Re: [EnergyPlus_Support] Schedules



You are probably in a daylight saving period.

Look in the Tips and Tricks document about daylight saving time.


On 2015-03-08 16:03, Fakeha Sehar fakeha_s@xxxxxxxxx [EnergyPlus_Support] wrote:
I have occupancy schedule defined as below. As an example considering
the highlighted section ,as per this schedule occupancy should reduce
to 0.5 after noon and become 0.95 after 1pm, right? When I simulate
the building I observe from 11am to noon occupancy is 0.5. Similarly,
till 7am occupancy is 0.2 then its 0.95. Please explain.

For: Weekdays, !- Field 9
 Until: 06:00, !- Field 10
 0.0, !- Field 11
 Until: 07:00, !- Field 12
 0.1, !- Field 13
 Until: 08:00, !- Field 14
 0.2, !- Field 15
 Until: 12:00, !- Field 16
 0.95, !- Field 17
 Until: 13:00, !- Field 18
 0.5, !- Field 19
 Until: 17:00, !- Field 20
 0.95, !- Field 21
 Until: 18:00, !- Field 22
 0.7, !- Field 23
 Until: 20:00, !- Field 24
 0.4, !- Field 25
 Until: 22:00, !- Field 26
 0.1, !- Field 27
 Until: 24:00, !- Field 28
 0.05, !- Field 29

__._,_.___

-------------------------
 Posted by: Fakeha Sehar <fakeha_s@xxxxxxxxx>
-------------------------

 Primary EnergyPlus support is found at:
 http://energyplus.helpserve.com [1] or send a message to
energyplus-support@xxxxxxxx

 The primary EnergyPlus web site is found at:
 http://www.energyplus.gov [2]

 The group web site is:
 http://groups.yahoo.com/group/EnergyPlus_Support/ [3]

 Attachments are currently allowed but be mindful that not everyone
has a high speed connection. Limit attachments to small files.

 EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under
the Documentation link and press the "search" button.

 Visit Your Group [4]

 	* New Members [5] 7

 [6]
 * Privacy [7] * Unsubscribe * Terms of Use [8]

__,_._,___

Links:
------
[1] http://energyplus.helpserve.com
[2] http://www.energyplus.gov
[3] http://groups.yahoo.com/group/EnergyPlus_Support/
[4]
https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlY3ZudXFhBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTQyNTg1MjIyNg--
[5]
https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmM3E3b2YxBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzE0MjU4NTIyMjY-
[6]
https://groups.yahoo.com/neo;_ylc=X3oDMTJkNDRwMXBhBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxNDI1ODUyMjI2
[7] https://info.yahoo.com/privacy/us/yahoo/groups/details.html
[8] https://info.yahoo.com/legal/us/yahoo/utos/terms/