Re: [EnergyPlus_Support] [html report] Heat pump for service hot water





Francesco,
Take a look at creating Meter:Custom objects.  They allow you to collect any components into a custom meter definition.  The Meter:CustomDecrement object is also helpful.

On Tue, Jul 7, 2015 at 10:09 AM, fpasserini.tn@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hello.

In my model there are three geothermal heat pumps that are connected to a loop whose function is space heating. In the same model there is a heat pump that produces service hot water.

The heat pumps are modeled with the object HeatPump:WaterToWater:EquationFit:Heating

In the .html report (â??Report: Annual Building Utility Performance Summaryâ??, table â??End Uses By Subcategoryâ??) all the heat that is produced by the four heat pumps is considered as â??Heatingâ??. Could I have in the report a distinction between the heat that is produced for space heating and the heat that is produced for service hot water?

For some objects there is the field "End-Use Subcategory", but there isn't for the object HeatPump:WaterToWater:EquationFit:Heating

Best Regards





--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

Life is not easy.  Itâ??s never been easy. Expecting it to be easy is not a healthy attitude.
Relax. Refresh. Regroup. Carry on.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___