[EnergyPlus_Support] Re: Zone as supply side in OpenStudio





The only way I know of to do this in OS is to use a Fan:ZoneExhaust with a Balanced Exhaust Fraction Schedule. The other option would be to write an EnergyPlus Measure to add the ZoneMixing (one directional transfer) or ZoneCrossMixing (two directional transfer) objects to the IDF created by OS since these objects are not yet supported in OS.