If the air temperature were maintained at the cooling setpoint all the time, then the PMV would be the same in all the zones unless for some reason they have differing humidities. Are they served by the same AHU? If it is window ventilated, are the ventilation rates equal? AFN would take the building height and stack effect into account. Differing leakage and window ventilation (height dependant) may result in differing humidities. PMV is basically a function of operative temperature and humidity. operative temperature is almost the average of the mean radiant and air temps. The difference must lay with these factors. Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity) i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23 On 04.03.2015, at 21:27, "Fakeha Sehar fakeha_s@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
__._,_.___ Posted by: "jeannieboef@xxxxxxxxx" <jeannieboef@xxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |