RE: [EnergyPlus_Support] Tempering Valve in DHW loop with a solar tank [1 Attachment]





Dear Mr. Griffith,

thanks for the prompt response.

It is a WaterHeater:Mixed. In my opinion it is not the solar tank which causes the high DHW energy demand. It is rather the tempering valve which does not regulate the mass flow rate properly.

As you can see in the attached diagram, there is always a mass flow rate on the use side of the solar tank regardless of the inlet and outlet temperature. There should only be a mass flow rate when the inlet temperature is higher than the outlet temperature.

Another problem is the setpoint node you have to specify in the TemperingValve. Obviously is must be the same node of the plant loop (setpoint temperature 60°C). So if the the solar tank temperature is higher than 60 °C the tempering valve tries to decrease this mass flow by mixing it up with the return flow of the DHW demand loop. 

Regards,
Christian


__._,_.___
View attachments on the web

Posted by: ricci.richter@xxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
PrivacyUnsubscribeTerms of Use

__,_._,___
Attachment Converted: "d:\eudora\attach\140828 Mass flow regulation of TemperingValve.pdf"