694.44W/m2 = (2*2500/18+0.25*2*2500/18)*2 =
2 blade server racks @ 128 servers per rack = 2*25 kW + 25% ancillary equipment (data storage, UPS, etc.) + 100% future growth in server closet 18m2

Australian Minimum Energy Performance Standards
http://www.energyrating.gov.au/wp-content/uploads/Energy_Rating_Documents/Product_Profiles/Other/Data_Centres/200905-data-centre-efficiency.pdf

...alternatively ASHRAE Journal Feb 2013, Internal IT Load Profile Variability = 538 to 2153 W/m2 for Data Centers and 108 to 161 W/m2 for offices


2014-09-26 16:10 GMT+02:00 Jim Dirkes jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
 

Dear forum,

It is routine for a small â?? medium building to contain a â??data roomâ?? for servers and telephone equipment.  This small room may be served by an air conditioning system that is also small ? less than ~5kW.>

I am looking for information or research about the load profile for this type of installation and cannot find anything except for larger data centers.  Can you tell me of something that is applicable?

Thanks in advance for your help.

 

BPT-e-mail-signature-template_readable-text

 

The more one does what is good, the freer one becomes. There is no true freedom except in the service of what is good and just.

 




__._,_.___

Posted by: Jean Marais <jeannieboef@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___