|
HI Jim, Your air terminal is zero-sized, AirTerminal:SingleDuct:VAV:Reheat, VAV_LLRecRm, Sched_AlwaysOn, NodeOut_VVDpr_LLRecRm, NodeOut_ZnSpltr_LLRecRm, 0, Constant, 0.3, 0, , Coil:Heating:Water, Coil-Rht_LLRecRm, Autosize, 0, NodeIn_Zn_LLRecRm, 0.001, Reverse; In EnergyPlus, the air flow rates are set by the air terminal units. The fan tries to respond to the air terminal requests but if they are zero then the fan will not run. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] Dear Forum, I have defined a simple system with a VAV fan serving several zones. Throughout the year, the fan never produces flow, despite:
I have not been able to determine how the fan can be scheduled "on" and produce no flow... Thanks in advance for your assistance. -- James V Dirkes II, PE, BEMP, LEED AP The more one does what is good, the freer one becomes. There is no true freedom except in the service of what is good and just. __._,_.___ Posted by: "Brent Griffith" <Brent.Griffith@xxxxxxxxxxxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |