[EnergyPlus_Support] Re: Ventilation control strategy for ASHRAE 90.1 compliance



As with most things involving DCV, this is a sticky situation.



I think the best indiciation is to look at how the system would operate if you were to run it in the real world in your "Baseline" configuration. Would pumping 12,000 cfm of outdoor air into the zones in question without activating the exhaust fans overpressurize the space? Can the exhaust damper on the outdoor air unit handle 12,000 cfm, or does it require relief through the separate exhaust fans? If the Baseline configuration is not feasible, then you probably can't take credit for the savings.



Also, if outdoor air units are purely make up air units for the kitchen, then they are technically considered process energy, and therefore unregulated under Appendix G. And thus, required to be modeled identically between Baseline and Proposed cases unless an exceptional calculation measure can be demonstrated. In that case, you must demonstate that interlocking make up air and exhaust fans is not common practice, which is a hard sell.



Sorry to be contrary,





Luke







__._,_.___

 Posted by: luke.dorna@xxxxxxxxx

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=32237/stime=1402518266>

<https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJla29kZjg3BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTQwMjUxODI2Ng-->Visit Your Group
* <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmNWZpZHI3BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzE0MDI1MTgyNjY->New Members 12
<https://groups.yahoo.com/neo;_ylc=X3oDMTJkcm8zOXFwBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxNDAyNTE4MjY2><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___