Hello, Calculating outdoor airflow is simple. In your model you have already specified this (or you should have), probably something like airflow per occupant, per floor area, or a mix of both. I don't know where your project is located but as far as I can tell, it's the same everywhere, there's a code that mandates it and prescribes those values (ashrae 62.1 for example). Anyways, in your case see what the peak outdoor air requirement is. Calculate an equivalent ACH (air changes per hour, typically m3/h of required Fresh air divided by space volume), and use that for your infiltration schedule for Design Days only. Or you could use an interior equipment to do the same if cooling is the problem. Same idea... That'll get the sizing routine to get it right. The calc isn't complicated, but if you need more guidance let me know, Good luck, Julien Envoyé de mon iPhone Le 19 avr. 2015 à 05:21, "ad3_prasetya@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> a écrit :
__._,_.___ Posted by: Julien Marrec <julien.marrec@xxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |