[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Chiller operating hours





Hi all,


I'm modelling an office building which has 6 chillers for the chilled water loop. Therefore, I have set up 6 HVACTemplate:Plant:Chiller and 1 HVACTemplate:Plant:ChilledWaterLoop . But the problem I'm finding is that only 1 chiller appears to be working and the rest of them just remain off all the time. 


What I'm aiming to do is to control the hours of operation of every chiller manually and independently (by means of schedules or any other similar method) but I can't find the way to do so. For instance, turning ON all 6 chillers during peak load periods and turn them OFF during winter.


I would really appreciate if anyone could give me a hint to solve this problem or just reference me to any example or case where they might have experienced this or a similar issue.


Thanks so much!


Marcos




__._,_.___

Posted by: marcusbrown1326@xxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___