The output you cite is for absorbed solar, not incident. If you really want incident, I’d suggest using the output variable “Surface Outside Face Incident Solar Radiation Rate per Area” and take the value for the base surface that surrounds the window subsurface. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] It seems "Surface Outside Face Solar Radiation Heat Gain Energy" will only report solar radiation incident for non-window surfaces. __._,_.___ Posted by: "Brent Griffith" <Brent.Griffith@xxxxxxxxxxxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |