Re: [EnergyPlus_Support] How to set water pump with HVACTemplate





Dear Jin,
EnergyPlus always autosizes multiple plant object such as the cooling tower and chiller so that each component can supply 100% of the load.
I am not very familiar with the Templates, but it appears that a cooling tower and chiller can have a "Sizing Factor".  Try using Sizing Factor = 0.25; that should make each tower and chiller 25% of the total load.


On Fri, May 8, 2015 at 2:35 AM, sangjin722@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hi, users

I have a problem with HVACTemplate.
I am using HVACTemplate to model Appendix G system 7 and according to building peak cooling load, it need 4 cooling towers.
But after I get the results, I found that the flow rate of each condenser water pump is same with the pump flow rate which simulate with 1 cooling tower.
It means that the condenser water flow rate became 4 times more than that with 1 cooling tower.
How can I fix the model so that I can get the reasonable results?
Thanks.

- Jin




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

The truth is still the truth, even if nobody believes it.  A lie is still a lie, even if everyone believes it.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___