Re: [EnergyPlus_Support] questions regarding the heat recovery VRF systems
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: Re: [EnergyPlus_Support] questions regarding the heat recovery VRF systems
- From: "Richard Raustad RRaustad@xxxxxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
- Date: Thu, 09 Oct 2014 12:19:23 -0400
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Thu, 09 Oct 2014 10:19:37 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1412871569; bh=lNm1QcPhE5u/TfxWDM2yslvueIIZoBhh4CBf4KyDNF8=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:In-reply-to:To:Message-id:Organization:User-Agent:References:X-Originating-IP:X-Original-From:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding:From:Subject; b=3nBXbDSY46WmgWHI4xyKAiT+6li7srFs72eVUBK//rfyicy1npl50nZXpkvTXgZcfTs8KFKjOhIm2+PivzFo8QJ+ngkw1jqxKMRUY8SWcva0keSmjKkixYwEXeKTO77tJT4/kdsk4u50ys+6Ffotp5mJy7Zv25Fs2X0D3eLeFDo=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echoe; d=yahoogroups.com; b=0KQZFQ17qkIdFR+/5n1Co2xJ5j0eiUtNEppi2SNzpdXQ+zEp52V6hKdJe1MBq9AEcnw2Jm8CJuUva3Y7kll8Fx4/kdkj+dkl0JT4elVga4WEmqlXaXeSfE9SkftNpk21kxDo2+hZk5jtjc4XOtCZu1aBG0zTfzQTSbUVWaajlIs=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- In-reply-to: <m16att+6vl0uj@YahooGroups.com>
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Organization: Florida Solar Energy Center
- References: <m16att+6vl0uj@YahooGroups.com>
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: Mozilla/5.0 (Windows NT 6.1; WOW64; rv:24.0) Gecko/20100101 Thunderbird/24.6.0
That field means the VRF system can simultaneously cool and heat the
zones. For example, one zone connected to a single VRF system condenser
requires cooling and another requires heating, at the same time.
Check to see if any of the terminal units are ever operating in
different modes.
The report variable VRF Heat Pump Operating Mode will NOT tell you if
simultaneous cooling and heating occurs, only what operating mode the
condenser is using at the current time step.
You could report for all terminal units:
Zone VRF Air Terminal Total Cooling Rate
Zone VRF Air Terminal Total Heating Rate
If all terminal units only show a cooling (or heating) rate, the VRF
system is NOT simultaneously cooling and heating.
------------------------------------
Posted by: Richard Raustad <rraustad@xxxxxxxxxxxx>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
------------------------------------
Yahoo Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo Groups is subject to:
https://info.yahoo.com/legal/us/yahoo/utos/terms/