…to partially answer my own question, E+ apparently has a problem controlling loop temperature when the loop flow is greater than it needs (why bypass doesn’t
seem to help I don’t know). Once I let my main loop pump slow to zero flow (I initially slowed to about 20% flow for typical VFD control) and autosize it instead of using the flows from the ME, loop temperature control improved… I am uncertain if the control properly cascades through the heat exchanger isolations I am using. Ned Lyon, P.E. (MA, WV) SIMPSON GUMPERTZ & HEGER
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
I am modeling a proposed design for a mixed loop water to air HVAC system. The cooling tower and boilers are connected to the mixed loop by heat exchangers. I’m having trouble
controlling the mixed loop temperature and plant operation. For instance for the cooling tower, the mixed loop is pumping 300 gpm (minimum pump flow from a 1800 gpm variable speed pump) while the cooling tower side of the heat exchanger ramps all the way
up to 1800 gpm full capacity (headered pump). The cooling tower is temperature controlled off the supply branch outlet and the mixed loop is temperature controlled off the mixed loop mixer for cooling and heating heat exchangers. The mixed loop also does
not drop to the low temperature set point even though there is heating call to the boiler. We also seem to have some issues with zone multipliers. We have plenty of mixed loop pumping capacity, but we have lots of unmet hours with the equipment we were given. When we
autosize the zone equipment, we get 2-3 times equipment sizes, but still at minimum pump flow. Any insight could be helpful. Ned Lyon, P.E. (MA, WV) 781.907.9000 main __._,_.___ Posted by: "Edward G. Lyon" <EGLyon@xxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |