Dear Jim,
Is this method of calculation also valid for VRF systems? In e+ output I couldn't find VRF COPs reported, neither nominal nor AHRI. How can I get them in output?

Thank you for your helpful contributions.

Hisham

---In EnergyPlus_Support@xxxxxxxxxxxxxxx, <jim@...> wrote :

Francesco,

I am not able to stop and look carefully at your message, but I think the following (from my personal notes) may help?.

 

Equivalent COP calculation (How to specify a DX coil in EnergyPlus so a desired COP results)

EnergyPlus calculates DX coil energy by using a COP value that is defined differently than that used by manufacturers of packaged air

conditioning equipment.

For all equipment, the definition of COP is (cooling capacity / power), with both terms expressed in the same units.

Manufacturers and AHRI (their rating organization) define the terms as:

Cooling capacity  = total cooling capacity of the system

Power = Total equipment power, including supply fan, compressor, condenser fans and controls

EnergyPlus defines the COP terms for a DX coil as:

Cooling capacity  = total cooling capacity of the system  (same as manufacturers)

Power = compressor and condenser fans  (Note: No supply fan or controls!)

Most real-world packaged air conditioning equipment is not applied with the same operating conditions as exist in the AHRI test setup,

so EnergyPlus is well justified to do things differently than AHRI.  Nonetheless, because of the different definitions, an EnergyPlus user

must derive an equivalent COP for the DX coil that will result in something close to the manufacturer's actual energy performance.

Conveniently, controls use very little power, the AHRI test conditions require a specific small fan pressure, and fan efficiency and system Î?T

fall in a relatively narrow range. This means that the power burden of fan and controls is very proportional to cooling capacity for this

type of equipment.  EnergyPlus defaults to a value of  0.365 W/cfm (773.3 W / m3/s) for the combination of fan and controls.

For an AHRI-rated packaged AC equipment manufacturer:

COPahri =

Qtotal

Eqn #1; where both Q and P are both expressed in Watts or BTUH

Ptotal

This can be expressed as:

COPahri =

Qtotal

Eqn #2; where Pfan includes the supply fan and controls

Pdx + Pfan

For an EnergyPlus DX coil:

            COPe+ =

Qtotal

Eqn #3; where Pdx is the power of compressor and condenser fans (only)

Pdx

If we assume that Pfan can be considered a constant (K) and that K = airflow * 773.3 W / m3/s, Eqn #2 becomes:

COPahri =

Qtotal

Pdx + 773.3 * Airflow

(airflow in m3/s)

Qtotal =

COPahri * (Pdx + 773.3 * Airflow)

Qtotal =

COPahri*Pdx + COPahri*773.3*Airflow

AHRI fan power1:

773.3

W / m3/s

Qtotal - COPahri*773.3*Airflow =

COPahri*Pdx

Ref: AHRI 210/240-2008 pp4, 5

365.0

W / 1000 cfm

for split systems

Pdx =

Qtotal - COPahri*773.3*Airflow

Eqn #4

2,118.64

cfm (1 m3/s)

COPahri

1.555

delta P

0.500

fan efficiency

Then, substituting Pdx into Eqn #3 :

773.3

Power (watts)

            COPe+ =

Qtotal

Qtotal - COPahri*773.3*Airflow

COPahri

AHRI fan power2:

200

W / m3/s

            COPe+ =

Qtotal * COPahri

Eqn #5

Ref: BPT estimate

94.4

W / 1000 cfm

Qtotal - COPahri*773.3*Airflow

for self-contained (e.g., PTAC) systems

2,118.64

cfm (1 m3/s)

or (since most US manufacturers use EER instead of COP):

0.400

delta P

            COPe+ =

Qtotal * EERahri / 3.412

Eqn #6

0.500

fan efficiency

Qtotal - EERahri/3.412*773.3*Airflow

198.9

Power (watts)

ASHRAE 90.1 minimum efficiency tables cite specific AHRI standards, so it is appropriate to assume the above COP derivation for Baseline

systems. Proposed systems will use the manufacturer data for EER.

Note:

For ASHRAE 90.1-compliant energy models, the "baseline" specified fan power is much greater than what is included for an AHRI-rated



__._,_.___

Posted by: hisham.rashrash@xxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___