Are you talking about the CurvefitTool?

Located here: "C:\EnergyPlusV8-1-0\PreProcess\HVACCurveFitTool\CurveFitTool.xlsm"

(obviously replace the C:\EnergyPlusV8-1-0 to where you have installed it)

--
Julien Marrec, EBCP, BPI MFBA
Ingénieur en efficacité énergétique du bâtiment
T: +33 6 95 14 42 13
www.julienmarrec.com

DoYouBuzz : www.doyoubuzz.com/julien-marrec_1
LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr
LinkedIn (en) : www.linkedin.com/in/julienmarrec


2014-07-03 15:14 GMT+02:00 fpasserini.tn@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
 

Hello, I am not able to find the spreadsheet that "leads you to obtain the three curves after providing the performance chiller data values". Could you help me, please? 

I know the EER and the ESEER of a chiller (ESEER is the "European version" of the IPLV) but I have troubles calculating the coefficients of the EIRFPLR curve. I read at the following link that is more complicated than I thought: http://energyplus.helpserve.com/Knowledgebase/Comments/Submit/61/
Regards

 




---In EnergyPlus_Support@xxxxxxxxxxxxxxx, <nachogo27@...> wrote :

Hi,
You can read the documentation,the engineering reference pdf file.It has the chiller models very well explained.
I have also uploaded an spreadsheet to the yahoo group which leads you to obtain the three curves after providing the performance chiller data values.
I hope this can help you.
Ignacio Gomis

---------- Forwarded message ----------
From: andresdagm
Date: Tuesday, 31 July 2012
Subject: [EnergyPlus_Support] cop and iplv values of a chiller, also i have the part load performance
To: EnergyPlus_Support@xxxxxxxxxxxxxxx


 

dear,
Good day,
I have the cop and iplv values of a chiller, also i have the part load performance values of
EEFT Evaporator entering fluid temperature
ELFT Evaporator leaving fluid temperature
CEFT entering condenser water temperature
CLFT leaving condenser water temperature
CAP (ton)
PCT Power
kw/TR
for each part load(15,20,30...100%)

I dont know how to set it or how to transform it to can set this values in energy+, i think that the program could generate a curve with only COP and IPLv but i havent cant find that. Also i have tried to use Chiller:EIR and the EIRPLR curve is:

  EIRFPLR   y = 1.9927x2 - 1.9632x + 1.0078
R² = 0.9499

i dont know if it is correct, also i dont know set up the other 2 curves because both are for full load, well, i think that because there ae onl function of temperatures.

thank you in advance.


 




__._,_.___

Posted by: Julien Marrec <julien.marrec@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___