ÂJeremiah,
This has been discussed in the past on this forum and it seems that a number of us include a cooling system, but use a zone setpoint that effectively keeps cooling from turning on. I see that you are referring to another part of 90.1, the Energy Cost Budget, rather than Appendix G. Itâ??s language is similar, however.
(90.1-2010 Table G3.1 1b)Â All conditioned spaces in the proposed design shall be simulated as being both heated and cooled even if no heating or cooling system is to be installed. Temperature and humidity control setpoints and schedules as well as temperature control throttling range shall be the same for proposed and baseline building designs.
Exception: Spaces using Baseline System types 9 and 10 shall not be simulated with mechanical cooling.
Â
My logic has been this:
·        The minimum goal of Appendix G and USGBC is for the Proposed building to use 5% less energy annually than a fictitious â??Baselineâ?? building.
·        If we add cooling energy where none will exist, and assume that cooling adds 30 - 50% to the annual energy. The comparison becomes completely skewed away from the actual buildingâ??s energy use.
Â
Why does it make sense to say weâ??ve saved energy with a number that has no bearing on reality? Perhaps ASHRAE 90.1 allows, or even expects this skewed value, but I feel it does a disservice to our credibility as modelers. Of course, it may result in less LEED points, too?..
Â
Â
Â
James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653Â
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Monday, August 04, 2014 3:14 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] URGENT: LEED- Cooling Unmet Hours - ASHRAE 2010 - Heated Only Storage - System 9 or 10Â
Â
My understanding of ASHRAE 90.1 indicates that you can not simply turn the thermostat way up or off. I think what you need to do for your model is to use a theoretical system per ASHRAE 90.1 requirements, eg a packaged single zone air cooled system. Â I have included some images below that may help.Â
Â
Do you have a copy of the standard and users guide? If not you should most likely get yourself a copy.Â
Â
Â
Â
Â
Â
Â
â??â??
Jeremiah D. Crossett  | Senior Analyst  | LEED Green AssociateÂ
â??â??
120 E. Pritchard St. Â | Asheboro, NC 27203Â
â??â??
 | Mobile 503-688-8951
 Â
Â
Â
Â
Â
On Sun, Aug 3, 2014 at 11:01 PM, hisham.rashrash@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
Â
Dear Santiago,
Many thanks, can you please show me a snapshot of where this option is in DB? I am using detailed HVAC mode, is this option valid for this mode also?
Â
If I am following this correctly, does it mean that setting a very high cooling setpoint also solves this problem and unmet hours will be zero for these spaces?
Â
Your help is appreciated.
Â
Hisham
Â
__._,_.___