensionless}
> > -.35; !- Wind Pressure Coefficient Value 8 {dimensionless}
> >
> > AirflowNetwork:MultiZone:WindPressureCoefficientValues,
> > Block1:Zone1_Wall_3_0_0, !- Name
> > Cp Data, !- AirflowNetwork:MultiZone:WindPressureCoefficientArray Name
> > 0.4, !- Wind Pressure Coefficient Value 1 {dimensionless}
> > 0.1, !- Wind Pressure Coefficient Value 2 {dimensionless}
> > -.3, !- Wind Pressure Coefficient Value 3 {dimensionless}
> > -.35, !- Wind Pressure Coefficient Value 4 {dimensionless}
> > -.2, !- Wind Pressure Coefficient Value 5 {dimensionless}
> > -.35, !- Wind Pressure Coefficient Value 6 {dimensionless}
> > -.3, !- Wind Pressure Coefficient Value 7 {dimensionless}
> > 0.1; !- Wind Pressure Coefficient Value 8 {dimensionless}
> >
> > AirflowNetwork:MultiZone:WindPressureCoefficientValues,
> > Block1:Zone1_Wall_4_0_0, !- Name
> > Cp Data, !- AirflowNetwork:MultiZone:WindPressureCoefficientArray Name
> > -.3, !- Wind Pressure Coefficient Value 1 {dimensionless}
> > -.35, !- Wind Pressure Coefficient Value 2 {dimensionless}
> > -.2, !- Wind Pressure Coefficient Value 3 {dimensionless}
> > -.35, !- Wind Pressure Coefficient Value 4 {dimensionless}
> > -.3, !- Wind Pressure Coefficient Value 5 {dimensionless}
> > 0.1, !- Wind Pressure Coefficient Value 6 {dimensionless}
> > 0.4, !- Wind Pressure Coefficient Value 7 {dimensionless}
> > 0.1; !- Wind Pressure Coefficient Value 8 {dimensionless}
> >
> > AirflowNetwork:MultiZone:WindPressureCoefficientValues,
> > Block1:Zone1_Wall_4_0_0_0_0_0_Win, !- Name
> > Cp Data, !- AirflowNetwork:MultiZone:WindPressureCoefficientArray Name
> > -.3, !- Wind Pressure Coefficient Value 1 {dimensionless}
> > -.35, !- Wind Pressure Coefficient Value 2 {dimensionless}
> > -.2, !- Wind Pressure Coefficient Value 3 {dimensionless}
> > -.35, !- Wind Pressure Coefficient Value 4 {dimensionless}
> > -.3, !- Wind Pressure Coefficient Value 5 {dimensionless}
> > 0.1, !- Wind Pressure Coefficient Value 6 {dimensionless}
> > 0.4, !- Wind Pressure Coefficient Value 7 {dimensionless}
> > 0.1; !- Wind Pressure Coefficient Value 8 {dimensionless}
> >
> > AirflowNetwork:MultiZone:WindPressureCoefficientValues,
> > Block1:Zone1_Wall_5_0_0, !- Name
> > Cp Data, !- AirflowNetwork:MultiZone:WindPressureCoefficientArray Name
> > -.2, !- Wind Pressure Coefficient Value 1 {dimensionless}
> > -.35, !- Wind Pressure Coefficient Value 2 {dimensionless}
> > -.3, !- Wind Pressure Coefficient Value 3 {dimensionless}
> > 0.1, !- Wind Pressure Coefficient Value 4 {dimensionless}
> > 0.4, !- Wind Pressure Coefficient Value 5 {dimensionless}
> > 0.1, !- Wind Pressure Coefficient Value 6 {dimensionless}
> > -.3, !- Wind Pressure Coefficient Value 7 {dimensionless}
> > -.35; !- Wind Pressure Coefficient Value 8 {dimensionless}
> >
> > AirflowNetwork:MultiZone:WindPressureCoefficientValues,
> > Block2:Zone1_Wall_5_0_0_0_0_0_Win, !- Name
> > Cp Data, !- AirflowNetwork:MultiZone:WindPressureCoefficientArray Name
> > -.2, !- Wind Pressure Coefficient Value 1 {dimensionless}
> > -.35, !- Wind Pressure Coefficient Value 2 {dimensionless}
> > -.3, !- Wind Pressure Coefficient Value 3 {dimensionless}
> > 0.1, !- Wind Pressure Coefficient Value 4 {dimensionless}
> > 0.4, !- Wind Pressure Coefficient Value 5 {dimensionless}
> > 0.1, !- Wind Pressure Coefficient Value 6 {dimensionless}
> > -.3, !- Wind Pressure Coefficient Value 7 {dimensionless}
> > -.35; !- Wind Pressure Coefficient Value 8 {dimensionless}
> >
> > AirflowNetwork:MultiZone:WindPressureCoefficientValues,
> > Extra Crack 1, !- Name
> > Cp Data, !- AirflowNetwork:MultiZone:WindPressureCoefficientArray Name
> > 0, !- Wind Pressure Coefficient Value 1 {dimensionless}
> > 0, !- Wind Pressure Coefficient Value 2 {dimensionless}
> > 0, !- Wind Pressure Coefficient Value 3 {dimensionless}
> > 0, !- Wind Pressure Coefficient Value 4 {dimensionless}
> > 0, !- Wind Pressure Coefficient Value 5 {dimensionless}
> > 0, !- Wind Pressure Coefficient Value 6 {dimensionless}
> > 0, !- Wind Pressure Coefficient Value 7 {dimensionless}
> > 0; !- Wind Pressure Coefficient Value 8 {dimensionless}
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: SIZING:PARAMETERS ===========
> >
> > Sizing:Parameters,
> > 1.2, !- Heating Sizing Factor
> > 1.2, !- Cooling Sizing Factor
> > 2; !- Timesteps in Averaging Window
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:SENSOR ===========
> >
> > EnergyManagementSystem:Sensor,
> > Zonetemp1, !- Name
> > Block1:Zone1, !- Output:Variable or Output:Meter Index Key Name
> > Zone mean air temperature; !- Output:Variable or Output:Meter Name
> >
> > EnergyManagementSystem:Sensor,
> > Zonetemp2, !- Name
> > Block2:Zone1, !- Output:Variable or Output:Meter Index Key Name
> > Zone mean air temperature; !- Output:Variable or Output:Meter Name
> >
> > EnergyManagementSystem:Sensor,
> > Top1, !- Name
> > Block1:Zone1, !- Output:Variable or Output:Meter Index Key Name
> > Zone Operative Temperature; !- Output:Variable or Output:Meter Name
> >
> > EnergyManagementSystem:Sensor,
> > text, !- Name
> > , !- Output:Variable or Output:Meter Index Key Name
> > Site Outdoor Air Drybulb Temperature; !- Output:Variable or Output:Meter Name
> >
> > EnergyManagementSystem:Sensor,
> > tempmedmob, !- Name
> > People Block1:Zone1, !- Output:Variable or Output:Meter Index Key Name
> > Zone Thermal Comfort CEN 15251 Adaptive Model Running Average Outdoor Air Temperature; !- Output:Variable or Output:Meter Name
> >
> > EnergyManagementSystem:Sensor,
> > sched, !- Name
> > schedprova, !- Output:Variable or Output:Meter Index Key Name
> > schedule value; !- Output:Variable or Output:Meter Name
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:ACTUATOR ===========
> >
> > EnergyManagementSystem:Actuator,
> > MyOpenFactor1, !- Name
> > Block1:Zone1_Wall_4_0_0_0_0_0_Win, !- Actuated Component Unique Name
> > Airflow network window/door opening, !- Actuated Component Type
> > venting opening factor; !- Actuated Component Control Type
> >
> > EnergyManagementSystem:Actuator,
> > MyOpenFactor2, !- Name
> > Block2:Zone1_Wall_5_0_0_0_0_0_Win, !- Actuated Component Unique Name
> > Airflow network window/door opening, !- Actuated Component Type
> > venting opening factor; !- Actuated Component Control Type
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:PROGRAMCALLINGMANAGER ===========
> >
> > EnergyManagementSystem:ProgramCallingManager,
> > Temp_controlled_open_factor, !- Name
> > BeginTimestepBeforePredictor, !- EnergyPlus Model Calling Point
> > Temp_Opening_Controller1,!- Program Name 1
> > Temp_Opening_controller2;!- Program Name 2
> >
> > EnergyManagementSystem:ProgramCallingManager,
> > Initialize Random Number Generator, !- Name
> > BeginNewEnvironment, !- EnergyPlus Model Calling Point
> > InitRandomSeed; !- Program Name 1
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:PROGRAM ===========
> >
> > EnergyManagementSystem:Program,
> > InitRandomSeed, !- Name
> > Set seed = ActualDateAndTime, !- Program Line 1
> > Set dummy = @SeedRandom seed; !- Program Line 2
> >
> > EnergyManagementSystem:Program,
> > Temp_Opening_controller2,!- Name
> > if Zonetemp1>0, !- Program Line 1
> > set myopenfactor2 =@RandomUniform 0 1, !- Program Line 2
> > endif; !- A4
> >
> > EnergyManagementSystem:Program,
> > Temp_Opening_controller1,!- Name
> > if tempmedmob>10, !- Program Line 1
> > set tcomf=0.33*tempmedmob+18.8, !- Program Line 2
> > else, !- A4
> > set tcomf=0.09*tempmedmob+22.6, !- A5
> > endif, !- A6
> > set a=tcomf+2, !- A7
> > set b=tcomf-2, !- A8
> > set testerna=text, !- A9
> > set num=(2.71828^(0.171*top1+0.166*text-6.4)), !- A10
> > set den=(num+1), !- A11
> > set pw=(num/den), !- A12
> > run finestra1; !- A13
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:SUBROUTINE ===========
> >
> > EnergyManagementSystem:Subroutine,
> > finestra1, !- Name
> > if (sched>0), !- Program Line 1
> > set plim=@RandomUniform 0 1, !- Program Line 2
> > if ((Zonetemp1>a) || (Zonetemp1<b)), !- A4
> > if (pw>plim), !- A5
> > set myopenfactor1=1, !- A6
> > else, !- A7
> > set myopenfactor1=0, !- A8
> > endif, !- A9
> > endif, !- A10
> > else, !- A11
> > set myopenfactor1=0, !- A12
> > endif, !- A13
> > return; !- A14
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:GLOBALVARIABLE ===========
> >
> > EnergyManagementSystem:GlobalVariable,
> > testerna, !- Erl Variable 1 Name
> > pw, !- Erl Variable 2 Name
> > a, !- Erl Variable 3 Name
> > b, !- A4
> > tcomf, !- A5
> > plim; !- A6
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:OUTPUTVARIABLE ===========
> >
> > EnergyManagementSystem:OutputVariable,
> > temperatura esterna ems, !- Name
> > testerna, !- EMS Variable Name
> > Averaged, !- Type of Data in Variable
> > ZoneTimestep; !- Update Frequency
> >
> > EnergyManagementSystem:OutputVariable,
> > Probabilita finestra, !- Name
> > pw, !- EMS Variable Name
> > Averaged, !- Type of Data in Variable
> > ZoneTimestep; !- Update Frequency
> >
> > EnergyManagementSystem:OutputVariable,
> > Tcomf+2, !- Name
> > a, !- EMS Variable Name
> > Averaged, !- Type of Data in Variable
> > ZoneTimestep; !- Update Frequency
> >
> > EnergyManagementSystem:OutputVariable,
> > Tcomf-2, !- Name
> > b, !- EMS Variable Name
> > Averaged, !- Type of Data in Variable
> > ZoneTimestep; !- Update Frequency
> >
> > EnergyManagementSystem:OutputVariable,
> > P lim, !- Name
> > plim, !- EMS Variable Name
> > Averaged, !- Type of Data in Variable
> > ZoneTimestep; !- Update Frequency
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: OUTPUT:VARIABLEDICTIONARY ===========
> >
> > Output:VariableDictionary,
> > regular; !- Key Field
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: OUTPUT:SURFACES:LIST ===========
> >
> > Output:Surfaces:List,
> > Details; !- Report Type
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: OUTPUT:SURFACES:DRAWING ===========
> >
> > Output:Surfaces:Drawing,
> > DXF, !- Report Type
> > Triangulate3DFace; !- Report Specifications 1
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: OUTPUT:CONSTRUCTIONS ===========
> >
> > Output:Constructions,
> > Construction; !- Details Type 1
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: OUTPUT:ENERGYMANAGEMENTSYSTEM ===========
> >
> > Output:EnergyManagementSystem,
> > Verbose, !- Actuator Availability Dictionary Reporting
> > Verbose, !- Internal Variable Availability Dictionary Reporting
> > Verbose; !- EMS Runtime Language Debug Output Level
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: OUTPUT:TABLE:SUMMARYREPORTS ===========
> >
> > Output:Table:SummaryReports,
> > AnnualBuildingUtilityPerformanceSummary, !- Report 1 Name
> > SensibleHeatGainSummary, !- Report 2 Name
> > InputVerificationandResultsSummary, !- Report 3 Name
> > ClimaticDataSummary, !- Report 4 Name
> > EquipmentSummary, !- Report 5 Name
> > EnvelopeSummary, !- Report 6 Name
> > LightingSummary, !- Report 7 Name
> > HVACSizingSummary, !- Report 8 Name
> > SystemSummary, !- Report 9 Name
> > ComponentSizingSummary, !- Report 10 Name
> > OutdoorAirSummary, !- Report 11 Name
> > ObjectCountSummary; !- Report 12 Name
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: OUTPUTCONTROL:TABLE:STYLE ===========
> >
> > OutputControl:Table:Style,
> > CommaAndHTML, !- Column Separator
> > JtoKWH; !- Unit Conversion
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: OUTPUTCONTROL:REPORTINGTOLERANCES ===========
> >
> > OutputControl:ReportingTolerances,
> > 0.2, !- Tolerance for Time Heating Setpoint Not Met {deltaC}
> > 0.2; !- Tolerance for Time Cooling Setpoint Not Met {deltaC}
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: OUTPUT:VARIABLE ===========
> >
> > Output:Variable,
> > *, !- Key Value
> > Temp Media Mobile esterna giornaliera, !- Variable Name
> > Timestep; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > Site Outdoor Air Drybulb Temperature , !- Variable Name
> > Daily; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > Site Outdoor Air Drybulb Temperature, !- Variable Name
> > monthly; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > Site Outdoor Air Dewpoint Temperature, !- Variable Name
> > monthly; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > Site Outdoor Air Barometric Pressure, !- Variable Name
> > monthly; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > AFN Surface Venting Window or Door Opening Factor, !- Variable Name
> > Detailed; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > Temp Media Mobile esterna giornaliera; !- Variable Name
> >
> > Output:Variable,
> > *, !- Key Value
> > Site Outdoor Air Drybulb Temperature; !- Variable Name
> >
> > Output:Variable,
> > *, !- Key Value
> > Zone Thermal Comfort CEN 15251 Adaptive Model Running Average Outdoor Air, !- Variable Name
> > Timestep; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > Zone Operative Temperature, !- Variable Name
> > Hourly; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > Zone Operative Temperature, !- Variable Name
> > Daily; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > Zone Operative Temperature, !- Variable Name
> > Monthly; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > Zone Thermal Comfort CEN 15251 Adaptive Model Running Average Outdoor Air Temperature, !- Variable Name
> > Hourly; !- Reporting Frequency
> >
> > Output:Variable,
> > , !- Key Value
> > temperatura esterna ems, !- Variable Name
> > Timestep; !- Reporting Frequency
> >
> > Output:Variable,
> > , !- Key Value
> > probabilita finestra, !- Variable Name
> > Detailed; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > P lim, !- Variable Name
> > Detailed; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > Tcomf+2, !- Variable Name
> > Hourly; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > Tcomf-2, !- Variable Name
> > Hourly; !- Reporting Frequency
> >
> > Output:Variable,
> > schedprova, !- Key Value
> > schedule value, !- Variable Name
> > Detailed; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > People Total Heating Energy , !- Variable Name
> > Monthly; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > Zone Mean Air Temperature ; !- Variable Name
> >
> > Output:Variable,
> > *, !- Key Value
> > AFN Zone Infiltration Air Volume, !- Variable Name
> > Hourly; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > AFN Zone Infiltration Air Volume, !- Variable Name
> > Daily; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > AFN Zone Infiltration Air Volume, !- Variable Name
> > Monthly; !- Reporting Frequency
> >
> > Output:Variable,
> > *, !- Key Value
> > AFN Zone Infiltration Air Volume, !- Variable Name
> > Annual; !- Reporting Frequency
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: OUTPUT:METER ===========
> >
> > Output:Meter,
> > Volume infiltrazione totale, !- Name
> > Hourly; !- Reporting Frequency
> >
> > Output:Meter,
> > Volume infiltrazione totale, !- Name
> > Daily; !- Reporting Frequency
> >
> > Output:Meter,
> > Volume infiltrazione totale, !- Name
> > Monthly; !- Reporting Frequency
> >
> > Output:Meter,
> > Volume infiltrazione totale, !- Name
> > Annual; !- Reporting Frequency
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: OUTPUT:METER:METERFILEONLY ===========
> >
> > Output:Meter:MeterFileOnly,
> > Volume infiltrazione totale, !- Name
> > Hourly; !- Reporting Frequency
> >
> > Output:Meter:MeterFileOnly,
> > Volume infiltrazione totale, !- Name
> > Monthly; !- Reporting Frequency
> >
> > Output:Meter:MeterFileOnly,
> > Volume infiltrazione totale, !- Name
> > Daily; !- Reporting Frequency
> >
> > Output:Meter:MeterFileOnly,
> > Volume infiltrazione totale, !- Name
> > Annual; !- Reporting Frequency
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: METER:CUSTOM ===========
> >
> > Meter:Custom,
> > Volume infiltrazione totale, !- Name
> > Generic, !- Fuel Type
> > *, !- Key Name 1
> > AFN Zone Infiltration Air Volume; !- Output Variable or Meter Name 1
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: OUTPUT:SQLITE ===========
> >
> > Output:SQLite,
> > SimpleAndTabular; !- Option Type
> >
> >
> > !- =========== ALL OBJECTS IN CLASS: OUTPUT:DIAGNOSTICS ===========
> >
> > Output:Diagnostics,
> > DisplayAdvancedReportVariables; !- Key 1
> >
> 
> --
> Dr. Ery Djunaedy
> Research Scientist - Building Simulation Specialist
> Integrated Design Lab University of Idaho
> 306 S 6th ST, Boise, ID 83702
> Phone: <tel:208-429-0220>208-429-0220
> 




__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31514/stime=1394730070>

<https://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJldDN1dGYxBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5NDczMDA3MA-->Visit Your Group
* <https://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJmamhpYXNvBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTQ3MzAwNzA-?o=6>New Members 10
<https://groups.yahoo.com/;_ylc=X3oDMTJkaXVxbGg2BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzk0NzMwMDcw><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___