Remember that the Demand End Use Components Summary is the
power use for each end use component at the specific "time
of peak" shown at the top of the table when the peak demand
for the entire building for that energy was set. Exterior
lighting for example would probably not be part of the peak
electrical demand because it occurs at night and the peak is
probably set during the day. The same goes for heating and
cooling depending on the timing of the peak demand for the
building.
Jason
On 7/3/2014 12:20 PM, Jim Dirkes
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx [EnergyPlus_Support] wrote:
>
>
> I think I have seen this when the kW value is less than 0.5.
> I think some rounding occurs in the report creation. Does
> that apply for your system?
>
> *James V Dirkes II, PE, BEMP, LEED AP**
> **www.buildingperformanceteam.com*
> <http://www.buildingperformanceteam.com/>*
> **Energy Analysis, Commissioning & Training Services**
> *1631 Acacia Drive, Grand Rapids, MI 49504USA
> 616 450 8653
>
> *From:*EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
> *Sent:* Thursday, July 03, 2014 1:01 PM
> *To:* EnergyPlus_Support@xxxxxxxxxxxxxxx
> *Subject:* [EnergyPlus_Support] Summary reports problem -
> Demand end-use is 0 W, while energy end-use is not 0kWh
>
> Dear group,
>
> Has anyone encountered this problem before? The summary
> report shows 0 W in the *Demand End Use Components Summary
> table, *while still having energy reported for that end-use
> not 0?
>
> This happened in different projects and for different
> end-use categories, eg. this case *Exterior lightin*g, or on
> another project *cooling and heating*.
>
> Any thoughts on what might be the problem?
>
> Regards,
>
> Santiago
>
>
>
>
------------------------------------
Posted by: Jason Glazer <jglazer@xxxxxxxx>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
------------------------------------
Yahoo Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo Groups is subject to:
https://info.yahoo.com/legal/us/yahoo/utos/terms/