Electric Energy Use [GJ] | Electric Demand [W] | Natural Gas Energy Use [GJ] | Natural Gas Demand [W] | Additional Energy Use [GJ] | Additional Demand [W] | |
Interior Lighting | 209.22 | 15226.29 | 0.00 | 0.00 | 0.00 | 0.00 |
Exterior Lighting | 67.23 | 0.00 | 0.00 | 0.00 | 0.00 | 0.00 |
Space Heating | 0.12 | 0.00 | 29.71 | 123993.87 | 0.00 | 0.00 |
Space Cooling | 992.21 | 75817.96 | 0.00 | 0.00 | 0.00 | 0.00 |
......... | .............. |
|
ÂRemember that the Demand End Use Components Summary is the
power use for each end use component at the specific "time
of peak" shown at the top of the table when the peak demand
for the entire building for that energy was set. Exterior
lighting for example would probably not be part of the peak
electrical demand because it occurs at night and the peak is
probably set during the day. The same goes for heating and
cooling depending on the timing of the peak demand for the
building.
Jason
On 7/3/2014 12:20 PM, Jim Dirkesjim@xxxxxxxxxxxxxxxxxxxxxxxxxxx [EnergyPlus_Support] wrote:> *James V Dirkes II, PE, BEMP, LEED AP**
>
>
> I think I have seen this when the kW value is less than 0.5.
> I think some rounding occurs in the report creation. Does
> that apply for your system?
>
> **www.buildingperformanceteam.com*
> <http://www.buildingperformanceteam.com/>*
> **Energy Analysis, Commissioning & Training Services**
> *1631 Acacia Drive, Grand Rapids, MI 49504USA
> 616 450 8653
>
> *From:*EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
> *Sent:* Thursday, July 03, 2014 1:01 PM
> *To:* EnergyPlus_Support@xxxxxxxxxxxxxxx
> *Subject:* [EnergyPlus_Support] Summary reports problem -> report shows 0 W in the *Demand End Use Components Summary
> Demand end-use is 0 W, while energy end-use is not 0kWh
>
> Dear group,
>
> Has anyone encountered this problem before? The summary
> table, *while still having energy reported for that end-use> end-use categories, eg. this case *Exterior lightin*g, or on
> not 0?
>
> This happened in different projects and for different
> another project *cooling and heating*.
>
> Any thoughts on what might be the problem?
>
> Regards,
>
> Santiago
>
>
>
>