[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Fan will not produce airflow





Oh.  My.  Goodness.
I looked everywhere ... except there.  Thank you!

On Mon, Nov 3, 2014 at 7:34 AM, 'Brent Griffith' brent.griffith@xxxxxxxxxxxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

HI Jim,

 

Your air terminal is zero-sized,

 

AirTerminal:SingleDuct:VAV:Reheat,

VAV_LLRecRm,

Sched_AlwaysOn,

NodeOut_VVDpr_LLRecRm,

NodeOut_ZnSpltr_LLRecRm,

0,

Constant,

0.3,

0,

,

Coil:Heating:Water,

Coil-Rht_LLRecRm,

Autosize,

0,

NodeIn_Zn_LLRecRm,

0.001,

Reverse;

 

In EnergyPlus, the air flow rates are set by the air terminal units.  The fan tries to respond to the air terminal requests but if they are zero then the fan will not run.

 

 

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Saturday, November 1, 2014 2:08 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Fan will not produce airflow [2 Attachments]

 

 

Dear Forum,

I have defined a simple system with a VAV fan serving several zones.  Throughout the year, the fan never produces flow, despite:

  • The fan schedule is ON as expected for many hours
  • Various zones have a cooling demand and unmet cooling loads
  • The discharge air setpoint for the air loop is lower than the actual temperature
  • The fan is autosized at about 11 m3/s, i.e. it's not zero.

I have not been able to determine how the fan can be scheduled "on" and produce no flow...

Thanks in advance for your assistance.

 

 

--

 

James V Dirkes II, PE, BEMP, LEED AP
The Building Performance Team
1631 Acacia Drive, Grand Rapids, MI 49504
(M) 616 450 8653

The more one does what is good, the freer one becomes. There is no true freedom except in the service of what is good and just.




--

 

James V Dirkes II, PE, BEMP, LEED AP
The Building Performance Team
1631 Acacia Drive, Grand Rapids, MI 49504
(M) 616 450 8653

The more one does what is good, the freer one becomes. There is no true freedom except in the service of what is good and just.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___
Attachment not found:
C:\Users\lklawrie\Downloads\Embedded\BPT Logo 35pct7.png