Vincent

The efficacy of the lights is in your input, EnergyPlus will take
whatever you define as the efficacy.

If you define 10W/m2 for a zone, and your daylight sensor is set at
500 lux, then YOU are telling EnergyPlus that your light is at 50
lumen per watt.

You can change the LPD to 1 W/m2, with the same 500 lux setpoint, then
YOU are telling EnergyPlus that your light is at 500 lumen per watt.

EnergyPlus always assumes that in the absence of daylighting, your
electric lights will be able to meet the daylight sensor setpoint.

It's not a mystery under the hood, but it is simply your input.

Makes sense?

Ery


On Thu, 19 Jun 2014, vincent lacour vlacour@xxxxxxxxx [EnergyPlus_Support] wrote:

> Thanks Rahul, but this does not address the issue.  Everything in
> Daylighting:controls is inLUX whereas everything in Lights is in Watts.
>  What is missing is the efficiency of the lights, i.e. how much LUMEN you
> can get with 1W.  With a led you get 50 lumen; with an incandescent light
> bulb you get only 10 lumen.  There must be a lumen/watt ratio under the
> energyplus hood, but where????
> 
> 
> On Thu, Jun 19, 2014 at 6:09 PM, rahula7@xxxxxxxxx [EnergyPlus_Support] <
> EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
> 
> >
> >
> > If you look at the Daylighting:Controls object, there are a number of
> > fields:
> > - Lighting control type
> > - Minimum input power fraction for continuous dimming control
> > - Minimum input power fraction for continuous dimming control
> > - Number of control steps
> >
> > These fields combine to determine how much lighting power will be supplied
> > after subtracting the daylight contribution. It's all there in the I/O
> > Reference.
> >
> > Rahul
> >
> >  
> >

-- 
Dr. Ery Djunaedy
Research Scientist - Building Simulation Specialist
Integrated Design Lab University of Idaho
306 S 6th ST, Boise, ID 83702
Phone: 208-429-0220


------------------------------------
Posted by: Ery Djunaedy <ery.mailinglist@xxxxxxxxx>
------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.

------------------------------------

Yahoo Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo Groups is subject to:
    https://info.yahoo.com/legal/us/yahoo/utos/terms/