[EnergyPlus_Support] Re: Can HVAC system take air from earth tubes instead of ambient?





Hi all,

First of all I would like to thank you for the great solution you find for the EarthTube issue. I had to set up earth tubes in my model and I encountered the same problem as you. But after using your EMS code, this problem seems to be perfectly solved!

As of now, I am trying to get more accurate results on my earth tube system simulations but I find another shortcoming of the E+ EarthTube object.

In my actual building I have an earth-tube system which consists of 7 pipes (50m lenght each) that feed the HVAC system of the building for pre-cooling. But E+ only allows to set up 1 pipe per Zone so I'm afraid that the simulation results may differ from the real performance.

So far, only two alternatives I have thought of are:
 1. Set up and equivalent length (1 pipe of 350m) or
 2. Divide my room into 7 equal zones and set one EarthTube in each of them

First alternative I think, it may affect in a wrong way to the pressure drop in the pipe, thus to the Fan Electricity consumption
As for the second one, I'm not sure if the outlet temperatures coming of the EarthTube will still be consistent according to the actual performance due to mixing and heat gains.

I would really appreciate any comments or solutions.

Thank you!!

Cheers

Marcos Perez-Vazquez



__._,_.___

Posted by: marcusbrown1326@xxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___