[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: Maximum Flow Rate Error





Hi there, I see this warning very often. Is this 'flow rate per wat (m³/s.W)' range a technological limitation for coils? 
Could not find anything about this in either I/O or Eng. Reference. Can anybody help me out of my ignorance in this area?

Regards,
Santiago.

2013-05-20 11:16 GMT-03:00 FrancescoP <direzionecontraria@xxxxxxxx>:
 

Hello, does that warning refer to a Coil:Cooling:DX:SingleSpeed ?
The warning massage concerns the ratio between the fields "Rated Air Flow Rate" and "Rated Total Cooling Capacity". If you are using the autosizing mode, you could see what "Rated Total Cooling Capacity" is calculated (e.g. in the .eio file) and then you could try imposing a value of the "Rated Air Flow Rate" in order to get a ratio between "Rated Air Flow Rate" and "Rated Total Cooling Capacity" that is in the acceptable range (the range should be indicated in the following part of the warning massage). Then you simulate again.
Best Regards
Francesco Passerini

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Ivan Mezzacapa <ivan_slip@...> wrote:
>
> Hi!
> my simulation gaves me this error.
> "Rated air volume flow rate per watt of rated totalcooling capacity is out of range"
> anyone nows how can i solve this?
> Thanks!
>
> Técg. Ivan Mezzacapa
> Projetista de Ar Condicionado / Consultor de Eficiência Energética em Ar Condicionado
> LinkedIN: http://www.linkedin.com/in/ivanmezzacapaFacebook: http://www.facebook.com/ivan.mezzacapaCelular: (11)9963-9326
>




__._,_.___

Posted by: Santiago Velez <santiagogvelez@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___