The three floors each have their own separate cooling systems. The design conditions for the three cooling systems are same . The three floors are identical. There is no window ventilation.

Inline image

The above figures are when cooling set point is 27C and lower ones for 24C.I am unable to understand by raising temp. to 27C bottom core zone starts behaving differently. Its operating temperatures, PMV go high when all zones cooling set point temperatures have been raised and cooling systems are indentical.


On Wednesday, March 4, 2015 4:10 PM, "'jeannieboef@xxxxxxxxx' jeannieboef@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:


 
If the air temperature were maintained at the cooling setpoint all the time, then the PMV would be the same in all the zones unless for some reason they have differing humidities. Are they served by the same AHU? If it is window ventilated, are the ventilation rates equal? AFN would take the building height and stack effect into account. Differing leakage and window ventilation (height dependant) may result in differing humidities.

PMV is basically a function of operative temperature and humidity. operative temperature is almost the average of the mean radiant and air temps. The difference must lay with these factors.

Mit freundlichen GrüÃ?en- Sent from my iPhone (excuse the brevity)

i. A.
Jean Marais
b.i.g. bechtold
Tel.   +49 30 6706662-23

On 04.03.2015, at 21:27, "Fakeha Sehar fakeha_s@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:

 
I am unable to figure about below

I have three floors, with one core zone and five perimeter zones each. When the core zone cooling set point is 24C, the top floor is slightly more hot (higher PMV index) as it receives more sunlight,  than the mid and bottom floors. Similarly, mid floor has higher PMV index than bottom.

Now when I raise the set point to 27C, I notice that mid floor has the lowest PMV index. Bottom floor has much higher PMV index than mid floor. The sensible cooling rate is higher than that of mid floor, why? Bottom floor PMV index should still have been the lowest.




__._,_.___
View attachments on the web

Posted by: Fakeha Sehar <fakeha_s@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.





__,_._,___
Attachment not found:
D:\Eudora\Attach\blob2.jpg