Re: [EnergyPlus_Support] Outdoor Air / Mechanical Ventilation in VRF





I noticed what Jim mentioned as well-- Also for for the report you are looking for I think you need to specify "VentilationRateProcedure" in the System Outdoor Air Method field of the system sizing, see below.

AirLoop Name DOASBuilding2:EastClassrooms
Type of Load to Size On VentilationRequirement
Design Outdoor Air Flow Rate autosize
Minimum System Air Flow Ratio 1.0
Preheat Design Temperature 2
Preheat Design Humidity Ratio 0.008
Precool Design Temperature 11
Precool Design Humidity Ratio 0.008
Central Cooling Design Supply Air Temperature -17.7777777777778
Central Heating Design Supply Air Temperature -17.7777777777778
Sizing Option NonCoincident
100% Outdoor Air in Cooling Yes
100% Outdoor Air in Heating Yes
Central Cooling Design Supply Air Humidity Ratio 0
Central Heating Design Supply Air Humidity Ratio 0
Cooling Design Air Flow Method DesignDay
Cooling Design Air Flow Rate 0
Heating Design Air Flow Method DesignDay
Heating Design Air Flow Rate 0
System Outdoor Air Method VentilationRateProcedure
Zone Maximum Outdoor Air Fraction




â??â??
Jeremiah D. Crossett
 
 | Senior Analyst  | LEED Green Associate 
â??â??
7411 SW Capitol Highway | Portland, OR 97219 
â??â??
 | Mobile 503-688-8951
  




On Mon, Oct 27, 2014 at 10:30 AM, adriana.lira@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hi Jim!


I have two systems in this model:
1.- Central system, where the zones have 0 people, indeed.
2.- VRF Terminal Units, which zones do have people. These zones are:
      - TECBLG1F:INFOMAINTENANCE
      - TECBLG1F:OPERATIONS
      - OFFBLG1F:OPENOFFICE
      - OFFBLG1F:RECEPTION
    &nbs p; - OFFBLG1F:CONFROOM2
      - OFFBLG1F:CONFROOM1
      - OFFBLG2F:OFFICE2
  &nb sp;   - OFFBLG2F:OPENOFFICE
      - OFFBLG2F:OFFICE1

 When I simulate the model, the OUTDOOR AIR SUMMARY section of the report, shows zero mechanical ventilation. 

Reading previous conversations, I noticed that several people had the same problem regarding VRF systems, before.

Have you modeled VRF?

Best,

Adriana
    
     




__._,_.___

Posted by: Jeremiah Crossett <jcrossett@xxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___