Re: [EnergyPlus_Support] UFAD+Radiant Ceiling System Modeling Guidence





I don't think this is do-able directly.
Usually we supply 6/12 to the AHU and 15/18 to the ceiling. The ceiling gets it water indirectly via either a tank or water-water plate heatexchanger which recieves 6/12 but supplies 15/18.

You can't connect one AHU coil to two loops, so either use 2 coils (one for each temperature) or perhaps supply it via a heatexchanger or tank where you can set changing supply temps...but I reckon you'll get quite a few reverse action / normal action control warnings from your coil controller.

Mit freundlichen GrüÃ?en- Sent from my iPhone (excuse the brevity)

i. A.
Jean Marais
b.i.g. bechtold
Tel.   +49 30 6706662-23

On 07.08.2014, at 13:50, "Javed Iqbal eee.javed@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:

 

Dear All,

I am trying to model a complex HVAC system to evaluate annual performance in climatic zone 1A. Here are some details on system arrangements and operational priority:

  1. The central plant has two chillers generating chilled water at 15/19 degC and 6/12 degC. 
  2. Each floor will be served by UFAD and Ceiling supply Radiant system. The UFAD supplied with AHU supply chilled water temperature of 6/12 degC whereas Ceiling Radiant system with chilled water supply of 15/19 degC  to cater Sensible and Latent Heat inside thermal zone.
  3. There is DOAS installed to cater OA load. The DOAS AHU coil will be supplied with two chilled water supply, one at 15/19degC and second at 6/12degC. 
Has anyone successfully modeled such mechanical configuration in Eplus. I would appreciate to get expert advice on following points:
  1. Is it possible to model above plant configuration in EPlus?
  2. Is it possible to create two loop supply at different temperature for a Air Handling Unit?
  3. Is it possible to create two systems operating simultaneously for a zone in EPlus?
Any technical advice or references would be highly appreciated.

Thanks in advance,

--


Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst 







__._,_.___

Posted by: "jeannieboef@xxxxxxxxx" <jeannieboef@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.





__,_._,___