[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] epw file with measured values




The reported values after the run are excluding daylight savings shifts. The time that you see on the x-axis should in your case be UTC+1. At least that is my understanding.


2014-04-14 9:08 GMT+02:00 <<mailto:marko.ignjatovic1980@xxxxxxxxx>marko.ignjatovic1980@xxxxxxxxx>:
>  
Hi all,
> 
> I have measured main climatic parameters for the last several months and would like to create epw file. I know how to do it but i have several doubts and would like someone to check and comment if something I misunderstood:
> 1. all parameters are measured in UTC time, epw file contains standard local time values (in my case UTC +1)
> 2. my country follows DST convention (DST start last Sunday in March, DST ends last Sunday in October)
> 3. My intention is to calibrate E+model with data obtained through BMS which is in local time (during DST it is UTC+2, outside DST it is UTC+1)
> 4. I converted all measured outside parameters from UTC to UTC+1 (offsetting by +1 hour)
> 5. in IDF i stated DST Start and End dates (for the weather file I created - outside measured period existing epw vaules remained - not an issue since they are outside my RunPeriod)
> 6. My biggest concern: If I report environment variables during DST RunPeriod in hourly resolution, should them be read from epw file and have offset +1hour? - In my variables report it look like some interpolated values (close to those in epw file) are reported with no offset
> 
> Any help is welcome.
> 
> Sincerely





__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31720/stime=1397472110>

<https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlaWxxNGJyBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5NzQ3MjExMA-->Visit Your Group
* <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmcGc5M3AzBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTc0NzIxMTA->New Members 9
<https://groups.yahoo.com/neo;_ylc=X3oDMTJkZXVmMHZhBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzk3NDcyMTEw><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___