[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Chiller operating hours





Hi, refer to the example files that come with Eplus installation. There are examples of "Little chiller" and "Big chiller" working together and how their availability is scheduled. Also a little bit of fiddling with programming with EMS seems to make such tasks easier. There is an excel file in the examples folder that describes which idf file you have to refer to for your specific needs. Give it a go. Cherrs.

On 14/02/2015 5:42 AM, "Jim Dirkes jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Marcos,
If you are autosizing the chillers, all 6 of them will be autosized at 100% of needed capacity.  This means that only one chiller can meet the entire load.
You might try setting the Chiller Sizing Factor = .17 for each chiller.

On Fri, Feb 13, 2015 at 3:10 AM, marcusbrown1326@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hi all,


I'm modelling an office building which has 6 chillers for the chilled water loop. Therefore, I have set up 6 HVACTemplate:Plant:Chiller and 1 HVACTemplate:Plant:ChilledWaterLoop . But the problem I'm finding is that only 1 chiller appears to be working and the rest of them just remain off all the time. 


What I'm aiming to do is to control the hours of operation of every chiller manually and independently (by means of schedules or any other similar method) but I can't find the way to do so. For instance, turning ON all 6 chillers during peak load periods and turn them OFF during winter.


I would really appreciate if anyone could give me a hint to solve this problem or just reference me to any example or case where they might have experienced this or a similar issue.


Thanks so much!


Marcos





--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

The truth is like a lion; you donâ??t have to defend it. Let it loose; it will defend itself.



__._,_.___

Posted by: Tilek Aberra <tilek.aberra@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___