[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: "strange" autosize of Coil:Cooling:DX:SingleSpeed





I wonder why sizing of any sort matters to the reviewers when the coil is not used.  In other words, I agree.
It may be worth an explanation to the reviewers, since they seem to be unfamiliar with how E+ does its work.

On Fri, Dec 5, 2014 at 10:44 AM, fpasserini.tn@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Thank you, Jim.

The problem is that the reviewers wrote that the cooling capacity of the baseline model seems to be oversized (17 times). They have compared the sum of the capacities of the Coil:Cooling:DX:SingleSpeed objects with â??COOLING:ELECTRICITY {Maximum}[W]â?? (report PeakEnergyEndUseElectricityPart2Monthly) and the ratio is about 17. The fact is that a lot of spaces are not cooled in the real building and for them I imposed a cooling setpoint temperature equal to 40°C (both for the design day and for the annual simulation).

Iâ??m trying to understand how the cooling coils are autosized when in the table â??Zone Coolingâ?? the â??Calculated Design Loadâ??, â??User Design Loadâ??, â??Calculated Design Air Flowâ??, and â??User Design Air Flowâ?? are equal to 0. In EngineeringReference.pdf Iâ??m reading the paragraph â??DX Coil Sizingâ?? . It seems that to autosize the DX cooling coil EnergyPlus considers the â??rated air flow rateâ??, which is â??the maximum of the heating and cooling design flow rates from the design arrayâ??. If I have understood the reference guide correctly, the DX cooling coil is autosized in order to cool the "rated air flow rate" to the supply temperature, which is evaluated by the setpointmanager (in this case SetpointManager:SingleZone:Cooling).  

I could explain to the reviewers that since those coils never work they donâ??t affect the energy requirements.

Do you agree?

Best Regards



---In EnergyPlus_Support@xxxxxxxxxxxxxxx, <jim@...> wrote :

Francesco,
I think E+ sizes a coil whenever it does autosizing, but its size or capacity has nothing to do with whether it actually is used.
I often include a coil in my objects because its part of a template, but just schedule it to be OFF.  E+ sizes it, but never actually uses the coil., so energy = 0.  It's normal and OK.

On Thu, Dec 4, 2014 at 12:34 PM, fpasserini.tn@... [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

I'm autosizing HVAC systems according to appendix G of ASHRAE 90.1 (baseline model). They are Systems 3 (PSZ-AC Packaged rooftop air conditioner).

In a zone where in the real building there is no cooling I have imposed 40°C as cooling setpoint. I can see in the .eso output that during the design day the zone temperature is always less than 40°C and the â??Cooling Coil Total Cooling Rateâ?? (Coil:Cooling:DX:SingleSpeed) is always equal to 0 W. Moreover, in the .html report â??HVAC Sizing Summaryâ?? in the table â??Zone Coolingâ?? the â??Calculated Design Loadâ?? and the â??User Design Loadâ?? are equal to 0. Nevertheless, in the table â??DX cooling coilâ?? of the html report â??Equipment Summaryâ?? the â??Standard Rated Net Cooling Capacity [W]â?? is not 0 (it is quite high? 35603 W). Why? If the design load is 0 and thee coil is autosized, then its capacity should be equal to 0, shouldn't it?

The coil is controlled by SetpointManager:SingleZone:Cooling

The system doesn't provide outdoor air.

In Sizing:System the "Cooling Design Air Flow Method" is DesignDay.

With Regards

Francesco




--

 

James V Dirkes II, PE, BEMP, LEED AP
The Building Performance Team
1631 Acacia Drive, Grand Rapids, MI 49504
(M) 616 450 8653

If I decide to act with strength and honor in some instances, but not always, I have made my integrity optional.  It's all or nothing.




--

 

James V Dirkes II, PE, BEMP, LEED AP
The Building Performance Team
1631 Acacia Drive, Grand Rapids, MI 49504
(M) 616 450 8653

If I decide to act with strength and honor in some instances, but not always, I have made my integrity optional.  It's all or nothing.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___
Attachment not found:
C:\Users\lklawrie\Downloads\Embedded\BPT Logo 35pct22.png